KL8001 Power terminal - Technical data
KL8001 | Power Terminal | |
Number of power terminals per Bus Coupler | 10 max. | If you operate two contactors with each power terminal (reversing contactor connection) then you may only use 5 power terminals with each Bus Coupler. |
Number of contactors per Bus Coupler | 10 max. | |
Type of fastening and mechanical connection | Suitable for Siemens contactors of the Sirius 3RT10 series, size S00 | |
Type of connection power path | Screw terminals for core cross-sections up to 2 x 2.5 mm2 | |
Power path current loading (back-up fuse) | 25 A max. | |
Power path short-circuit strength | up to 5000 A | |
Power path internal resistance | < 1 mΩ | |
Setting range of rated current | via rotary switch: 0.9 A to 9.9 A | |
via KS2000 or parameter registers: 0.9 A to 15.0 A | ||
Selectable tripping classes | CLASS 5, 10, 15, 20, 25, 30 selectable | |
Measured values | Current, voltage, effective power, cos j, energy consumption, switching cycles, operating hours | |
Measuring accuracy (at balanced load) | 0.15 Arms; 2 Vrms; 5 W; 1 kWh | |
Crosstalk between the channels at unbalanced load | up to 3% from the difference | |
Measuring voltage | 500 V | |
Type of K-bus connection | 2 x flat plug socket, 10 pin | |
K-bus current consumption (5 VDC) | typically 150 mA | |
Contactor control voltage current consumption (24 VDC) | When contactor switched off: typically 7 mA | |
When contactor switched on: typically 7 mA + current in the contactor coil | ||
Dielectric strength | 500 V (power contact/K-bus), 6000 V (mains supply/K-bus) | |
Behavior under short-circuit conditions | conforms to EN 60947-4-1 (assignment type 2)/VDE 102 | |
Triggering tolerance | conforms to IEC 947, as well as UL and CSA | |
Configuration options | Automatic over the fieldbus using the KS2000 configuration software, manual (rated current) | |
Width in the process image | 96 bits I/O (see description of the process image) | |
Permissible ambient temperature range during operation | 0°C ... +55°C | |
Permissible ambient temperature range during storage | -25°C ... +85°C | |
Permissible relative air humidity | 95 %, no condensation | |
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 | |
EMC immunity / emission | conforms to EN 61000-6-2 / EN 61000-6-4 | |
Weight | approx. 90 g | |
Dimensions (W x H x D) | approx. 45 mm x 69 mm x 74 mm | |
Mounting | With lugs and connecting pins to Siemens contactors of the 3RT1016 series | |
Installation position | variable (although you must observe the permitted installation positions of the contactors) | |
Protection class | IP20 | |
Approvals/Markings* | CE, UKCA, EAC | |