MP_JR_Actuator_Configuration
MP_JR_Actuator_Configuration 1:
This function block is used to configure the rotary actuators for butterfly valves JR. Further information can be found at www.belimo.com.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
MP_JR_Actuator_Configuration 2: Inputs
  MP_Address                   : USINT := 1;
  bStart                       : BOOL;
  bRead_Write                  : BOOL;
  strDataKL6771                : DataKL6771;
  nSensor1Type_Write           : E_MP_EV_V4_Sensor1Type;
  nSensor2Type_Write           : E_MP_EV_V4_Sensor1Type;
  nSensor1PassiveType_Write    : E_MP_EV_V4_Sensor1PassiveType;
  nSensor2PassiveType_Write    : E_MP_EV_V4_Sensor1PassiveType;
  nBusFailAction_Write         : E_MP_EV_V4_BusFailAction;
  bSetpointSource_Write        : BOOL;
  nCommunicationWatchdog_Write : UINT := 120;
  rMaximumLimit_Write          : LREAL;
Type
MP_Address
USINT
MP-Bus address of the slave.
bStart
A positive edge starts the function block.
bRead_Write
If FALSE then READ only; if TRUE then READ and WRITE.
strDataKL6771
DataKL6771
The data structure with which the KL6771() function block must be linked.
nSensor1Type_Write
Sensor 1 Type
nSensor2Type_Write
Sensor 2 Type
Only available if nSensor1Type_Write <> MPBus_EV_SensorPassive_None.
Only available if nSensor2Type_Write <> MPBus_EV_SensorPassive_None.
Bus failure action.
TRUE = bus; FALSE = analog
UINT
Communication monitoring in s (5...3600).
rMaximumLimit_Write
LREAL
Maximum limit in % (30..100).
MP_JR_Actuator_Configuration 3: Outputs
  bBusy                  : BOOL;
  bError                 : BOOL;
  iErrorId               : MP_Error;
  nBusFailAction         : E_MP_EV_V4_BusFailAction;
  nCommunicationWatchdog : UINT;
  bSetpointSource        : BOOL;
  rMaximumLimit          : LREAL;
  nSensor1Type           : E_MP_EV_V4_Sensor1Type;
  nSensor2Type           : E_MP_EV_V4_Sensor1Type;
  nSensor1PassiveType    : E_MP_EV_V4_Sensor1PassiveType;
  nSensor2PassiveType    : E_MP_EV_V4_Sensor1PassiveType;
Type
bBusy
This bit is set for as long as the function block is active.
This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable.
iErrorId
MP_ERROR
This output outputs an error code in the event of an error. bError goes TRUE at the same time.
nBusFailAction
Bus failure action.
UINT
Communication monitoring in sec (5...3600).
bSetpointSource
rMaximumLimit
LREAL
Maximum limit in s (30..100).
nSensor1Type
Sensor 1 Type
nSensor2Type
Sensor 2 Type
nSensor1PassiveType
nSensor2PassiveType
Prerequisites
Development Environment
PLC library to include
TwinCAT from v3.1.4024.66
Tc2_MPBus from 3.7.1.0