MP_EPIV

MP_EPIV 1:

This function block is used to control a pressure-independent control ball valve. For more information please visit www.belimo.com.

MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. If bStart remains TRUE, the device is addressed cyclically with a period specified by the time in TMPolling. The time should be set longer than 1 s. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.

MP_EPIV 2: Inputs

VAR_INPUT
  MP_Address    : USINT := 1;
  bStart        : BOOL;
  bSet          : BOOL;
  bOpen         : BOOL;
  bClose        : BOOL;
  bReset        : BOOL;
  iSensorTyp    : INT;
  Setpoint      : USINT;
  MaxVol        : WORD;
  strDataKL6771 : DataKL6771;
  TMpolling     : TIME := t#10s;
END_VAR

Name

Type

Description

MP_Address

USINT

MP-Bus address of the slave.

bStart

BOOL

A positive edge starts the function block. If this remains continuously TRUE, the function block will be activated cyclically with a period specified by the time in TMPolling.

bSet

BOOL

A positive edge writes the data MaxVol and MinVol to the actuator.

bOpen

BOOL

A positive edge opens the dampers of the actuator, while a negative edge cancels the forced ventilation.

bClose

BOOL

A positive edge closes the dampers of the actuator, while a negative edge cancels the forced closure.

bReset

BOOL

A positive edge resets the actuator's error messages.

iSensorTyp

INT

0: no sensor connected, 1: digital sensor connected, 2: analog sensor connected (0...35 V), 3...6: output of a resistance in ohms (3..5 applies to PT1000, NI1000 and NI1000LuS; 6 applies to NTC). To convert to a temperature, use the corresponding conversion functions.

Setpoint

USINT

Set volume flow rate in % (0..100).

MaxVol

WORD

Maximum volume flow rate in % (30..100).

strDataKL6771

DataKL6771

The data structure with which the KL6771() function block must be linked.

TMpolling

TIME

The time for which the function block should address the actuator. Default 10 s, minimum time 1 s.

MP_EPIV 3: Outputs

VAR_OUTPUT
  bBusy                  : BOOL;
  bError                 : BOOL;
  iErrorId               : MP_Error;
  ActValue               : WORD;
  bMP_Sensor_Digi        : BOOL;
  iMP_Sensor_Analog      : INT;
  Volume_lmin            : WORD;
  iVnom_lmin             : INT;
  act_MaxVol             : INT;
  act_MinVol             : INT;
  bErr_ActHunt           : BOOL;
  bErr_MecTrv            : BOOL;
  bErr_MecOvld           : BOOL;
  bPositionSetByHand     : BOOL;
  bSynchronisationActive : BOOL;
END_VAR

Name

Type

Description

bBusy

BOOL

This bit is set for as long as the function block is active.

bError

BOOL

This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable.

iErrorId

MP_ERROR

This output outputs an error code in the event of an error. bError goes TRUE at the same time.

ActValue

WORD

Contains the current position of the actuator (0..100 %).

bMP_Sensor_Digi

BOOL

If a digital sensor is connected, its state is indicated through this variable. iSensorTyp must be "1".

iMP_Sensor_Analog

INT

If an analog sensor is connected, its value is indicated through this variable. iSensorTyp must be "2...6".

Volume_lmin

WORD

Output of volume flow rate in l/min.

iVnom_lmin

INT

Nominal air volume flow in l/min.

act_MaxVol

INT

Maximum set volume flow rate in %.

act_MinVol

INT

Minimum set volume flow rate in %.

bErr_ActHunt

BOOL

Actuator error, "Regulating oscillation"; the actuator is swinging backwards and forwards.

bErr_MecTrv.

BOOL

Actuator error, "Positioning angle exceeded": the actuator has passed more than 10° beyond the adaptation position.

bErr_MecOvld.

BOOL

Actuator error, "Overload"; the set position could not be reached.

bPositionSetByHand

BOOL

The actuator position was changed manually.

bSynchronisationActive

BOOL

The actuator is synchronizing.

Requirements

Development environment

PLC library to include

TwinCAT from v3.1.4020.32

Tc2_MPBus from 3.4.6.0