FB_BA_Swi4DALI
FB_BA_Swi4DALI 1:
This function block is used to read a DALI 4-fold push button.
For information on the function of the DALI device used, please refer to the manufacturer's device documentation.
Function
The device itself is specified by the instance numbers of the buttons, nInstButton1...nInstButton4.
The device's internal notification system is always used, which automatically sends a telegram as soon as a button press or release is detected.
The states of the buttons are also queried cyclically. This ensures that the state of the buttons is always corrected if a telegram is "lost".
The DALI push button function block can be initialized with fixed parameters via the input bInitialize, see VAR CONSTANT.
FUNCTION_BLOCK FB_BA_Swi4DALI
  bEn                    : BOOL;
  bInitialize            : BOOL;
  nAdr                   : BYTE;
  nInstButton1           : BYTE;
  nInstButton2           : BYTE;
  nInstButton3           : BYTE;
  nInstButton4           : BYTE;
  ipDALICommunication    : Tc3_DALI.I_DALICommunication;
  bButton1               : BOOL;
  bButton2               : BOOL;
  bButton3               : BOOL;
  bButton4               : BOOL;
  bInitializing          : BOOL;
  bErr                   : BOOL;
VAR_INPUT CONSTANT PERSISTENT
  nPrdQuery              : UDINT := 60;
VAR CONSTANT
  nEventFilter           : DWORD := 131;
  eEventPriority         : Tc3_DALI.E_DALIEventPriority := Tc3_DALI.E_DALIEventPriority.Middle;
  eEventScheme           : Tc3_DALI.E_DALIEventScheme := Tc3_DALI.E_DALIEventScheme.DeviceInstance;
  nRepeatTimer           : UINT := 160;
  nShortTimer            : UINT := 500;
  nDoubleTimer           : UINT := 0;
  nStuckTimer            : BYTE := 20;
FB_BA_Swi4DALI 2: VAR_INPUT
Type
bEn
Enabling the function block: a TRUE signal at this input enables the function.
bInitialize
A positive edge at this input starts the DALI initialization routine, which transfers the set parameters to the DALI device, see FB_BA_Swi4DALI.
nAdr
BYTE
DALI short address of the push button sensor.
nInstButton1... nInstButton4
BYTE
Numbers of the push button instances to be queried.
ipDALICommunication
Interface pointer to the DALI communication block.
FB_BA_Swi4DALI 3: VAR_OUTPUT
Type
bButton1...bButton4
State of the individual push buttons (TRUE = pressed).
bInitializing
The sensor is in the DALI initialization phase, i.e. the entered parameters are transferred to the DALI device.
bErr
Error output. A plain text is output in TwinCAT in the error list in the output window.
FB_BA_Swi4DALI 4: VAR_INPUT CONSTANT PERSISTENT
Type
nPrdQuery
UDINT
Query interval of the switch states. This query is only used for correction if an incorrect state is detected due to a telegram error.
VAR CONSTANT
FB_BA_Swi4DALI 5:
The following parameters cannot be changed and are transferred to the DALI device by the initialization routine.
Type
nEventFilter
DWORD
DALI event filter mask for occupancy sensors. This value is set to 7 and thus queries the Occupied, Vacant and Repeat Event states.
eEventPriority
DALI event priority with which input notification events are sent by the instance of the DALI control device, set to Middle.
eEventScheme
DALI event scheme. This is set to DeviceInstance (device/instance addressing with short address and instance number).
nRepeatTimer
UINT
Repeat Timer as a multiple of 20 ms. Set to 8 (=160 ms).
nShortTimer
UINT
Short Timer as a multiple of 20 ms. Set to 25 (=500 ms).
nDoubleTimer
UINT
Double Timer as a multiple of 20 ms. Set to 0 (=0 ms). This means that this value is set to the vendor-specific minimum value.
nStuckTimer
BYTE
Stuck Timer in seconds. Set to 20 s.