FB_BA_AC_ErcTSuACtrl

FB_BA_AC_ErcTSuACtrl 1:

The template represents the supply air temperature control of an energy recovery system with the sequence controller Ctrl.

The sequence controller is enabled via the input variable bEn. If the control direction of the energy recovery system is indirect (heating mode) and the air conditioning system is in dehumidification mode bDehumf at the same time, energy recovery is blocked.

The sequence controllers are enabled for sequence control using the stSeqLink data and command structure. This is indicated by the variable bSeqActv.

Control direction

The control direction of the sequence controller Ctrl is selected based on a comparison of the outside temperature with the extract air temperature.

If the outside temperature is lower than the extract air temperature, the control direction of the sequence controller Ctrl is indirect (heating mode), see E_BA_Action.

If the outside temperature is higher than the extract air temperature, the control direction of the sequence controller Ctrl is direct (cooling mode), see E_BA_Action.

FB_BA_AC_ErcTSuACtrl 2:
FB_BA_AC_ErcTSuACtrl 3:

The initialization of the template takes place within the method FB_Init.

Block diagram

FB_BA_AC_ErcTSuACtrl 4:

Syntax

FUNCTION_BLOCK FB_BA_AC_ErcTSuACtrl EXTENDS FB_BA_View
VAR_INPUT
  bEn                 : BOOL;
  fSpTSuA             : REAL;
  fTSuA               : REAL;
  bSync               : BOOL;
  fSync               : REAL;
  bDehumf             : BOOL;
  fTExtA              : REAL;
  fTWth               : REAL;
END_VAR
VAR_OUTPUT
  fY                  : REAL;
  eAction             : E_BA_Action;
  bIsActive           : BOOL;
  bSeqActv            : BOOL;
END_VAR
VAR_IN_OUT
  stSeqLink           : ST_BA_SeqLink;
END_VAR
VAR_INPUT CONSTANT PERSISTENT
  {attribute 'parameterCategory' := 'Behaviour'}
  fHysActionOn        : REAL := 0.25;
  {attribute 'parameterCategory' := 'Behaviour'}
  fHysActionOff       : REAL := -0.25;
END_VAR
VAR_INPUT CONSTANT
  Ctrl                : FB_BA_SeqCtrl;
END_VAR
VAR
  HysAction           : FB_BA_Swi2P;
END_VAR

FB_BA_AC_ErcTSuACtrl 5: Inputs

Name

Type

Description

bEn

BOOL

Enable for the frequency controller Ctrl.

fSpTSuA

REAL

Setpoint of the supply air temperature.

fTSuA

REAL

Measured value of the supply air temperature.

bSync

BOOL

Pulse for synchronization of the sequence controller Ctrl.

fSync

REAL

Value for the synchronization of the sequence controller Ctrl.

bDehumf

BOOL

Indicates with a TRUE that the air conditioning system is in dehumidification mode.

fTExtA

REAL

Measured value extract air temperature

fTWth

REAL

Measured value weather temperature

FB_BA_AC_ErcTSuACtrl 6: Outputs

Name

Type

Description

fY

REAL

Control value output

eAction

E_BA_Action

The output of the control direction of the supply air controller Ctrl is required within an air conditioning system for the setpoint strategy.

bIsActive

BOOL

The sequence controller is the active one in the sequence control.

bSeqActv

BOOL

The sequence controller is implemented in the control sequence.

FB_BA_AC_ErcTSuACtrl 7: Inputs/outputs

Name

Type

Description

stSeqLink

ST_BA_SeqLink

The data and command structure is the link between the supply air temperature sequence controller Ctrl and the supply air temperature sequence controller TSeqLink of an air conditioning system.

FB_BA_AC_ErcTSuACtrl 8: Inputs CONSTANT PERSISTENT

Name

Type

Description

fHysActionOn

REAL

Upper switching point of the hysteresis HysAction to determine the control direction of the supply air controller Ctrl.

fHysActionOff

REAL

Lower switching point of the hysteresis HysAction to determine the control direction of the supply air controller Ctrl.

FB_BA_AC_ErcTSuACtrl 9: Inputs CONSTANT

Name

Type

Description

Ctrl

FB_BA_SeqCtrl

The supply air temperature sequence controller Ctrl is the core of this template. It is responsible for the supply air temperature control of the cooler.

The sequence controller is also part of the supply air temperature sequence control of an air conditioning system, see sample FB_BA_AC_SeqT. The data exchange within this sequence control takes place via the data and command structure stSeqLink.

The global variable E_BA_AC_SeqNumber_T.eEnergyRecovery gives the sequence controller its sequence number within the temperature sequence control.

Variables

Name

Type

Description

HysAction

FB_BA_Swi2P

The two-position switch determines the control direction of the sequence controller depending on the outside temperature fTWth and the extract air temperature fTExtA and the switching points of the hysteresis fHysActionOn/fHysActionOff.

If the subtraction of the outside temperature fTWth and the extract air temperature fTExtA > fHysActionOn, then the output of the function block HysAction is TRUE. The control direction of the sequence controller Ctrl is therefore direct and energy recovery is in cooling mode.

If the subtraction of the outside temperature fTWth and the extract air temperature fTExtA < fHysActionOff, then the output of the function block HysAction is FALSE. The control direction of the sequence controller Ctrl is therefore indirect and energy recovery is in heating mode.