0x80n0 | Configuration data
Index 80n0 AI Settings Ch. (n+1), (for n = 0 (Ch. 1) … n = 1 (Ch. 2))
Index (hex)
Meaning
Data type
Flags
Default
80n0:0
AI Settings
Maximum subindex
UINT8
RO
0x18 (24dec)
80n0:01
Enable user scale
User scaling is enabled.
BOOLEAN
RW
0x00 (0dec)
80n0:02
Presentation
Representation:
0: Signed presentation
1: Unsigned presentation
2: Absolute value with MSB as sign
Signed amount representation
BIT3
RW
0x00 (0dec)
80n0:05
Siemens Bits
The S5 bits are displayed in the three low-order bits.
BOOLEAN
RW
0x00 (0dec)
80n0:06
Enable Filter 1
Enables filter 1, which makes PLC-cycle-synchronous data exchange unnecessary
BOOLEAN
RW
0x01 (1dec)
80n0:07
Enable Limit 1
Enables limit 1
BOOLEAN
RW
0x00 (0dec)
80n0:08
Enable Limit 2
Enables limit 2
BOOLEAN
RW
0x00 (0dec)
80n0:0A
Enable User Calibration
Enables the user calibration
BOOLEAN
RW
0x00 (0dec)
80n0:0B
Enable Vendor Calibration
Enables the vendor calibration
BOOLEAN
RW
0x01 (1dec)
80n0:0E
Swap Limit Bits
Swaps the limit bits
BOOLEAN
RW
0x00 (0dec)
80n0:11
User Scale Offset
User scale offset
INT16
RW
0x0000 (0dec)
80n0:12
User Scale Gain
User scale gain.
The gain is a fixed-point number with the factor 2-16.
The value 1 corresponds to 65535dec (0x00010000hex) and is limited to +/-0x7FFFF.
INT32
RW
0x00010000 (65536dec)
80n0:13
Limit 1
First limit value for setting the status bits
INT16
RW
0x0000 (0dec)
80n0:14
Limit 2
Second limit value for setting the status bits
INT16
RW
0x0000 (0dec)
80n0:15
Filter Settings
This object determines the digital filter settings, if it is enabled via “Enable Filter” (index 0x8000:06).
The possible settings are sequentially numbered.
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
Refer to the Note on setting the filter characteristics
UINT16
RW
0x0000 (0dec)
80n0:17
User Calibration Offset
User calibration offset
INT16
RW
0x0000 (0dec)
80n0:18
User Calibration Gain
User calibration gain
INT16
RW
0x4000 (16384dec)
0x80n0 | Configuration data 1:
The filter characteristics are set via index 0x8000:15
The filter frequencies are set for all channels centrally via index 0x8000:15 (channel 1). All other corresponding indices 0x80n0:15 have no parameterization function! The latest firmware version (see status table) returns an EtherCAT-compliant error message, if the filter characteristics of other channels (index 0x80n0:06, 0x80n0:15) are set.
Index 80nC AI User Calibration Data Ch. (n+1), (for n = 0 (Ch. 1) … n = 1 (Ch. 2))
Index (hex)
Meaning
Data type
Flags
Default
80nC:0
Max. subindex
UINT8
RO
0x0D (13dec)
80nC:01
Calibration Date
4 bytes of free memory space;
here it is possible to store the calibration date in the form of 8 CHAR, for example
OCTET-STRING[4]
RW
{0}
80nC:03
S0
Real32 coefficient S0
REAL32
RW
0x00000000 (0dec)
80nC:04
S1
Real32 coefficient S1
REAL32
RW
0x00000000 (0dec)
80nC:05
S2
Real32 coefficient S2
REAL32
RW
0x00000000 (0dec)
80nC:06
S3
Real32 coefficient S3
REAL32
RW
0x00000000 (0dec)
80nC:0D
S1n
Real32 coefficient S1n
REAL32
RW
0x00000000 (0dec)
Index 80nD AI Advanced Settings Ch. (n+1), (for n = 0 (Ch. 1) … n = 1 (Ch. 2))
Index (hex)
Meaning
Data type
Flags
Default
80nD:0
Max. subindex
UINT8
RO
0x2A (42dec)
80nD:11
Input Interface
Input Interface values:
0 – None
2 – V ±10V
14 – V 0-10V
17 – I ±20mA
18 – I 0-20mA
19 – I 4-20mA
20 – I 4-20mA NAMUR
UINT16
RW
0x0002 (2dec)
80nD:12
Integer Scaler
Integer Scaler values:
0 – Extended Range
3 – Legacy Range
UINT16
RW
0x0000 (0dec)
80nD:17
Low Range Error
“Low Range” limit value (see chapter “Range error”)
INT32
RW
0xFFFF8000 (-32768dec)
80nD:018
High Range Error
“High Range” limit value (see chapter “Range error”)
INT32
RW
0x00007FFF (32767dec)
80nD:1A
Filter 2 Settings
Filter 2 Settings values:
0 – Off
1 – HP 0.001 Hz
2 – HP 0.01 Hz
3 – HP 0.1 Hz
4 – HP 1 Hz
5 – HP 10 Hz
UINT16
RW
0x0000 (0dec)
80nD:1C
User Scale Offset (Real32)
User scale offset (Real32)
REAL32
RW
0x00000000 (0.0)
80nD:1D
User Scale Gain (Real32)
User scale gain (Real32)
REAL32
RW
0x3F800000 (1.0)
80nD:27
Low Range Error (Real32)
“Low Range (Real32)” limit value (see chapter “Range error”)
REAL32
RW
0xC12BCC79 (-10.7374201)
80nD:28
High Range Error (Real32)
“High Range (Real32)” limit value (see chapter “Range error”)
REAL32
RW
0x412BCC79 (10.7374201)
80nD:29
Limit 1 (Real32)
Limit 1 limit value
REAL32
RW
0x00000000 (0.0)
80nD:2A
Limit 2 (Real32)
Limit 2 (INT16) in the AI settings is adjusted automatically
REAL32
RW
0x00000000 (0.0)
80nD:2B
Steady State Window
Time constant for the “Steady State” bit (see chapter “Steady State”)
UINT16
RW
0x0064 (100dec)
80nD:2C
Steady State Tolerance
Tolerance window for the “Steady State” bit
REAL32
RW
0x3F800000 (1065353216dec)
80nD:2D
Low Range Warning (Real32)
“Low Range (Real32)” warning limit value (see chapter “Range Warning”)
REAL32
RW
0xC1200000 (-1054867456dec)
80nD:2E
High Range Warning (Real32)
“High Range (Real32)” warning limit value (see chapter “Range Warning”)
REAL32
RW
0x41200000 (1092616192dec)