BAC_HW_LglPrev_01
Application
The template provides a protective function for preventing the formation of legionella in the hot water.
The protective function is enabled for a specific timeframe through the switching schedule Sched. In the template the minimum tank temperature rTMin is compared with the set value SpLglPrev, and a charging command bLglPrev and set value rSpLglPrev are issued.
The aim is for the tank temperature to be maintained for a certain time TiLglPrev within the timeframe Sched. If this condition was not met, an alarm is generated AlmLglPrev.
Interface
System diagram
Block diagram
rTMin : REAL;
rTMin: Input minimum tank temperature
bLglPrev : BOOL;
rSpLglPrev : REAL;
bLglPrev: Output request legionella protection
rSpLglPrev: Output set value legionella protection
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | Task |
Sched | Input switching schedule enable legionella prevention | |
TMin | Display of minimum temperature rTMin of hot water tank. | |
SpLglPrev | AV object for entering the setpoint for legionella prevention. | |
HysOn | The two-point switch indicates that legionella prevention is active, depending on the minimum hot water tank temperature rTMin and the setpoint for legionella prevention SpLglPrev. | |
TiLglPrev | AV object for entering the duration of legionella prevention. | |
DlyOn | TON | Timer delay legionella prevention successful. |
RS_Active | RS | Signal latch legionella prevention active |
RS_Done | RS | Signal latch timeframe legionella prevention completed. |
Alm | Logging and further processing of the legionella setpoint alarm not reached | |
AlmLglPrev | Reports legionella setpoint alarm not reached to MCL. | |
OpModPrio | The priority switch prioritizes the legionella prevention operating modes. | |
OpModInd | The BACnet MV object indicates the currently valid operation mode of the legionella protection function. |
Version history
Version number | Comments |
1.0.0.1 | First release |