Basic function principles
The EL6080 supports 2 methods of accessing the memory: with cyclic process data and via acyclic SDO/CoE access. The memory can be deleted, for example, in further settings.
Delivery state
The EL6080 is delivered ready for operation with no predefined acyclic data structures.
Basic function principles 1:
General information on data consistency
The EL6080 can be used for the failsafe storage of cyclic machine data.  A corresponding feedback message in Status (cyclic operation) confirms that the data has been adopted correctly by the EL6080. The data must appear correctly in the CoE in acyclic operation mode.
An operational case may occur where the terminal is switched off or the task is stopped during (a)cyclic access for writing. In this case, shadow buffers or the NOVRAM in the EL6080 ensure data consistency at the lowest level, so that the last correctly written data set can always be accessed. At application level, however, the user must take care himself through appropriate use that the application adopts consistent data, for example, at the start (e.g. continuous counters or ID recognition in the data to be saved).
Sample:
Several acyclic data objects are defined from 1 to 3 that are continuously written to by the application in sequence, e.g. 3 axis positions that are determined simultaneously in the application. The power fails during access for writing to object 2. Object 1 now contains the current axis position 1, but objects 2 & 3 contain outdated positions. At restart, the application must not assume that it is receiving 3 axis positions originating from the same point in time.
The same side effects must be taken into account in the case of simultaneous operation of the EL6080 and Persistent/Retain/Other NOVRAM data (e.g. from FC cards or CX).
Basic function principles 2:
Readiness for operation of the EL6080
It is imperative that you ensure in your application that the terminal has a valid WorkingCounter WcState before beginning with writing and, in particular, reading communication! Process data delivered by an EtherCAT slave when the WcState is ≠ 0 (even if the data is ≠0) must be discarded as invalid!
Basic function principles 3:
CoE directory EL6080
The functionality of the EL6080 results in CoE objects being deleted or created during reparameterisation. Please refer to the notes in order to ensure correct online CoE display.
Basic function principles 4:Fig.133: Default process image of the EL6080 after insertion
Status word
The status word (SW) is in the input process image and is transferred from the terminal to the controller.
Bit
SW.15
SW.14
SW.13
SW.12
SW.11
SW.10
SW.9
SW.8
Acyclic mode, 4-bit counter is incremented for each successful save
Bit
SW.7
SW.6
SW.5
SW.4
SW.3
SW.2
SW.1
SW.0
Cyclic operation with handshake, "Writing Started"
Control word
The control word (CW) is in the output process image and is transferred from the controller to the terminal.
Bit
CW.15
CW.14
CW.13
CW.12
CW.11
CW.10
CW.9
CW.8
Bit
CW.7
CW.6
CW.5
CW.4
CW.3
CW.2
CW.1
CW.0
Cyclic operation with handshake, "Start Writing"
Data traffic with cyclic process data
The user can create one set of process data with an arbitrary structure, max. 1280 bytes. This data set can be written cyclically in its entirety to the terminal or read by it. Individual access to the constituent parts of this data set is not possible (keyword: addressing). Control is effected by the task by means of a handshake via Control/Status Word, so that several task cycles may be necessary for saving or reading back, depending on the extent of the data and the cycle time.
When the EL6080 is switched on, the regularly saved data from the last operating session is offered immediately via the inputs for reading in.
Commissioning: The cyclic process image must be created identically at inputs and outputs, max. 1280 bytes. Creation by right-clicking Inputs/Outputs.
Basic function principles 5:Fig.134: Manual creation of the cyclic process data
If the input and output are created with different sizes, the terminal start-up fails: “PREOP to SAFEOP failed”.
If more than 1280 bytes are created, the terminal start-up fails with “Invalid SM In/Out Cfg”.
Basic function principles 6:
Structure of the process data in TwinCAT 2.10
The structure of the Input/Output data is subject to the following restriction up to TwinCAT 2.10 build 1330: all defined variables must be composed of n*bytes; individual bits or such types of composed structures are not permissible. If such data is defined, the EL6080 attains the OP state, but reports an error due to Working Counter = 1.
Samples:
Basic function principles 7:Fig.135: Permissible configurations
Basic function principles 8:Fig.136: Impermissible configuration up to TwinCAT b2.10 b1330
Cyclic operation with handshake, recommended operating sequence:
  1. Output the input data to the terminal; set ControlWord = 1.
  2. Once the terminal has successfully adopted the data, StatusWord = 1 is returned.
  3. Set ControlWord = 0.
  4. Wait until StatusWord = 0 is returned; the terminal is then ready for a new write access operation.
Basic function principles 9:Fig.137: Cyclic operation with handshake
Typical example of a measurement for a cyclic write process according to the sequence described above (Beckhoff reserves the right to make unannounced amendments):
Basic function principles 10:
Process data image and frame length
In the case of short cycle times, an extensive process image for the EL6080 can result in an Ethernet frame that is longer than the cycle time. Therefore, in order to use the entire 1280 bytes of the cyclic process image, the cycle time must be at least >= 200 µs.
Data traffic with acyclic CoE access
In acyclic access, the user can create up to 255 memory objects that may also be differently sized. These objects can be specifically accessed from the PLC task via acyclic SDO access (Service Data Objects) for writing or reading; see sample program. This read/write access proceeds considerably slower than the above-described cyclic memory access.
The created structure can only be changed in the terminal status PREOP. It can also be generally locked to prevent further changes.
Background information: the entire memory capacity is administered in the form of CoE objects (CAN over EtherCAT). The administration data (number and byte size) is located in the Object Index 0x2F00 with its subindexes; the stored data itself in the CoE objects from 0x2000: 0x2000, 0x2008, 0x2010, 0x2018 etc.
A memory object in acyclic access can comprise 1 to 8190 bytes.
The following procedure is recommended in order to use acyclic access:
Calculation of the memory space
The available 128 KB (131,072 bytes) of memory are subdivided as follows:
Sample: The acyclic memory objects Obj1, Obj2 and Obj3 are defined with 1,000, 3,000 and 7,000 bytes respectively --> x = 11,000 bytes and y = 7,000 bytes. Thus 113,072 bytes of memory space remain.
Definition of the memory objects via the StartUp list
The desired structure of the memory objects must be created once only in the status PREOP in the CoE directory in CoE object 0x2F00. This is also possible offline in the System Manager (without a terminal being connected). At start-up, the EL6080 checks whether the memory structure has changed and if necessary creates the objects in the memory accordingly.
Basic function principles 11:
Change in the data structure
If the data structure or the object 0x2F00 is changed, all existing data in the EL6080 is deleted. The data structure can be locked to prevent it being changed by setting the lock object 0xF200:02.
Procedure in short:
  1. Set Locked in CoE object 0xF200:02 = 0 (set manually in the System Manager or via PLC).
  2. Enter the StartUp command for the CoE object 0x2F00
    Contents: Number of objects + respective lengths in bytes.
    To be observed: complete access, byte alignment, no empty objects possible, only possible in P -> S transition, 16 bit entries, max. 127 memory objects.
  3. Reloading the configuration.
  4. For checking: reload the CoE directory.
  5. Set Locked in CoE object 0xF200:02 = 1 (set manually in the System Manager or via PLC), thus locking the structure to prevent further changes.
Procedure in detail:
The procedure to specify the structure of the memory objects as required by the user is as follows:
Basic function principles 12:Fig.138: Variable start state of the EL6080
Following start-up, the EL6080 contains either an already changed memory structure or the default memory structure. The CoE objects from 0x2000 and 0x2F00 are important in the following. Fig. Variable start state of the EL6080 shows in the EL6080 an object of size 1 byte:
The EL6080 should now be reconfigured to the memory structure
i.e. a total of 270 bytes in 4 memory objects, which can each be accessed acyclically via the CoE. A corresponding entry for this must be made in the EL6080’s StartUp list. This list is empty in the EL6080 in the default state.
Basic function principles 13:Fig.139: Addition of a new StartUp entry
This is achieved via New.. in the EL6080 StartUp tab.
Basic function principles 14:Fig.140: Definition of the StartUp entry
A window opens in which the new StartUp entry can be defined.
Basic function principles 15:
StartUp list selection dialog
If no CoE entries are offered (see Fig. Definition of the startup entry), the reason is as follows: you are working offline (i.e. with no live terminal connected) and there is no dictionary in the ESI (EtherCAT Slave Information, XML description) of the EL6080 that you are using.
In this case you can also define StartUp entries entirely manually, i.e. enter Index and Subindex manually.
Sample:
Confirm with OK. The new StartUp entry looks like this:
Basic function principles 16:Fig.141: New EL6080 StartUp entry
This configuration must now be loaded to the EL6080 and, in particular, the status transition PREOP-->SAFEOP must be performed as defined in the Startup entry.
Click the Reload button (Fig. Reload the configuration):
Basic function principles 17:Fig.142: Reload the configuration
The old entry is still visible in the CoE-Online tab.
The reason is that TwinCAT primarily only loads the values of CoE objects that are known to the System Manager. If the CoE structure changes on the device, the System Manager has to be instructed to load the new structure, which may differ from the default structure according to XML/Dictionary.
Load the reconfigured CoE directory (Fig. Complete reload of the CoE directory):
Basic function principles 18:Fig.143: Complete reload of the CoE directory
The newly defined memory objects are now visible and enabled, see Fig. Modified CoE directory.
Basic function principles 19:
Updating the CoE directory
In order to update the display of the CoE directory, use AutoUpdate, UpdateList or the appropriate dialog under Advanced.
Basic function principles 20:Fig.144: Modified CoE directory
Basic function principles 21:
Displaying larger CoE objects
In the sample chosen here, the contents of the 3rd memory object in CoE object 0x2010 are not shown in the TwinCAT display, see fig. Changed CoE directory, because the contents are too large for the display. Regardless of that, the contents naturally exist.
Online access to the memory objects during operation
For access from the PLC, function blocks from the Beckhoff TcEtherCAT.lib such as FB_EcCoESdoWriteEx can be used. A write call in the form
fbWriteCoE(
sNetId:=sAmsNetId,
nSlaveAddr:= tAmsAddr.port ,
nSubIndex:= 0,
nIndex:= 16#2000 + ((byObjectNo - 1) * 8),
pSrcBuf:= pDataForWrite,
cbBufLen:= wSizeOfData,
bExecute:= TRUE,
tTimeout:= tAdsTimeOut,
bCompleteAccess:= FALSE,
bBusy=> ,
bError=> ,
nErrId=> );
is used in the attached sample program (download).
Supplementary settings
Deleting existing data
If the value <BECF6080> is entered in the CoE object ‘Code Word’ (0xF008) , the EL6080 deletes all existing data at the next restart (status transition INIT --> PREOP). The structure of the acyclic data is retained.
This reset also deletes the LOCK in 0xF200:02.
Protecting an acyclic structure against being changed
If the CoE object 0xF200:02 is set to <1>, the structure from CoE object 0x2F00 can no longer be changed.
Basic function principles 22:Fig.145: Lock in the CoE