IDN 76 (S-0-0076) Position Data Scaling Type
Defines the scaling options for all position data. The supported scaling types are indicated in bold-face type. The following scaling types are available: 0001(Hex), 0081(Hex), 0009(Hex), 0089(Hex), 000A(Hex) and 008A(Hex).
If linear scaling is selected without modulo format on (bit 7 = 1), the software limit switches are automatic switched on (refer to IDN 49 , 50, 55 and IDN 3004 ).
If modulo format is selected, the drive operates without interpolation.
If rotational scaling is selected and the rotational position resolution ( IDN 79 ) is different from 1048576 or 65536 the modulo format must switch on, this will check during run up. A change of bit 7 will initiate a warm start procedure (refer to IDN 128 during run up. With set the operation mode within IDN 32 or 33 to position control with external feedback, this IDN will set to 004A(Hex) as a fixed setting. The drive can only operate with a fixed rotational scaling for the position data in this case (refer to IDN 79 ).
Data Length:
2 bytes
Non-Volatile:
Yes
Data Type:
Binary
Write Access:
CP2
Minimum:
0001H
Run-Up Check:
CP3
Maximum:
008AH
Cyclic Transfer:
Default:
000AH
Serial Equiv:
SERCSET (Bits 24 – 31)
Units:
Version:
5.04
IDN Type:
PS
ADS Index Group (hex.):
0x004C
Definition:
Bit
Value
Scaling Method
000
Reserved: No Scaling
001
Linear Scaling
010
Rotational Scaling
3
Standard Scaling Type
0
Preferred Scaling
1
Parameter Scaling
4
Reserved: Units for Linear Scaling
0
1
Meters (m)
Inches (in)
4
Units for Rotational Scaling
0
Degrees
1
Reserved
5
Reserved
6
Data Reference
0
At the Motor Shaft
1
At the Load (Only for rotational scaling)
7
Processing Format
0
Absolute Format
1
Modulo Format (See IDN 103 )
15-8
Reserved