FB_SMISlaveAddrRead
FB_SMISlaveAddrRead 1:
The function block FB_SMISlaveAddrRead reads the address (0-15) of a drive.
FB_SMISlaveAddrRead 2: Inputs
  bStart           : BOOL;
  dwAddr           : DWORD := 0;
  eAddrType        : E_SMIAddrType := eSMIAddrTypeAddress;
  dwAddrOption     : DWORD := 0;
  eCommandPriority : E_SMICommandPriority := eSMICommandPriorityMiddle;
Type
bStart
The function block is activated and the command is sent by applying a positive edge to this input.
dwAddr
DWORD
Manufacturer code (0-15), address of a device (0-15), bit field (16 bits) for group addressing or slave ID (32-bit key ID). This input has no meaning if a broadcast is sent.
eAddrType
E_SMIAddrType
Defines whether the input dwAddr is to be evaluated as a manufacturer code, the address of a device, for group addressing or as a slave ID.
dwAddrOption
DWORD
If the SMI device is addressed by slave ID (eAddrType = eSMIAddrTypeSlaveId), then the manufacturer code must be specified via this input.
eCommandPriority
Priority (high, medium or low) with which the command is processed by the PLC library.
FB_SMISlaveAddrRead 3: Inputs/outputs
  stCommandBuffer : ST_SMICommandBuffer;
Type
stCommandBuffer
ST_SMICommandBuffer
Reference to the structure for communication (buffer) with the function block FB_KL6831KL6841Communication()
FB_SMISlaveAddrRead 4: Outputs
  bBusy       : BOOL;
  bError      : BOOL;
  udiErrorId  : UDINT;
  bySlaveAddr : BYTE;
Type
bBusy
This output is set as soon as the function block processes a command and remains active until the command has been processed.
This output is switched to TRUE as soon as an error occurs during the execution of a command. The command-specific error code is contained in udiErrorId. The output is reset to FALSE by the reactivation of the function block via the input bStart.
udiErrorId
UDINT
Contains the command-specific error code of the most recently executed command. It is reset to 0 by the reactivation of the function block via the input bStart (see error codes).
bySlaveAddr
BYTE
The read slave address (0-15)
Development Environment
PLC library to include
TwinCAT from v3.1.4020.14
Tc2_SMI from 3.3.5.0
