ELM310x - Technical data
Technical data | ELM3102-00x0 | ELM3104-00x0 |
Analog inputs | 2 channel (differential) | 4 channel (differential) |
Time relation between channels to each other | Simultaneous conversion of all channels in the terminal, synchronous conversion between terminals, if DistributedClocks will be used | |
ADC conversion method | ΔΣ (Delta-Sigma) with internal sample rate | |
5.12 Msps | 8 Msps | |
Cutoff frequency input filter hardware | Before AD converter: Within ADC after conversion: | |
Low pass | Low pass | |
Type sinc3/average filter The ramp-up time/ settling time/ delay caused by the filtering will be considered within the DistributedClocks-Timestamp. | ||
Resolution | 24 bit (including sign) | |
Connection technology | 2‑wire | |
Sampling rate (per channel, simultaneous) | 50 µs/20 ksps | 100 µs/10 ksps |
Free down sampling by Firmware via decimation factor | ||
Oversampling | 1…100 selectable | |
Supported EtherCAT cycle time (depending on the operation mode) | DistributedClocks: min. 100 µs, max. 10 ms FrameTriggered/Synchron: min. 200 µs, max. 100 ms FreeRun: not yet supported | |
Connection diagnosis | No; recommended: 4…20 mA measuring range | |
Internal analog ground AGND | Existing by external connection to -Uv | |
Overvoltage protection of the inputs related on ‑Uv (internal ground) | +IN1, -IN1: at approx. 12 ±0.5 V | |
Internal power supply | via E-bus | |
Current consumption E-bus | typ. 340 mA | typ. 490 mA |
Current consumption power contacts | - | |
Thermal power dissipation | typ. 3 W | |
Dielectric strength - destruction limit | Max. permitted short-term/continuous voltage between each contact points ±I1, ±I2, +Uv and –Uv: non-supplied ±40 V, supplied ±36 V Note: -Uv corresponds to internal AGND | |
Recommended operation voltage range to compliance with specification | Max. permitted voltage during specified normal operation between ±I1 and ±I2: typ. ±10 V against –Uv Note: -Uv corresponds to internal AGND | |
Common data | ELM3102-00x0 | ELM3104-00x0 |
Distributed Clocks | Yes, with Oversampling n = 1…100, accuracy << 1 μs | |
Special features | Extended Range 107 %, freely configurable numeric filters, TrueRMS, integrator/differentiator, non-linear scaling, PeakHold | |
Functional diagnosis 1) | Yes | |
Electrical isolation channel/channel 2) | no | |
Electrical isolation channel/E-Bus 2) | Functional insulation, 707 V DC (type test) | |
Electrical isolation channel/SGND 2) | Functional insulation, 707 V DC (type test) | |
Configuration | via the EtherCAT Master, e.g. TwinCAT | |
Note to cable length | Signal cable lengths to the sensor / encoder over 3 m must be shielded, the shield design must be in line with the state of the art and be effective. For larger cable lengths > 30 m, a suitable surge protection should be provided if appropriate interference could affect the signal cable. | |
1) see chapters Self-test and self-test report and Connection test/switchable connection diagnosis
2) see notes to potential groups within chapter Power supply, potential groups
Basic mechanical | ELM3102-00x0 | ELM3104-00x0 |
Connection type | 2-pin. PushIn spring-loaded technology, service plug | |
Dimensions (W x H x D) | See chapter Housing | |
Mounting | on 35 mm rail conforms to EN 60715 | |
Note Mounting | Plug partly not within scope of delivery, see chapter | |
Weight | Approx. 350 g | |
Permissible ambient temperature range during operation | -25…+60 °C | |
Permissible ambient temperature range during storage | -40…+85 °C | |
Environmental data | ELM3102-00x0 | ELM3104-00x0 |
Permissible operating altitude range | 0 up to 2000 m (derating at higher altitudes on request) | |
Relative humidity | max. 95%, no condensation | |
Protection class | IP 20 | |
Installation position | Variable | |
Normative data | ELM3102-00x0 | ELM3104-00x0 |
Vibration-/shock resistance | Conforms to EN 60068-2-6 / EN 60068-2-27 | |
EMC-resistance / emission | Conforms to EN 61000-6-2 / EN 61000-6-4 | |
Approvals/ markings *) | CE, UKCA, cULus_60, EAC | |
EMC notes | In case of the "PushIn" connector, ESD air discharges conforming to EN 61000-6-4 into the connectors or to the lines connected there can lead to measurement deviations up to ±FSV within the respective channel or to other channels by crosstalk. Peak voltages (surge) conforming to EN 61000-6-2 that are applied to the cable shield can lead to measurement deviations up to ±FSV. | |