MC_TorqueControl
MC_TorqueControl 1:
The MC_TorqueControl function block switches an axis under NC control to the “Cyclic Synchronous Torque Mode” (CST) and sets a torque setpoint for it. In this operation mode, the NC also provides the parameterized “VelocityLimitHigh” & “VelocityLimitLow” as linkable objects to the drive controller (Axis->Drive->Outputs->nDataOut5/nDataOut6) in the cyclic interface.
To change the operation mode without jerking, the dead time compensation must be activated in the NC axis.
Supported Beckhoff hardware
AX5xxx
AX8xxx / AMP8xxx / MD8xxx
Compact drive technology (servo)
MC_TorqueControl 2: from FW v2.14 b0001
MC_TorqueControl 3: from FW v1.05 b0001
MC_TorqueControl 4: from FW v01
(ELM72xx and AMI8xxx)
DANGER
Danger to life or risk of serious injury or damage to property due to unintentional movements of the axis
When using the function block, the axis is switched to CST mode. After using the function block (especially after error situations), the axis may still be in CST mode. This can lead to sudden and unplanned movements (especially with lifting axes) when the axis is released.
  • Ensure that there is no hazard as defined by the risk assessment.
  • Check the current operation mode via the function block MC_ReadDriveOperationMode.
  • If the axis is not in a position-related operation mode (CSV/CSP), transfer it before an enable:
    – directly with MC_WriteDriveOperationMode into the desired position-related operation mode (CSV/CSP) or
    – indirectly with MC_Halt / MC_Stop into the desired position-related operation mode (CSV/CSP) (from TwinCAT 3.1.4024.40)
    Other function blocks that switch the axis indirectly into a position-related operation mode can only do this to a limited extent and are therefore not to be used for a deliberate operation mode change.
  • Subsequently, it is necessary to check again whether the axis is really in a position-related operation mode (CSV/CSP), if not, an abort with error handling is required.
For this module to be used effectively, the drive controller must support on-the-fly switching between operating modes and speed limitations in torque mode.
The relevant parameters are available for scaling the actual and setpoint torque in the Drive area in the NC axis parameters.
MC_TorqueControl 5: Inputs
    Execute            : BOOL;
    ContinuousUpdate   : BOOL;
    Relative           : BOOL;
    Torque             : LREAL;
    TorqueRamp         : LREAL;
    VelocityLimitHigh  : LREAL;
    VelocityLimitLow   : LREAL;
    BufferMode         : MC_BufferMode;
    Options            : ST_TorqueControlOptions;
Type
Execute
The command is executed with a rising edge.
ContinuousUpdate
If this input is TRUE on the rising edge at the "Execute" input, the "Torque", "TorqueRamp", "VelocityLimitHigh" and "VelocityLimitLow" inputs can be changed during the execution of the command and made effective as quickly as possible.
Relative
If this input is TRUE, the torque value is changed relatively by the specified value "Torque".
Torque
LREAL
Torque setpoint with which the drive is operated ("Relative" = FALSE) or by which the torque is to be changed ("Relative" = TRUE). (e.g. %)
Here, a positive torque setting means torque in a logically positive direction of movement.
TorqueRamp
LREAL
Rate of change of the torque setpoint ( e.g. %/s)
VelocityLimitHigh
LREAL
Upper velocity limit for limitation in CST mode (e.g. mm/s). This limitation must be configured accordingly in the process image.
VelocityLimitLow
LREAL
Lower velocity limit for limitation in CST mode (e.g. mm/s). This limitation must be configured accordingly in the process image.
BufferMode
MC_BufferMode
Currently only "Aborting" is supported.
Options
Data structure containing additional, rarely used parameters. The input can normally remain open.
See also: General rules for MC function blocks
MC_TorqueControl 6: Inputs/outputs
    Axis : AXIS_REF;
Type
Axis
AXIS_REF
Axis data structure that unambiguously addresses an axis in the system. Among other parameters it contains the current axis status, including position, velocity or error state.
MC_TorqueControl 7: Outputs
    InTorque           : BOOL;
    Busy               : BOOL;
    Active             : BOOL;
    CommandAborted     : BOOL;
    Error              : BOOL;
    ErrorID            : UDINT;
Type
InTorque
TRUE, if the axis has built up the set torque and no velocity limitation is active.
Busy
TRUE as soon as the command is started with Execute and as long as the command is processed. If "Busy" is FALSE, the function block is ready for a new order.
Active
Indicates that the function block controls the axis.
CommandAborted
TRUE if the command could not be executed completely.
Error
TRUE, if an error occurs.
ErrorID
UDINT
If the error output is set, this parameter supplies the error number.
Example MC_TorqueControl for AX8xxx
    Axis_Main              : AXIS_REF;
    bExecute_TorqueControl : BOOL;
    fTorque                : LREAL;
fTorque := 35;
fbTorqueControl(
    Axis               := Axis_Main,
    Execute            := bExecute_TorqueControl,
    ContinuousUpdate   := TRUE,
    Relative           := FALSE,
    Torque             := fTorque,
    TorqueRamp         :=   10,
    VelocityLimitHigh  :=  400,
    VelocityLimitLow   := -500,
    BufferMode         := ,
    Options            := ,
    InTorque           => ,
    Busy               => ,
    Active             => ,
    CommandAborted     => ,
    Error              => ,
    ErrorId            => );
MC_TorqueControl 8:
MC_TorqueControl 9:
Development Environment
Target platform
PLC library to include
TwinCAT v3.1.4024
PC or CX (x86)
Tc2_MC2