FB_DALIV2QueryEmergencyMode
The EMERGENCY MODE variable is read from the control gear.
Bit | Description |
0 | Reset mode. 0: no. |
1 | Emergency mode readiness (normal operation). 0: no. |
2 | Emergency mode. 0: no. |
3 | Extended emergency mode once mains voltage is available again. 0: no. |
4 | Function test active. 0: no. |
5 | Duration test active. 0: no. |
6 | Connected suppress push button is active. 0: not active or not available. |
7 | Connected mains voltage is active. 0: OFF. |
![]() | This command belongs to the application extended commands for DALI emergency lighting. These only work if they are preceded by the Enable Device Type 1 command, which can be sent with the function block FB_DALIV2EnableDeviceType. The Enable Device Type 1 command is internally placed automatically before all application extended commands for DALI emergency lighting. |
bStart : BOOL;
nAddr : BYTE;
bStart | BOOL | The function block is activated by a positive edge at this input. |
nAddr | BYTE | The address of a device or of a group |
eAddrType | Short address, group address or broadcast | |
eCommandPriority | Priority (high, medium or low) with which the command is processed by the library. |
Inputs/outputs
stCommandBuffer | ST_DALIV2CommandBuffer | Reference to the internal structure for communication with FB_KL6811Communication (KL6811) or FB_KL6821Communication (KL6821). |
Outputs
nErrorId : UDINT;
nEmergencyMode : BYTE;
bBusy | BOOL | When the function block is activated the output is set, and it remains active until execution of the command has been completed. |
bError | BOOL | This output is switched to TRUE as soon as an error occurs during the execution of a command. The command-specific error code is contained in nErrorId. Is reset to FALSE by the execution of a command at the inputs. |
nErrorId | UDINT | Contains the command-specific error code of the most recently executed command. Is reset to 0 by the execution of a command at the inputs (see error codes). |
nEmergencyMode | BYTE | Emergency mode (see table above) |
TwinCAT from v3.1.4020.14 | Tc2_DALI from v3.4.3.0 |
