FB_DALI102SendCommand
FB_DALI102SendCommand 1:
The FB_DALI102SendCommand function block sends the specified DALI command to the DALI control gear.
An additional parameter can be transferred for certain DALI commands via the nParameter input. The exact meaning of the parameter is defined in the DALI standard. These DALI commands are identified in the nParameter column in the table below.
The return value for the query commands is output at the nResponse output. The exact meaning of the parameter is defined in the DALI standard. These DALI commands are identified in the nResponse column in the table below.
Some DALI commands are sent twice, as required by the DALI standard for certain DALI commands. These DALI commands are identified in the send twice column in the table below.
If several instances of FB_DALI102SendCommand send DALI commands via the same DALI terminal, the DALI commands of the individual instances are not synchronized with each other. This can lead to undesirable behavior, for example, if parameters in DALI control gears are changed.
In most cases, several DALI commands must be sent to change a parameter. Among other things, the DALI command must also be used to set the DTR. As the DALI command for setting the DTR is always sent as a broadcast command, this has an effect on all DALI control gears in a DALI line. If several instances of FB_DALI102SendCommand change the parameters of DALI control gears on a DALI line at the same time, this can lead to undesirable side effects.
FB_DALI102SendCommand 2:
This means that only one instance of FB_DALI102SendCommand should be created per DALI line. The DALI commands must then be synchronized in the application that accesses FB_DALI102SendCommand.
FB_DALI102SendCommand 3: Inputs
  bStart            : BOOL;
  nAddress          : BYTE;
  nCommand          : INT;
  nParameter        : USINT;
Type
bStart
nAddress
BYTE
eAddressType
E_DALIAddressType
eCommandPriority
E_DALICommandPriority
FB_DALI102SendCommand 4:
Type
nCommand
INT
DALI command to be sent.
Possible DALI commands are listed in the table below.
nParameter
USINT
Additional parameter of a DALI command. Commands with additional parameters are listed in the table below.
FB_DALI102SendCommand 5: Outputs
  nResponse               : BYTE;
Type
ipResultMessage
I_TcMessage
bBusy
nResponse
BYTE
Return value of the query command. The table below shows the commands with potential return values.
FB_DALI102SendCommand 6: Properties
Type
Access
Initial value
ipDALICommunication
I_DALICommunication
Get, Set
NULL
Commands
nCommand
DALI command
nParameter
nResponse
Send twice
-1
DAPC
0
OFF
1
UP
2
DOWN
3
STEP UP
4
STEP DOWN
5
RECALL MAX LEVEL
6
RECALL MIN LEVEL
7
STEP DOWN AND OFF
8
ON AND STEP UP
9
ENABLE DAPC SEQUENCE
10
GO TO LAST ACTIVE LEVEL
11
CONTINUOUS UP
12
CONTINUOUS DOWN
16…31
GO TO SCENE
32
RESET
33
STORE ACTUAL LEVEL IN DTR0
35
SET OPERATING MODE
36
RESET MEMORY BANK
37
IDENTIFY DEVICE
42
SET MAX LEVEL
43
SET MIN LEVEL
44
SET SYSTEM FAILURE LEVEL
45
SET POWER ON LEVEL
46
SET FADE TIME
47
SET FADE RATE
48
SET EXTENDED FADE TIME
64…79
SET SCENE
80…95
REMOVE FROM SCENE
96…111
ADD TO GROUP
112…127
REMOVE FROM GROUP
128
SET SHORT ADDRESS
129
ENABLE WRITE MEMORY
144
QUERY STATUS
145
QUERY CONTROL GEAR PRESENT
146
QUERY LAMP FAILURE
147
QUERY LAMP POWER ON
148
QUERY LIMIT ERROR
149
QUERY RESET STATE
150
QUERY MISSING SHORT ADDRESS
151
QUERY VERSION NUMBER
152
QUERY CONTENT DTR0
153
QUERY DEVICE TYPE
154
QUERY PHYSICAL MINIMUM
155
QUERY POWER FAILURE
156
QUERY CONTENT DTR1
157
QUERY CONTENT DTR2
158
QUERY OPERATING MODE
159
QUERY LIGHT SOURCE TYPE
160
QUERY ACTUAL LEVEL
161
QUERY MAX LEVEL
162
QUERY MIN LEVEL
163
QUERY POWER ON LEVEL
164
QUERY SYSTEM FAILURE LEVEL
165
QUERY FADE TIME/FADE RATE
166
QUERY MANUFACTURER SPECIFIC MODE
167
QUERY NEXT DEVICE TYPE
168
QUERY EXTENDED FADE TIME
170
QUERY CONTROL GEAR FAILURE
176…191
QUERY SCENE LEVEL
192
QUERY GROUPS 0-7
193
QUERY GROUPS 8-15
194
QUERY RANDOM ADDRESS H
195
QUERY RANDOM ADDRESS M
196
QUERY RANDOM ADDRESS L
197
READ MEMORY LOCATION
255
QUERY EXTENDED VERSION NUMBER
256
TERMINATE
257
DTR0
258
INITIALISE
259
RANDOMISE
260
COMPARE
261
WITHDRAW
264
SEARCHADDR H
265
SEARCHADDR M
266
SEARCHADDR L
267
PROGRAM SHORT ADDRESS
268
VERIFY SHORT ADDRESS
269
QUERY SHORT ADDRESS
272
ENABLE DEVICE TYPE
273
DTR1
274
DTR2
275
WRITE MEMORY LOCATION
276
WRITE MEMORY LOCATION - NO REPLY
Prerequisites
Development environment
Required PLC library
TwinCAT from v3.1.4024.68