Gate/Latch input
The terminal provides an external Gate/Latch input for 24 VDC signals with a minimum pulse duration of tON > 1 µs. This can be used as follows:
- Lock counter value:
lock the counter value via a positive or negative edge (Enable pos/neg. gate) - Save counter value:
save the counter value in separate process data via a positive or negative edge (Enable latch extern 2 on positive/negative edge)
Lock counter value via a positive/negative edge at the gate input (Enable pos./neg. gate)
- The level at the Gate input at which the counter value is locked during runtime can be specified via index 0x8000:04 "Gate polarity".
 - 0: Disable gate
The Gate/Latch input is disabled. It can still be used as Latch extern 2 input. - 1: Enable pos. gate
The counter value is locked with HIGH level at the Gate/Latch input. - 2: Enable neg. gate
The counter value is locked with LOW level at the Gate/Latch input. - The current level at the Gate input is displayed via process data 0x6000:0C "Status of input gate".
Save counter value via a positive/negative edge at the Gate/Latch input (Enable latch extern 2 on positive/negative edge)
The Gate/Latch input may be used as a second latch input (Latch extern 2). To do this, the gate should be disabled.
![]()  | Deactivation of the gate Set the "Gate polarity" bit (index 0x8000:04) to "0 – Disable gate" in order to be able to use the Latch extern 2 input without disabling the counter value after the latch event.  |
- The counter value at the Latch extern 2 input can be saved via:
 - Index 0x7000:0C "Enable latch extern 2 on positive edge" = TRUE
At the first external latch pulse with positive edge at the Gate/Latch input the current counter value is stored in index 0x6000:22 "Latch value 2". - Index 0x7000:0D "Enable latch extern 2 on negative edge" = TRUE
At the first external pulse with negative edge at the Gate/Latch input the current counter value is stored in index 0x6000:22 "Latch value 2". - Simultaneous activation of 0x7000:0C and 0x7000:0D
On the first pulse at the Gate/Latch input, regardless of the polarity of the edge, the current counter value is stored in index 0x6000:22 "Latch value 2". - Specification whether it is necessary to reactivate the command to save the counter value via:
 - "Enable continuous latch extern 2" Index 0x8000:23 = FALSE
The following pulses at the Gate/Latch input have no influence on the Latch value in index 0x6000:22 "Latch value 2" if the bit in index 0x7000:0C or 0x7000:0D is set.
Only when index 0x6002:12 "Latch extern 2 valid" is FALSE, a new counter value can be written to the Gate/Latch input in index 0x6000:22 "Latch value 2". - "Enable continuous latch extern 2" index 0x8000:23 = TRUE
The counter value is written to index 0x6002:12 "Latch value 2" for each parameterized edge at the Gate/Latch input.
There is no need to reactivate index 0x7000:0C or 0x7000:0D. - The status of the Gate/Latch input can be recorded via index 0x6000:0C "Status of input gate".
 - Saving of the counter value in index 0x6000:22 "Latch value 2" is confirmed via bit 0x6002:12 "Latch extern 2 valid".
![]()  | Simultaneous use of Gate und Latch extern 2 When using index 0x8000:04 "Gate polarity"(1 = "Enable pos. gate") and simultaneously activating index 0x7000:0C "Enable latch extern 2 on positive edge", the current counter value is initially stored in index 0x6000:22 "Latch value 2" when a positive edge is detected at the Gate/Latch input. The counter value is then blocked. The same applies to the use of index 0x80n00:04 "Gate polarity" (2 = "Enable neg. gate") and simultaneous activation of index 0x7000:0D "Enable latch extern 2 on negative edge" at a negative edge at the Gate/Latch input.  |
![]()  | Multiple activation of the latch function If several commands are activated simultaneously to save the counter value in the "Latch value" process data (index 0x60n0:12), only the command that is set first is accepted by the terminal.