Features CoE
Notice
Features CoE 1:
Parameterization via the CoE list (CAN over EtherCAT)
The EtherCAT device is parameterized via the CoE - Online tab (with a double click on the respective object) or via the Process Data tab (assignment of PDOs). A detailed description can be found in the EtherCAT System-Documentation in chapter “EtherCAT subscriber configuration”
Please note the general CoE notes in the EtherCAT System Documentation in chapter “CoE-interface” when using/manipulating the CoE parameters:
- Keep a startup list if components have to be replaced
- Differentiation between online/offline dictionary,
- existence of current XML description
- use “CoE reload” for resetting changes
Depending on the main PDO/optional PDOs, further settings can be selected in the CoE list (CAN over EtherCAT).
The following CoE settings are possible from object 0x8010 and are shown below in their default settings:
Features CoE 2:
Fig.45: “CoE online” tab
The parameters are described on page Object description and parameterization.
Frequency
Frequency measurement
Measurement sequence
Features CoE 3:
Fig.46: Frequency measurement principle in enhanced operation mode
Period calculation
Features CoE 4:
Frequency and period measurement
From the explanatory notes above it is apparent that the frequency measurement can measure the current axis status (velocity) significantly more accurately than the period measurement. Frequency measurement is therefore preferable, if possible.
Latch
Features CoE 5:
“Latch C valid” bit
Only when the value in the input process data “Latch C valid” (index 0x6010:01) is FALSE can a new counter value be written to the latch input.
Features CoE 6:
“Latch extern valid” bit
Only when the value in the input process data “Latch external valid” (index 0x6010:02) is FALSE can a new counter value be written to the latch input.
Reset
Up/down counter
Over-/underflow
Wire break detection “Open circuit detection”
Notice
Wire break detection “Open circuit detection” vs. Single-ended cables (TTL interface)
Due to the nature of the technology, “Wire break detection” does not work with single-ended cables (TTL interface).
Micro-increments
Features CoE 7:
Fig.47: Frequency measurement principle in enhanced operation mode
The highly constant query cycles (accuracy: 100 ns) of the distributed clocks systems enable the terminal to interpolate axis positions between the counted encoder increments from a certain speed. The interpolation resolution is 8 bit, corresponding to 256 values. A standard encoder with 1,024 bars with 4-fold evaluation and micro-increments thus becomes a high-resolution axis encoder with 4096 * 256 = 1,048,576 bars.
Underrunning of the minimum velocity is indicated by the object 0x6010:08 (extrapolation stall) in the process data.