EP23x9-0022 - Introduction
EP23x9-0022 - Introduction 1:
16-channel digital combi, 24 V DC
The EtherCAT Box EP23x9-0022 has 16 digital channels, each of which can be configured as an input or an output. A configuration whether a channel (Pin 2 and 4 of M12-socket)is to be used as input or output is not required; the input circuit is internally permanently connected to the output driver so that a set output is automatically displayed in the input process image.
The inputs of EP2339-0022 have a filter of 3.0 ms.
The inputs of EP2349-0022 have a filter of 10 µs.
The outputs can handle load currents up to 0.5 A, are short-circuit proof and protected against polarity reversal. The sum current of all outputs is limited to 4 A.
The connected sensors are supplied via an internal, short-circuit proof driver module with a total of 0.5 A for all sensors. The inputs and outputs are supplied from UP. The signal state is displayed by LEDs; the signal connection is established via screw-type M12 connectors.
EP23x9-0022 - Introduction 2:
Supply of the connected sensors from UP, not from US
In contrast to many other modules, the EP23x9-0022 EtherCAT Box supplies digital sensors from the Up peripheral voltage and not from the Us control voltage! Nevertheless, an overload of the sensor power supply (current > 0.5 A) is also indicated here by red lighting of the LED US.
Notice
For shutdown in the event of a fault, do not supply sensors externally
If the design of your installation is such that the supply voltage Up is switched off in the event of a fault, you must not power the connected sensors externally, but only through the EP23x9-0022! Otherwise, when the Up energy is switched off, the EP23x9-0022 can continue to draw energy from the external sensor power supply, and the outputs will not be switched off!
Notice
Damage to sensitive signal transducers due to current peaks
The protective circuit of a digital input can cause an inrush current peak of well over 2 mA during the switching operation. This current spike can damage sensitive signal transducers such as reed switches.
  • When using sensitive signal transducers, insert a series resistor before the digital input to reduce the inrush current peak. E.g. 1 kΩ
Quick links
Technical data
Process image
Dimensions
Signal interface