ELM310x - Technical data
Technical data
ELM3102-00x0
ELM3104-00x0
Analog inputs
2 channel (differential)
4 channel (differential)
Time relation between channels to each other
Simultaneous conversion of all channels in the terminal, synchronous conversion between terminals, if Distributed Clocks will be used
ADC conversion method
ΔΣ (Delta-Sigma) with internal sample rate
5.12 Msps
8 Msps
Cutoff frequency input filter hardware
(see explanations in chapter
Firmware filter concept)
Before AD converter:
hardware low pass -3 dB @ 30 kHz
type butterworth 3th order
Within ADC after conversion:
Low pass
-3 dB @ 5.3 kHz, ramp-up time 150 µs
Low pass
-3 dB @ 2.6 kHz, ramp-up time 300 µs
Type sinc3/average filter
The ramp-up time/ settling time/ delay caused by the filtering will be considered within the Distributed Clocks-Timestamp.
Resolution
24 bit (including sign)
Connection technology
2‑wire
Sampling rate (per channel, simultaneous)
50 µs/20 ksps
100 µs/10 ksps
Free down sampling by Firmware via decimation factor
Oversampling
1…100 selectable
Supported EtherCAT cycle time
(depending on the operation mode)
Distributed Clocks: min. 100 µs, max. 10 ms
FrameTriggered/Synchron: min. 200 µs, max. 100 ms
FreeRun: not yet supported
Connection diagnosis
No; recommended: 4…20 mA measuring range
Internal analog ground AGND
Existing by external connection to -Uv
Overvoltage protection of the inputs related on ‑Uv (internal ground)
+IN1, -IN1: at approx. 12 ±0.5 V
Internal power supply
via E-bus
Current consumption E-bus
typ. 340 mA
typ. 490 mA
Current consumption power contacts
Thermal power dissipation
typ. 3 W
Dielectric strength - destruction limit
Max. permitted short-term/continuous voltage between each contact points ±I1, ±I2, +Uv and –Uv: non-supplied ±40 V, supplied ±36 V
Note: -Uv corresponds to internal AGND
Recommended operation voltage range to compliance with specification
Max. permitted voltage during specified normal operation between ±I1 and ±I2: typ. ±10 V against –Uv
Common data
ELM3102-00x0
ELM3104-00x0
Distributed Clocks
Yes, with Oversampling n = 1…100, accuracy << 1 μs
Special features
Extended Range 107 %, freely configurable numeric filters, TrueRMS, integrator/differentiator, non-linear scaling, PeakHold
Functional diagnosis 1)
Yes
Electrical isolation channel/channel 2)
no
Electrical isolation channel/E-Bus 2)
Functional insulation, 707 V DC (type test)
Electrical isolation channel/SGND 2)
Configuration
via the EtherCAT Master, e.g. TwinCAT
Note to cable length
Signal cable lengths to the sensor / encoder over 3 m must be shielded, the shield design must be in line with the state of the art and be effective. For larger cable lengths > 30 m, a suitable surge protection should be provided if appropriate interference could affect the signal cable.
1) see chapters Self-test and self-test report and Connection test/switchable connection diagnosis
2) see notes to potential groups within chapter Power supply, potential groups
Basic mechanical
properties
ELM3102-00x0
ELM3104-00x0
Connection type
2-pin. PushIn spring-loaded technology, service plug
Dimensions (W x H x D)
See chapter Housing
Mounting
on 35 mm rail conforms to EN 60715
Note Mounting
Plug partly not within scope of delivery, see chapter
Notes on connection technology
Weight
Approx. 350 g
Permissible ambient temperature range during operation
-25…+60 °C
Permissible ambient temperature range during storage
-40…+85 °C
Environmental data
ELM3102-00x0
ELM3104-00x0
Permissible operating altitude range
0 up to 2000 m (derating at higher altitudes on request)
Relative humidity
max. 95%, no condensation
Protection class
IP 20
Installation position
Variable
Normative data
ELM3102-00x0
ELM3104-00x0
Vibration-/shock resistance
Conforms to EN 60068-2-6 / EN 60068-2-27
EMC-resistance / emission
Conforms to EN 61000-6-2 / EN 61000-6-4
Approvals/ markings *)
CE, UKCA, cULus_60, EAC
EMC notes
In case of the "PushIn" connector, ESD air discharges conforming to EN 61000-6-4 into the connectors or to the lines connected there can lead to measurement deviations up to ±FSV within the respective channel or to other channels by crosstalk.
Peak voltages (surge) conforming to EN 61000-6-2 that are applied to the cable shield can lead to measurement deviations up to ±FSV.
