Configuration data
Index 8000 FB Settings
8000:0 | FB Settings | Maximum subindex | UINT8 | RO | 0x17 (23dec) |
8000:01 | Invert feedback direction | Inverting the count direction | BOOLEAN | RW | 0x00 (0dec) |
8000:02 | Referenced | Can be set to TRUE by the user. Is automatically set to FALSE as soon as a motor with a deviating serial number is recognized or if the feedback is single-turn. | BOOLEAN | RW | 0x00 (0dec) |
8000:0D | Offset position actual value source | Permitted values 0: Offset disabled 1: Encoder memory 2: Drive memory (default) |
8000:11 | Device type | 3: OCT (not changeable) | UINT32 | RW | 0x00000003 (3dec) |
8000:12 | Singleturn bits | Number of single-turn-bits | UINT8 | RW | 0x14 (20dec) |
8000:13 | Multiturn bits | Number of multi-turn-bits | UINT8 | RW | 0x0C (12dec) |
8000:14 | Observer bandwidth | Bandwidth of observer [Hz] | UINT16 | RW | 0x01F4 (500dec) |
8000:15 | Observer feed-forward | Load ratio[%] 50 % = moments of inertia of input and output are equal | UINT8 | RW | 0x01 (0dec) |
8000:17 | Positon offset | The position offset is subtracted from the raw position of the encoder. It can only be written with the axis stopped. | UINT32 | RW | 0x00000000 (0dec) |
Index 8001 FB Touch probe Settings
8001:0 | FB Touch probe Settings | Maximum subindex | UINT8 | RO | 0x12 (18dec) |
8001:11 | Touch probe 1 source | Permitted values: 1: Touch probe input 1 | UINT16 | RW | 0x0001 (1dec) |
8001:12 | Touch probe 2 source | Permitted values: 2: Touch probe input 2 | UINT16 | RW | 0x0002 (2dec) |
Index 8008 FB OCT Settings
8008:0 | FB OCT Settings | Maximum subindex | UINT8 | RO | 0x03 (3dec) |
8008:01 | Enable autoconfig | Configuration takes place automatically after the reading of the electronic type plate | BOOLEAN | RW | 0x00 (0dec) |
8008:02 | Reconfig identical motor | When replacing identical motors, reconfiguration takes place automatically after reading the electronic type plate. Enable autoconfig must be activated. | BOOLEAN | RW | 0x00 (0dec) |
8008:03 | Reconfig non-identical motor | When replacing non-identical motors, reconfiguration takes place automatically after reading the electronic type plate. Enable autoconfig must be activated. | BOOLEAN | RW | 0x00 (0dec) |
Index 8010 DRV Amplifier Settings
8010:0 | DRV Amplifier Settings | Maximum subindex | UINT8 | RO | 0x102 (66dec) |
8010:01 | Enable TxPDOToggle | Show TxPDO toggle in status word (bit 10) | BOOLEAN | RW | 0x00 (0dec) |
8010:02 | Enable input cycle counter | 1: enabled Two-bit counter that is incremented with each process data cycle up to a maximum value of 3, after which it starts again at 0 The low bit is represented in bit 10 and the high bit in bit 14 of the status word. | BOOLEAN | RW | 0x00 (0dec) |
8010:11 | Device type | 1: Servo drive (cannot be changed) | UINT32 | RW | 0x00000001 (1dec) |
8010:12* | Current loop integral time | Integral component of current controller This value is affected by automatic scanning. | UINT16 | RW | 0x000A (10dec) |
8010:13* | Current loop proportional gain | Proportional component of current controller This value is affected by automatic scanning. | UINT16 | RW | 0x0064 (100dec) |
8010:14 | Velocity loop integral time | Integral component of velocity controller | UINT32 | RW | 0x00000032 (50dec) |
8010:15 | Velocity loop proportional gain | Proportional component of velocity controller | UINT32 | RW | 0x00000096 (150dec) |
8010:17 | Position loop proportional gain | Proportional component of position controller | UINT32 | RW | 0x0000000A (10dec) |
8010:19 | Nominal DC link voltage | Rated DC link voltage | UINT32 | RW | 0x0000BB80 (48000dec) |
8010:1A | Min DC link voltage | Minimum DC link voltage | UINT32 | RW | 0x00001A90 (6800dec) |
8010:1B | Max DC link voltage | Maximum DC link voltage | UINT32 | RW | 0x0000EA60 (60000dec) |
8010:29 | Amplifier I2T warn level | I²T model warning threshold | UINT8 | RW | 0x50 (80dec) |
8010:2A | Amplifier I2T error level | I²T model error threshold | UINT8 | RW | 0x69 (105dec) |
8010:2B | Amplifier Temperature warn level | Overtemperature warning threshold | UINT16 | RW | 0x0320 (800dec) |
8010:2C | Amplifier Temperature error level | Overtemperature error threshold | UINT16 | RW | 0x03E8 (1000dec) |
8010:31 | Velocity limitation | Speed limitation | UINT32 | RW | 0x00040000 (262144dec) |
8010:32 | Short-circuit brake duration max | Max. duration of armature short-circuit brake | UINT16 | RW | 0x03E8 (1000dec) |
8010:33 | Stand still window | Standstill window | UINT16 | RW | 0x0000 (0dec) |
*) see index 0x9009 FB OCT Nameplate
8010:39 | Select info data 1 | Selection "Info data 1" | UINT8 | RW | 0x01 (1dec) |
1dec: Torque current (filtered 1 ms) [1000th of rated current] | |||||
2dec: DC link voltage [mV] | |||||
4dec: PCB temperature [0.1°C] | |||||
5dec: Errors: Bit0: ADC Error | |||||
6dec: Warnings: Bit2: Undervoltage | |||||
7dec: I2T Motor [%] | |||||
8dec: I2T Amplifier [%] | |||||
10dec: Input Level: Bit0: Digital Input 1 Level | |||||
8010:3A | Select info data 2 | Selection "Info data 2" | UINT8 | RW | 0x01 (1dec) |
8010:41 | Low-pass filter frequency | Load filter frequency The following values can be set: | UINT16 | RW | 0x0140 (320dec) |
8010:49 | Halt ramp deceleration | Halt ramp deceleration | UINT32 | RW | 0x0000F570 (62832dec) |
8010:50 | Following error window | Following error monitoring: following error window 0xFFFFFFFF (-1dec) = following error monitoring off | UINT32 | RW | 0xFFFFFFFF (-1 dec) |
8010:51 | Following error time out | Following error monitoring: timeout If the following error is larger than the following error window for a time that exceeds the timeout, this leads to an error reaction. | UINT16 | RW | 0x0000 (0 dec) |
8010:52 | Fault reaction option code | Allowed values | UINT16 | RW | 0x0000 (0 dec) |
8010:54 | Feature bits | The adjustable motor current values can be interpreted as peak values or RMS values. The feature bit enables the conversion. Peak value → Bit 0 = 0 (default for EL7201-001x) In the case of the EL7201-001x the output current can be increased with the help of the ZB8610 fan cartridge. Normal output current → Bit 1 = 0 (default) This allows you to set the following combinations: 0dec → normal output current interpreted as peak value 1dec → normal output current interpreted as RMS value 2dec → increased output current interpreted as peak value 3dec → increased output current interpreted as RMS value | UINT32 | RW | 0x00000000 (0 dec) |
8010:57 | Velocity feed forward gain | Velocity feedforward | UINT8 | RW | 0x64 (100dec) |
8010:65 | Invert direction of rotation | Reversal of the direction of rotation | BOOLEAN | RW | 0x00 (0dec) |
8010:66 | Enable cogging torque compensation | Activate cogging compensation | BOOLEAN | RW | 0x00 (0dec) |
Index 8011 DRV Motor Settings
8011:0 | DRV Motor Settings | Maximum subindex | UINT8 | RO | 0x2D (45dec) |
8011:11* | Max current | Peak current The adjustable motor current values can be interpreted as peak values or rms values. The feature bit (0x8010:54) enables the conversion. Peak value → Bit 0 = 0 (default with EL7201-001x) This value is affected by automatic scanning. | UINT32 | RW | 0x00001770 (6000dec) |
8011:12* | Rated current | Rated current The adjustable motor current values can be interpreted as peak values or rms values. The feature bit (0x8010:54) enables the conversion. Peak value → Bit 0 = 0 (default with EL7201-001x) This value is affected by automatic scanning. | UINT32 | RW | 0x000003E8 (1000dec) |
8011:13* | Motor pole pairs | Number of pole pairs This value is affected by automatic scanning. | UINT8 | RW | 0x03 (3dec) |
8011:15* | Commutation offset | Commutation offset (between electrical zero position and mechanical single-turn zero position) This value is affected by automatic scanning. | INT16 | RW | 0x0000 (0dec) |
8011:16* | Torque constant | Torque constant This value is affected by automatic scanning. | UINT32 | RW | 0x00000000 (0dec) |
8011:18* | Rotor moment of inertia | Mass moment of inertia of the motor This value is affected by automatic scanning. | UINT32 | RW | 0x00000000 (0dec) |
8011:19* | Winding inductance | Inductance This value is affected by automatic scanning. | UINT16 | RW | 0x000E (14dec) |
8011:1B* | Motor speed limitation | Velocity limitation This value is affected by automatic scanning. | UINT32 | RW | 0x00040000 (262144dec) |
8011:29 | I2T warn level | I2T model warning threshold | UINT8 | RW | 0x50 (80dec) |
8011:2A | I2T error level | I2T model error threshold | UINT8 | RW | 0x69 (105dec) |
8011:2B* | Motor Temperature warn level | Overtemperature warning threshold This value is affected by automatic scanning. | UINT16 | RW | 0x03E8 (1000dec) |
8011:2C* | Motor Temperature error level | Overtemperature error threshold This value is affected by automatic scanning. | UINT16 | RW | 0x05DC (1500dec) |
8011:2D* | Motor thermal time constant | Thermal time constant This value is affected by automatic scanning. | UINT16 | RW | 0x0028 (40dec) |
Index 8012 DRV Brake Settings
8012:0 | DRV Brake Settings | Maximum subindex | UINT8 | RO | 0x14 (20dec) |
8012:01 | Enable manual override | Manual release of the motor holding brake | BOOLEAN | RW | 0x00 (0dec) |
8012:02 | Manual brake state | 0: Release 1: Apply | BOOLEAN | RW | 0x00 (0dec) |
8012:11* | Release delay | Time the holding brake requires for opening (releasing) after the current was applied This value is affected by automatic scanning. | UINT16 | RW | 0x0000 (0dec) |
8012:12* | Application delay | Time the holding brake requires for closing (holding) after the current was switched off This value is affected by automatic scanning. | UINT16 | RW | 0x0000 (0dec) |
8012:13 | Emergency application timeout | Time the amplifier waits, until the rotation speed reaches the stand still window after stop request (set rotation speed 0 or Torque off). If the set waiting time is exceeded, the holding brake is triggered independently of the rotation speed. Note: For suspended (hanging) axes and the setting „torque off“ in error case, this parameter has to be set to an appropriate short time, to prevent the axis/load from drop/fall. | UINT16 | RW | 0x0000 (0dec) |
8012:14* | Brake moment of inertia | Mass moment of inertia of the brake This value is affected by automatic scanning. | UINT16 | RW | 0x0000 (0dec) |
The following note relates to the DMC objects 0x6030, 0x7030, 0x8030 and 0x8031.
![]() | Data type INT64 for all positions in the travel distance control The data type INT64 is used for all positions in the travel distance control.
Index 8030 DMC settings
8030:0 | DMC Settings | Maximum subindex | UINT8 | RO | 0x14 (20dec) |
8030:07 | Emergency deceleration | Deceleration for the emergency stop ramp. (In ms from rated motor speed to standstill) Unit: 1 ms | UINT16 | RW | 0x64 (100dec) |
8030:08 | Calibration position | If homing is successful, the "Actual position" is set to this value. | INT64 | RW | 0x0000000000000000 (0dec) |
8030:09 | Calibration velocity (towards plc cam) | Velocity on contact with the cam in 10000ths of the rated motor speed | INT16 | RW | 0x0064 (100dec) |
8030:0A | Calibration velocity (off plc cam) | Velocity on separation from the cam in 10000ths of the rated motor speed | INT16 | RW | 0x000A (10dec) |
8030:0E | Modulo factor | Feedback increments for one mechanical revolution | INT64 | RW | 0x0000000100000000 (4294967296dec) |
8030:12 | Block calibration torque limit | Torque limitation for approaching the end stop. In 1000ths of the rated motor current. | UINT16 | RW | 0x64 (100dec) |
8030:13 | Block calibration stop distance | After reaching the calibration position, the axis moves out of the end position by this distance. | INT64 | RW | 0x0000000100000000 (4294967296dec) |
8030:14 | Block calibration lag threshold | If this lag distance is exceeded, the axis is in the end position | INT64 | RW | 0x0000000100000000 (4294967296dec) |
8030:15 | Target position window | Target position window: The In-Target bit is set when the axis is within this window for at least the time set under 0x8030:16. | INT64 | RW | 0x16c16c1 |
8030:16 | Target position monitor time | s. 0x8030:15 time in Unit: ms | UINT16 | RW | 0x0014 (20dec) |
8030:17 | Target position timeout | When the set value generator has reached its end position | UINT16 | RW | 0x1770 (6000dec) |
Index 8031 DMC features
8031:0 | DMC Features | Maximum subindex | UINT8 | RO | 0x1B (27dec) |
8031:13 | Invert calibration cam search direction | Invert travel direction to search for limit switch | BOOLEAN | RW | 0x00 (0dec) |
8031:14 | Invert sync impulse search direction | Direction of rotation to leave the limit switch | BOOLEAN | RW | 0x01 (1dec) |
8031:19 | Calibration cam source | Source for the reference switch 0: Input 1 | ENUM8 | RW | 0x00 (0dec) |
8031:1A | Calibration cam active level | State of the reference switch in the actuated state 0: Hi | ENUM8 | RW | 0x00 (0dec) |
8031:B | Latch source | Source for the latch unit 0: Input 1 | ENUM8 | RW | 0x00 (0dec) |