MP_CMV

This function block is used to control and monitor a volume flow regulator.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. If bStart remains TRUE, the device is addressed cyclically with a period specified by the time in TMPolling. The time should be set longer than 1 second. bError is used to indicate an error in communication with the drive. The type of the error can be read with iErrorID.
Inputs
VAR_INPUT
MP_Address : USINT := 1;
bStart : BOOL;
bSet : BOOL;
bOpen : BOOL;
bClose : BOOL;
bReset : BOOL;
iSensorTyp : INT;
Setpoint : USINT;
MaxVol : WORD;
MinVol : WORD;
strDataKL6771 : DataKL6771;
TMpolling : TIME := t#10s;
END_VARName | Type | Description |
|---|---|---|
MP_Address | USINT | MP-Bus address of the slave. |
bStart | BOOL | A positive edge starts the function block. If this remains continuously TRUE, the function block will be activated cyclically with a period specified by the time in TMPolling. |
bSet | BOOL | A positive edge writes the data MaxVol and MinVol to the actuator. |
bOpen | BOOL | A positive edge opens the dampers of the actuator, while a negative edge cancels the forced ventilation. |
bClose | BOOL | A positive edge closes the dampers of the actuator, while a negative edge cancels the forced closure. |
bReset | BOOL | A positive edge resets the actuator's error messages. |
iSensorTyp | INT | 0: no sensor connected, 1: digital sensor connected, 2: analog sensor connected (0...35 V), 3...6: output of a resistance in ohms (3..5 applies to PT1000, NI1000 and NI1000LuS; 6 applies to NTC). To convert to a temperature, use the corresponding conversion functions. |
Setpoint | USINT | Set volume flow rate in % (0..100). |
MaxVol | WORD | Maximum volume flow rate in % (30..100). |
MinVol | WORD | 0…100 % Minimum volume flow rate |
strDataKL6771 | The data structure with which the KL6771() function block must be linked. | |
TMpolling | TIME | The time for which the function block should address the actuator. Default 10 s, minimum time 1 s. |
Outputs
VAR_OUTPUT
bBusy : BOOL;
bError : BOOL;
iErrorId : MP_Error;
ActValue : WORD;
bMP_Sensor_Digi : BOOL;
iMP_Sensor_Analog : INT;
AirVolume_m3h : WORD;
iVnom_m3h : INT;
act_MaxVol : INT;
act_MinVol : INT;
bErr_ActHunt : BOOL;
bErr_MecTrv : BOOL;
bErr_MecOvld : BOOL;
rTemperature : LREAL
END_VARName | Type | Description |
|---|---|---|
bBusy | BOOL | This bit is set for as long as the function block is active. |
bError | BOOL | This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable. |
iErrorId | This output outputs an error code in the event of an error. bError goes TRUE at the same time. | |
ActValue | WORD | Contains the current position of the actuator (0...100 %). |
bMP_Sensor_Digi | BOOL | If a digital sensor is connected, its state is indicated through this variable. iSensorTyp must be "1". |
iMP_Sensor_Analog | INT | If an analog sensor is connected, its value is indicated through this variable. iSensorTyp must be "2...6". |
AirVolume_m3h | WORD | Output of the volume flow rate in m³/h. |
iVnom_m3h | INT | Nominal air volume flow in m³/h. This output is available from version 1.12.0. VAV is read and must be > 0. If 0, then the calculation of AirVolume_m3h is not correct. |
act_MaxVol | INT | Maximum set volume flow rate in %. |
act_MinVol | INT | Minimum set volume flow rate in %. |
bErr_ActHunt | BOOL | Actuator error, "Regulating oscillation"; the actuator is swinging backwards and forwards. |
bErr_MecTrv | BOOL | Actuator error, "Positioning angle exceeded"; the actuator has passed more than 10° beyond the adaptation position. |
bErr_MecOvld | BOOL | Actuator error, "Overload"; the set position could not be reached. |
rTemperature | LREAL | Temperature in the duct in °C. |
Requirements
Development environment | PLC library to include |
|---|---|
TwinCAT from v3.1.4022.14 | Tc2_MPBus from 3.4.8.0 |