ELM354x - Technical data
Technical data
ELM3542-0000
ELM3544-0000
Analog inputs
2 channel (differential)
4 channel (differential)
Time relation between channels to each other
Simultaneous conversion of all channels in the terminal (multiplex), synchronous conversion between terminals, if DistributedClocks will be used. Timestamp each channel, typ. sampling offset related to channel 1:
Ch.1: 0 ms
Ch.2: + 200 µs (tbd.)
Ch.1: 0 ms
Ch.2: +200 µs
Ch.3: +400 µs
Ch.4: +600 µs
ADC conversion method
ΔΣ (Delta-Sigma) with internal sample rate 8 Msps
Cutoff frequency input filter hardware
(see explanations in chapter
Firmware filter concept)
Before AD converter:
hardware low pass -3dB @ 380 Hz (16544 kHz for quarter bridge in 4‑wire connection) (tbd.)
type butterworth 1th order
Within ADC after conversion:
low pass -3dB @ 2.75 kHz (tbd.)
type sinc5/average filter or sinc3 (tbd.)
The ramp-up time/ settling time/ delay caused by the filtering will be considered within the DistributedClocks-Timestamp.
Resolution
24 bit (including sign)
Connection technology
2/3/4/5/6/7 -wire
2/3/4/5/6 -wire
Sampling rate (per channel, multiplex)
1 ms/1 ksps
Free down sampling by Firmware via decimation factor, possible effective sampling interval each channel: 1 ms + n ⋅ 25 μs (tbd.)
Oversampling
1…20 selectable
Supported EtherCAT cycle time
(depending on the operation mode)
DistributedClocks: min. 100 µs, max. 10 ms (tbd.)
FrameTriggered/Synchron: min. 200 µs, max. 100 ms (tbd.)
FreeRun: not yet supported
Operation range SG
Quarter bridge (1 kΩ, 350 Ω, 120 Ω) with internal bridge extension,
half bridge, full bridge, voltage measurement, resistance measurement (tbd.)
Connection diagnosis
preliminary data/ provided is:
Channel-by-channel open-circuit detection of the connection cables (running operation or triggered diagnosis, up to 6‑wires)
Channel by channel short-circuit detection of all lines among each other (triggered diagnosis, up to 6 lines)
Additional process data and diagnostic evaluation of the connected sensor via TEDS interface
Internal analog ground AGND
Existing by external connection to -Uv
Overvoltage protection of the inputs related on ‑Uv (internal ground)
value to follow
Internal power supply
via E-bus
Current consumption E-bus
typ. 85 mA tbd.
Current consumption power contacts
60 mA typ. + load, in total, max. 150 mA typ.
70 mA typ. + load, in total, max. 240 mA typ.
Thermal power dissipation
typ. 3 W
Dielectric strength - destruction limit
Max. permitted short-term/continuous voltage between each contact point ±I1, ±I2, +Uv and –Uv: non-supplied ±30V (tbd.) supplied ±30V (tbd.)
Note: -Uv corresponds to internal AGND
Recommended operation voltage range to compliance with specification
value to follow
Common data
ELM3542-0000
ELM3544-0000
Distributed Clocks
Yes, with Oversampling n = 1…100, accuracy << 1 μs
Special features
Extended Range 107 %, freely configurable numeric filters, TrueRMS, integrator/differentiator, non-linear scaling, PeakHold
Bridge feeding-in supply-voltage free adjustable 1.5 V – 12 V (electronic overload protection per channel 120 mA)
2-wire TEDS-Interface (IEEE 1451.4 Class 2 MMI, Multiplex-operation)
externe Shunt-calibration possible
Bridge feeding-in supply-voltage free adjustable 1.5 V – 12 V (electronic overload protection per channel 65 mA)
Functional diagnosis 1)
Yes
Electrical isolation channel/channel 2)
no
Electrical isolation channel/E-Bus 2)
Functional insulation, 707 V DC (type test)
Electrical isolation channel/SGND 2)
Configuration
via the EtherCAT Master, e.g. TwinCAT
Note to cable length
Signal cable lengths to the sensor / encoder over 3 m must be shielded, the shield design must be in line with the state of the art and be effective. For larger cable lengths > 30 m, a suitable surge protection should be provided if appropriate interference could affect the signal cable.
1) see chapters Self-test and self-test report and Connection test/switchable connection diagnosis
2) see notes to potential groups within chapter Power supply, potential groups
Basic mechanical properties
ELM3542-0000
ELM3544-0000
Connection type
6-pin. PushIn spring-loaded technology, service plug
Dimensions (W x H x D)
See chapter Housing
Mounting
on 35 mm rail conforms to EN 60715
Note Mounting
Plug partly not within scope of delivery, see chapter
Notes on connection technology
Weight
Approx. 350 g
Permissible ambient temperature range during operation
0…+55 °C
Permissible ambient temperature range during storage
-25…+85 °C
Environmental data
ELM3542-0000
ELM3544-0000
Permissible operating altitude range
0 up to 2000 m (derating at higher altitudes on request)
Relative humidity
max. 95%, no condensation
Protection class
IP 20
Installation position
Variable
Normative data
ELM3542-0000
ELM3544-0000
Vibration-/shock resistance
Conforms to EN 60068-2-6 / EN 60068-2-27
EMC-resistance / emission
Conforms to EN 61000-6-2 / EN 61000-6-4
Approvals/ markings *)
CE, UKCA, EAC
EMC notes
In case of the "PushIn" connector, ESD air discharges conforming to EN 61000-6-4 into the connectors or to the lines connected there can lead to measurement deviations up to ±FSV within the respective channel or to other channels by crosstalk.
Surge voltages/surges in accordance with EN 61000-6-2 in the Up supply (power contact) when the "Connect Up- to GNDA" or "Connect Up- to AGND" connection is set in the CoE (F800:01) can lead to measurement deviations of up to ±MBE.