BAC_PID_01
Functional description
The template BAC_PID_01 is a universal PID controller.
The set value, actual value and control output are referenced via the BACnet value objects X, W and Y.
The PID controller is enabled via the input variable bEn.
Interface
Block diagram
bEn : BOOL;
rX : REAL;
rW : REAL;
rSync : REAL;
bSync : BOOL;
bEn: Enable
rX: Actual value
rW: Set value
rSync: Synchronisation value
bSync: Start synchronisation
rY : REAL;
rYMax : REAL;
rYMin : REAL;
rY: Control value output
rYMax: Maximum controller value
rYMin: Minimum controller value
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | Task |
X | The AV object is referenced to the actual value input of the BACnet loop object | |
W | The AV object displays the setpoint of the input rW and is referenced to the setpoint input of the BACnet loop object | |
En | The BV object is used to display the controller enable in the MCL or in a local operator display | |
PID | PID controller | |
rtrigSync | R_TRIG | A rising edge at input bSync triggers synchronization of the loop object to the value of rSync. |
Y | The AV object is referenced to the control value output of the BACnet loop object |
Version history
Version number | Comments |
1.0.1 | First release |