MC_CamScaling
MC_CamScaling 1:
This function block applies the scaling factor of an existing cam table coupling on a slave. InSync of the existing cam table coupling is not affected by this function block.
Definition:
FUNCTION_BLOCK MC_CamScaling
    Slave             : Type_Camming1D;
    CamObject         : Type_CouplingFunction1D;
    Execute           : BOOL;
    Scaling           : CamScalingData;
    ActivationOptions : CamActivationOptions;
    Done              : BOOL;
    Busy              : BOOL;
    Active            : BOOL;
    CommandAborted    : BOOL;
    Error             : BOOL;
    ErrorId           : UDINT;
MC_CamScaling 2: Inputs
Type
Slave
Type_Camming1D
Reference to the slave axis
CamObject
Reference to the cam object
Execute
Apply cam scaling at rising edge
Scaling
CamScalingData
New cam scaling
ActivationOptions
Options controlling how the cam coupling is activated (mode, position, reference object).
MC_CamScaling 3: Outputs
Type
Done
Cam scaling succeeded
Busy
Function block is not finished and new output values are to be expected.
Active
Function block has active control on the axis.
CommandAborted
Command is aborted by another command.
Error
Error occurred within function block.
ErrorId
UDINT
Error identifier
Further information
A cam plate coupling can be scaled with the function block MC_CamScaling. The raw table data of the cam plate are not affected; instead, the scaling refers to an active master/slave coupling. The following parameters can be modified: scaling factors for master and slave, and offsets for the cam plate within the coordinate system.
Optionally, the modification will only take effect from a certain master position, enabling precise scaling during the motion.
Notice
Property damage due to modifying an active cam plate coupling
This function block can also be used for an active cam plate. Valid changes are applied to the cam plate and may result in setpoint jumps. To activate cam plate scaling at a specific time or at a specific position, the following procedure is recommended:
  • Use ECamActivationMode.AtBoundary, ECamActivationMode.AtMasterCamPosition, or ECamActivationMode.AtMasterAbsolutePosition
  • Alternatively, create a copy of the active cam plate (using the CopyFrom() method) and make the changes to the copy. Next, switch between the cam plates (MC_CamExchange).
Version information
  • TwinCAT Standard >= v3.1.4026.23.1
  • TF5550 MC3 Camming >= v4.0.6 (includes TF5500 MC3 Base >= v4.0.6)
Required License
TC3 MC3 Camming