ELM324x - Technical data
Technical data |
ELM3244-0000 |
ELM3246-0000 |
Analog inputs |
4 channels |
6 channels |
Time relation between channels |
Consecutive conversion of all channels in the terminal (multiplex) Timestamp per channel, typ. sampling offset related to channel 1: synchronous conversion between terminals when Distributed Clocks is used. | |
Ch.1: 0 μs |
Ch.1: 0 μs | |
ADC conversion method |
ΔΣ (delta-sigma) with internal sampling rate | |
8 Msps |
8 Msps | |
Input filter limit frequency for hardware ELM features/firmware filter concept) |
Before AD converter: Within ADC after conversion: low-pass Type sinc3/average filter The rise time/settling time/delay caused by the filtering will be considered within the Distributed Clocks timestamp. | |
Resolution |
24 bit (including sign) | |
Connection technology |
2-/3-/4-wire | |
Sampling rate (per channel) |
1 ms / 1 ksps Free down sampling by firmware via decimation factor | |
Oversampling |
1...20 can be selected | |
Supported EtherCAT cycle time (dependent on operation mode) |
Distributed Clocks: min. 200 μs + n · 25 μs (n = 0, 1, 2, ..); max. 10 ms FrameTriggered/Synchronous: min. 200μs + n · 25 μs (n = 0, 1, 2, ..); max. 100 ms FreeRun: min. 200 μs + n · 25 μs (n = 0, 1, 2, ..); max. 100 ms | |
Internal resistance |
> 10 MΩ (sense against each other) | |
Resistance measurement application range 3) |
4-wire connection: 0 … 50 Ω 2/3/4-wire connection: 0 … 200 Ω, 0 … 500 Ω, 0 … 2 kΩ, 0 … 5 kΩ | |
Temperature application range (RTD) 3) |
Pt100, Pt200, Pt500, Pt1000, Ni100, Ni120, Ni1000, div. KT/KTY, div. NTC 2/3/4-wire connection | |
Connection diagnosis |
Wire break/short circuit | |
Internal analog ground AGND |
Not accessible | |
Overvoltage protection of the inputs related to AGND |
Not applicable, AGND is not accessible | |
Internal power supply |
Via E-bus | |
Current consumption via E-bus |
Typ. 400 mA |
Typ. 450 mA |
Current consumption of power contacts |
Thermal power loss |
Typ. 2 W |
Typ. 2.5 W |
Dielectric strength – destruction limit |
Max. permitted short-term/continuous voltage between the contact points: ±36 V | |
Recommended operating voltage range for compliance with specification |
Terminal supplies loads itself, do not feed in external power | |
General data | ELM3244-0000 | ELM3246-0000 |
Distributed clocks | Yes, with oversampling, accuracy << 1 μs | |
Special features | Extended range 107 %, freely configurable numeric filters, TrueRMS, integrator/differentiator, non-linear scaling, PeakHold | |
Functional diagnosis 1) | yes | |
Electrical isolation channel/channel 2) | no | |
Electrical isolation channel/E-Bus 2) | Functional insulation, 707 V DC (type test) | |
Electrical isolation channel/SGND 2) | Functional insulation, 707 V DC (type test) | |
Configuration | via the EtherCAT Master, e.g. TwinCAT | |
Note to cable length | Signal cable lengths to the sensor / encoder over 3 m must be shielded, the shield design must be in line with the state of the art and be effective. For larger cable lengths > 30 m, a suitable surge protection should be provided if appropriate interference could affect the signal cable. | |
1) see chapters Self-test and self-test report and Connection test/switchable connection diagnosis
2) see notes to potential groups within chapter Power supply, potential groups
3) 2/3-wire measurement is not yet adapted in the 2025 production status
Basic mechanical properties | ELM3244-0000 | ELM3246-0000 |
Connection type | 6 pin PushIn spring-loaded system, service plug | |
Dimensions (W x H x D) | See chapter Housing | |
Mounting | on 35 mm rail conforms to EN 60715 | |
Note Mounting | Plug partly not within scope of delivery, see chapter | |
Weight | Approx. 350 g | |
Permissible ambient temperature range during operation | 0…+55 °C | |
Permissible ambient temperature range during storage | -25…+85 °C | |
Environmental data | ELM3244-0000 | ELM3246-0000 |
Permissible operating altitude range | 0 to 2000 m (derating at higher altitudes on request) | |
Relative humidity | Max. 95 %, no condensation | |
Protection rating | IP20 | |
Installation position | variable | |
Normative information | ELM3244-0000 | ELM3246-0000 |
Vibration/shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 | |
EMC immunity/emission | conforms to EN 61000-6-2 / EN 61000-6-4 | |
Approvals/markings *) | CE, UKCA, EAC | |
EMC notes | In case of the "PushIn" connector, ESD air discharges conforming to EN 61000-6-4 into the connectors or to the lines connected there can lead to measurement deviations up to ±FSV within the respective channel or to other channels by crosstalk. Peak voltages (surge) conforming to EN 61000-6-2 that are applied to the cable shield can lead to measurement deviations up to ±FSV. | |