ELM360x - Technical data
Technical data
ELM3602-000x
ELM3604-000x
Analog inputs
2 channel (single-ended)
4 channel (single-ended)
Time relation between channels to each other
Simultaneous conversion of all channels in the terminal, synchronous conversion between terminals, if Distributed Clocks will be used
ADC conversion method
ΔΣ (Delta-Sigma) with internal sample rate
8 Msps
5.12 Msps
Cutoff frequency input filter hardware
(see explanations in chapter
Firmware filter concept)
Before AD converter:
hardware low pass -3 dB @ 30 kHz
type butterworth 3th order
Within ADC after conversion:
Low pass
-3 dB @ 13.6 kHz, ramp-up time 60 µs
Low pass
-3 dB @ 5.3 kHz, ramp-up time 150 µs
Type sinc3/average filter
The ramp-up time/ settling time/ delay caused by the filtering will be considered within the Distributed Clocks-Timestamp.
Resolution
24 bit (including sign)
Connection technology
2‑wire
Sampling rate (per channel, simultaneous)
20 µs/50 ksps
50 µs/20 ksps
Free down sampling by Firmware via decimation factor
Oversampling
1…100 selectable
Supported EtherCAT cycle time
(depending on the operation mode)
Distributed Clocks: min. 100 µs, max. 10 ms
FrameTriggered/Synchron: min. 200 µs, max. 100 ms
FreeRun: not yet supported
Operation range IEPE
Measuring ranges ±20/40/80/160/320/640 mV, ±1.25/2.5/5/10 V adjustable,
Current supply/ IEXCITE (IEPE Bias Current) 0/2/4 mA,
Acquisition of the modulated alternating voltage,
AC/DC coupling (parameterizable high pass),
2-wire-connection
Operation range voltage measurement
±10/5/2.5/1.25 V, ±640/320/160/80/40/20 mV, 0…10/20 V 1)
2-wire-connection
Connection diagnosis
Wire break/short cut
Internal analog ground AGND
Existing by external connection to -Uv
Overvoltage protection of the inputs related on ‑Uv (internal ground)
+Input1: at > +24 V and < -8 V respectively
Internal power supply
via E-bus
Current consumption E-bus
typ. 460 mA
typ. 650 mA
Current consumption power contacts
Thermal power dissipation
typ. 3 W
Dielectric strength - destruction limit
Max. permitted short-term/continuous voltage
Voltage between each contact point ±I1, ±I2, +Uv and –Uv: non-supplied ±40 V, supplied ±36 V
Voltage between every contact point and SGND (shield, mounting rail): ±36 V
Note: -Uv corresponds to internal AGND
Recommended operation voltage range to compliance with specification
Max. permitted voltage during specified normal operation
±I1 and ±I2: typ. ±10 V against –Uv,
for ELM360x: related to GND: -5...+21.5 V
1) The ELM360x can measure the range from -5 V to +21.5 V related to GND.
Common data
ELM3602-000x
ELM3604-000x
Distributed Clocks
Yes, with Oversampling n = 1…100, accuracy << 1 μs
Special features
Extended Range 107 %, freely configurable numeric filters, TrueRMS, integrator/differentiator, non-linear scaling, PeakHold
Functional diagnosis 1)
Yes
Electrical isolation channel/channel 2)
no
Electrical isolation channel/E-Bus 2)
Functional insulation, 707 V DC (type test)
Electrical isolation channel/SGND 2)
Configuration
via the EtherCAT Master, e.g. TwinCAT
Note to cable length
Signal cable lengths to the sensor / encoder over 3 m must be shielded, the shield design must be in line with the state of the art and be effective. For larger cable lengths > 30 m, a suitable surge protection should be provided if appropriate interference could affect the signal cable.
1) see chapters Self-test and self-test report and Connection test/switchable connection diagnosis
2) see notes to potential groups within chapter Power supply, potential groups
Basic mechanical properties
ELM3602-000x
ELM3604-000x
Connection type
Variant ELM360x-0000: 2-pin push-in spring-loaded technology, service plug
Variant ELM360x-0002: BNC, shielded
Note: shield is the analog ground, electrically isolated from housing
Dimensions (W x H x D)
See chapter Housing
Mounting
on 35 mm rail conforms to EN 60715
Note Mounting
Plug partly not within scope of delivery, see chapter
Notes on connection technology
Weight
Approx. 350 g
Permissible ambient temperature range during operation
-25…+60 °C
Permissible ambient temperature range during storage
-40…+85 °C
Environmental data
ELM3602-000x
ELM3604-000x
Permissible operating altitude range
0 up to 2000 m (derating at higher altitudes on request)
Relative humidity
max. 95%, no condensation
Protection class
IP 20
Installation position
Variable
Normative data
ELM3602-000x
ELM3604-000x
Vibration-/shock resistance
Conforms to EN 60068-2-6 / EN 60068-2-27
EMC-resistance / emission
Conforms to EN 61000-6-2 / EN 61000-6-4
Approvals/ markings *)
CE, UKCA, cULus_60, EAC
EMC notes
In case of the "PushIn" connector, ESD air discharges conforming to EN 61000-6-4 into the connectors or to the lines connected there can lead to measurement deviations up to ±FSV within the respective channel or to other channels by crosstalk.