Settings
Header
Pos. | Position of the terminal in the terminal block |
Type | Terminal type |
Channel | Channel whose parameters are displayed in the configuration screen |
Firmware | Firmware version of the K-bus PCB |
Configuration screen
In the Settings screen you can set of the behavior of the KL8001 Power Terminal.
Operation mode
Select from the various operation modes here.
Right motion enabled (PR32.0) | Enable for motor rotation to the right. Allows the motor to start rotating to the right using bit 5 in the extended control byte. |
Left motion enabled (PR32.1) | Enable for motor rotation to the left. Allows the motor to start rotating to the left using bit 6 in the extended control byte. |
Watchdog timer active (PR32.2) | Activates the watchdog. If the power terminal does not receive any data from the fieldbus for 100 ms, the watchdog switches the motor off and stops data transmission. |
Single phase analysis (PR32.3) | Activates analysis of the single phases. The phases are each compared with their associated register values, and analyzed individually. If you switch single phase analysis off, then the values entered for phase L1 applies to all three phases. |
Read rotary switches permanently (PR32.5) | In normal operation, the rotary switches for setting the rated current are read continuously. The transfer of modified values does not require a reset. |
Fast shut off
Select here the motor states for which fast shut off should be triggered after 500 ms.
Asymmetric load (PR32.8) | Activates fast shut off if the difference between the currents in L1, L2 or L3 exceeds the maximum permissible current difference. | |
Phase error (PR32.9) | Activates fast shut off if a phase fails. | |
Overvoltage* (PR32.10) | Activates fast shut off in the presence of overvoltage. | *) The voltages of the three phases are measured with reference to an artificial star point. |
Undervoltage* (PR32.11) | Activates fast shut off in the presence of undervoltage. | |
Overload (PR32.12) | Activates fast shut off in the presence of overload. | |
Underload (PR32.13) | Activates fast shut off in the presence of underload. | |
Registerdata
Enter the various threshold values here. The range of values for some of the input fields is restricted (e.g. the rated current must be between 0.0 and 25.0 A), and is automatically limited during input.
Rated current | Specification of the rated current for the L1, L2 and L3 phases. | |
Specification of the switch-on threshold for the L1, L2 and L3 phases. | ||
Specifying the threshold value for overvoltage | *) The voltages of the three phases are measured with reference to an artificial star point. | |
Specifying the threshold value for undervoltage | ||
Specification of the overload thresholds for the L1, L2 and L3 phases. | ||
Specification of the underload thresholds for the L1, L2 and L3 phases. | ||
Max. current difference (PR51) | Specification of the maximum permitted current difference between the L1, L2 and L3 phases. |
Tripping class (PR52) | Specification of the tripping class. |
Measuretime (PR53) | Specification of the measuring cycle time. |