BAC_ErcIcPrt_02
Functional description
The template is used to protect an energy recovery unit from icing up.
On actuation of the HighLimit of the differential pressure sensor DiffPrssExhMonit a ramp function is activated, which generates an analog limit signal.
The limitation of the energy recovery results in thawing through the warm exhaust air flow.
Interface
System diagram
Block diagram
rY : REAL;
rY: Ramp signal output. If the HighLimit of the differential pressure sensor is not triggered, 100% is output at rY
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | Task |
DiffPrssExhMonit | Differential pressure sensor over the heat exchanger on the exhaust air side | |
RampTi | Input of the rise time of the ramp signal | |
RampFnct | Ramp function, which generates a ramp signal that increases from 0%, if the differential pressure sensor was triggered. | |
RampVal | Display of the ramp signal | |
rtrigRamp | R_TRIG | Specifies the starting value 0% for the ramp function for one cycle, if the differential pressure switch was triggered. |
IO linking
Variables for linking with the terminals
Parameter | Type | optional | Process image |
AI_Differential_Pressure_Sensor | INT |
| Input | Analog input - measured value - differential pressure exhaust air |
Version history
Version number | Comments |
1.0.1 | First release |