Technical data
Technical data | EL9221-5000 | EL9221-6000 | EL9221-4030 | EL9221-6040 | EL9221-9060 | EL9221-9080 | EL9221-5090 |
Nominal voltage | 24 VDC (-15 %/+20 %) | ||||||
Nominal current | max. 10 A, adjustable | max. 4 A, adjustable | 3 A, fixed | 4 A, fixed | 6 A, fixed | 8 A, fixed | 10 A, fixed |
Nominal current steps | 1, 2, 3, 4, 5, 6, 7, 8, 9, 10 A | 1, 2, 3, 4 A |
Input current | max. 10 A (Input current = forwarding current + current of the own terminal), see note | ||||||
Number of outputs | 1 | ||||||
Output 1 | Terminal contact and power contact | ||||||
Power contacts (right) | +24 V DC protected; 0 V DC | ||||||
Number of digital inputs | 1 (24V DC falling edge -15% + 20%); same 0 V reference as input voltage | ||||||
Prewarning output load | Fixed 90%, 5% hysteresis | ||||||
Tripping behavior | |||||||
Restart time | ≥ 10 seconds**) | ||||||
Internal fuse (faile-safe element) | 15 A (F) | 6 A (T) | 4 A (T) | 6 A (T) | 10 A (F) | 10 A (F) | 15 A (F) |
Internal max. power dissipation limitation | typically 400 W for 20 ms | typically 160 W for 50 ms | typically 160 W for 50 ms | typically 160 W for 50 ms | typically 266 W for 30 ms | typically 266 W for 30 ms | typically 400 W for 20 ms |
Max. current limitation | typically 25 A for 20 ms | typically 10 A for 50 ms | typically 10 A for 50 ms | typically 10 A for 50 ms | typically 16 A for 30 ms | typically 16 A for 30 ms | typically 25 A for 20 ms |
Delay time | typical 15 ms**) | ||||||
Overcurrent protection operation without E-bus | Yes | ||||||
Switch-on capacitance | typically 20,000 µF***) | ||||||
Overvoltage shutdown | > 32 V DC | ||||||
Parallel connection of several outputs | not permissible | ||||||
E-Bus current consumption | typ. 80 mA | ||||||
Electrical connection to mounting rail | Yes | ||||||
Measuring error | typ. ± 100 mA @23°C+- 20°C @24 V | ||||||
Electrical isolation | 500 V (E-bus/signal voltage) | ||||||
Dimensions (W x H x D) | approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm) | ||||||
Weight | approx. 60 g | ||||||
Permissible ambient temperature range during operation | 0°C ... + 55°C | ||||||
Permissible ambient temperature range during storage | -25°C ... + 85°C | ||||||
Permissible relative air humidity | 95 %, no condensation | ||||||
Mounting | on 35 mm mounting rail according to EN 60715 | ||||||
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 | ||||||
EMC immunity / emission | conforms to EN 61000-6-2 / EN 61000-6-4 | ||||||
Installation position | see note! | ||||||
Protection class | IP20 | ||||||
Markings / Approvals*) | CE, EAC, UKCA |
**) for further explanations see note in chapter Commissioning
***) depending on: installed power supply, line resistance, load current, component tolerances, selected current range
Technical data | EL9222-5500 | EL9222-6600 | EL9222-4433 | EL9222-6644 | EL9222-9664 | EL9222-9482 |
Nominal current | Max. Ʃ10 A | max. 4 A, adjustable | 3 A / 3 A, | 4 A / 4 A, | 6 A / 4 A, | 8 A / 2 A, |
Nominal current steps | 1, 2, 3, 4, 5, 6, | 1, 2, 3, 4 A |
Number of outputs | 2 | |||||
Number of digital inputs | 2 (24V DC falling edge -15% + 20%); same 0 V reference as input voltage | |||||
Internal fuse (faile-safe element) (channel1/channel2) | 15 A (F) / | 6 A (T) / | 4 A (T) / | 6 A (T) / | 10 A (F) / | 10 A (F) / |
Internal max. power dissipation limitation | typically 400 W for 20 ms / | typically 160 W for 50 ms / typically 160 W for 50 ms | typically 160 W for 50 ms / typically 160 W for 50 ms | typically 160 W for 50 ms / typically 160 W for 50 ms | typically 266 W for 30 ms / | typically 266 W for 30 ms / |
Max. current limitation | typically 25 A for 20 ms / | typically 10 A for 50 ms / | typically 10 A for 50 ms / | typically 10 A for 50 ms / | typically 16 A for 30 ms / | typically 16 A for 30 ms / |
Technical data | EL9227-5500 | EL9227-6600 | EL9227-4433 | EL9227-6644 | EL9227-9664 | EL9227-9482 |
Nominal current | Max. Ʃ10 A, adjustable | Max. 4 A, adjustable | 3 A / 3 A, fixed | 4 A / 4 A, fixed | 6 A / 4 A, fixed | 8 A / 2 A, fixed |
Input current | max. 10 A (Input curr. = forwarding curr. + curr. of the own terminal), see note | |||||
Prewarning output load | Adjustable between 50% and 100%, 5% hysteresis | |||||
Restart time | ≥ 10 seconds (temperature-dependent)**) | |||||
Internal fuse (faile-safe element) (channel1/channel2) | 15 A (F) / 15 A (F) | 6 A (T) / 6 A (T) | 4 A (T) / 4 A (T) | 6 A (T) / 6 A (T) | 10 A (F) / 6 A (T) | 10 A (F) / 4 A (T) |
Internal max. power dissipation limitation and tripping time | typically 400 W for 20 ms / | typically 160 W for 50 ms / typically 160 W for 50 ms | typically 160 W for 50 ms / typically 160 W for 50 ms | typically 160 W for 50 ms / typically 160 W for 50 ms | typically 266 W for 30 ms / | typically 266 W for 30 ms / |
Max. current limitation | typically 25 A for 20 ms / typically 25 A for 20 ms | typically 10 A for 50 ms / typically 10 A for 50 ms | typically 10 A for 50 ms / typically 10 A for 50 ms | typically 10 A for 50 ms / typically 10 A for 50 ms | typically 16 A for 30 ms / typically 10 A for 50 ms | typically 16 A for 30 ms / typically 10 A for 50 ms |
Overcurr. prot. operation without E-bus | Yes | |||||
Switch-on capacitance | typically 20,000 µF****) | |||||
Undervoltage prewarning | Adjustable between 17 and 24 V DC | |||||
Reverse polarity switch-off | Yes | |||||
Reverse feed shutdown | UOut + 1 V > UIn | |||||
Open load detection | Yes* | |||||
Measuring error | typ. ± 75 mA @23°C+- 20°C @24 V | |||||
typ. ± 150 mV @23°C+- 20°C @24 V | ||||||
X * IN | Current | fast | standard | slow |
| t / in ms | ||
1.1 |
| 7,000 | 10,000 | 15,000 |
1.2 |
1.3 |
| 3,500 | 5,000 | 7,500 |
1.4 |
1.5 |
| 700 | 1,000 | 1,500 |
1.6 |
1.7 |
1.8 |
| 70 | 100 | 150 |
1.9 |
| 70 | 100 | 150 |
≥ 2 | Max. typ. 25 A*** | 1 | 8 | 12 |
| t / in ms | ||
1.1 |
1.2 |
1.3 |
1.4 |
1.5 |
1.6 |
1.7 |
1.8 |
| 70 | 100 | 150 |
1.9 |
| 70 | 100 | 150 |
≥ 2 | Max. typ. 16 A*** | 1 | 8 | 12 |
| t / in ms | ||
1.1 |
1.2 |
1.3 |
1.4 |
1.5 |
1.6 |
1.7 |
1.8 |
| 70 | 100 | 150 |
1.9 |
| 70 | 100 | 150 |
≥ 2 | Max. typ. 10 A*** | 1 | 8 | 12 |
*) only “standard” for these variants |
**) max. tolerance: <= 100 ms = +-4ms; >100 ms = +- 2 % |
***) tripping times above max. current see technical data internal max power/current limitation |
