Operating modes and settings
Watchdog activation/deactivation (index 0x4061:01, channel 1; index 0x40A1:01, channel 2)
This bit disables the watchdog timer. In the event of a communication fault the analog output value is not reset to the manufacturer or user default value.
If the bit is not set, the manufacturer or user default value is output (default).
Switching between manufacturer- or user-specific output value (index 0x4061:02, channel 1; index 0x40A1:02 channel 2)
The analog output value can, e.g. in the case of a failure of communication with the controller, be set to a user-specific value (index 0x4063). Object 0x4061:02 (channel 1) or object 0x40A1:02 (channel 2) activates this option (value: TRUE); the output values are determined with object 0x4063 (channel 1) or object 0x40A3 (channel 2). If this function is deactivated (value of object 0x4061:02, channel 1 or object 0x40A1:02, channel 2 is FALSE) then the manufacturer's default value (EL4102, EL4132: 0 V, EL4112: 0 mA, EL4122: 4 mA) is output.
No standard value is output if the watchdog timer is deactivated (the value of object 0x4061:01 for Channel 1 or of object 0x40A1:01 for Channel 2 is TRUE).
Activation of user scaling (index 0x4061:03, channel 1; index 0x40A1:03 channel 2)
User scaling is active (bit set):
Example: Calculation and calibration of the output value
The terminal places the raw values of its D/A converter into the DAC raw value object 0x4041:01 or 0x4081:01 (RAM). The output value is adjusted with the manufacturer's calibration values. User scaling can, optionally, follow:
YH =  (XDAC - BK) x  AK
Output value after manufacturer's calibration (corresponds to Yout when feature object 0x4061:03 or 0x40A1:03 is inactive)
YA = YH x AW x 216 + BW
Output value following user scaling
Example: Limitation of the output range of -5 V to +5 V in the case of EL4132, calculation of the GAIN factor of the user scaling
YA = YH x AW x 2-16 + BW
Calculation of the GAIN factor for an upper limit value of +5 V
(corresponds to a lower limit value of -5 V by shortening the sign)
↔(YA - BW) / (YH x 2-16) = AW
YA = 16383dec
corresponds to the desired upper limit value of +5 V
(16383 - 0) / 32767 x 2-16
YH = 32767dec
corresponds to the upper limit value of +10 V
= AW = 32767
BW = 0dec
corresponds to the offset of the user scaling
AW= 32767dec
corresponds to the offset value of the user scaling of +7 V
Example: Shifting of the output range of -3 V to +10 V in the case of EL4132, calculation of the OFFSET value of the user scaling
Calculation of the OFFSET value for the shifting of the lower limit value to -3 V
↔ YA -  YH x AW x 2-16  = BW
YA = (- 9831dec)
corresponds to the desired lower limit value of -3 V
(- 9831) - (- 32769 x 65536 x 2-16 )
YH = (-32769dec)
corresponds to the lower limit value of -10 V
= BW = 22938
AW = 65536dec
corresponds to the gain factor of the user scaling (factor 1)
BW = 22938dec
Operating modes and settings 1:
OFFSET value
The shifting of the output value by the OFFSET takes place linearly to the lower limit value (-10 V / -10 mA) or upper limit value (+ 10 V / +10 mA).
Legend
Object index (hex)
XDAC
Output value of the D/A converter
YA
Process data for controller
BK
Manufacturer calibration offset (only changeable if the object Producer codeword 4040 or 0x4080 is set)
4042:01, 4082:01
AK
Manufacturer calibration gain (only changeable if the object Producer codeword 4040 or 0x4080 is set)
4042:02, 4082:02
BW
User scaling offset (can be activated via index 0x4061:01 or 0x40A1:01 of the feature objects 0x4061 or 0x40A1)
4062:01, 40A2:01
AW
User scaling gain (can be activated via index 0x4061:01 or 0x40A1:01 of the feature objects 0x4061 or 0x40A1)
4062:02, 40A2:02
Presentation, index 0x4061:04, 0x4061:05 (channel 1); index 0x40A1:04, 0x40A1:05 (channel 2)
In the delivery state of the measured value is shown in two's complement format (signed integer).
Index 0x4061:04, 0x4061:05 (channel 1) and index 0x40A1:04, 0x40A1:05 (channel 2) offers the possibility of changing the method of representation of the output value (signed integer, magnitude-sign format or absolute value)
Output signal
Value
EL4102
Decimal
Hexadecimal
0 V
0
0x0000
5 V
16383
0x3FFF
10 V
32767
0x7FFF
Output signal
Value
EL4112
Decimal
Hexadecimal
0 mA
0
0x0000
10 mA
16383
0x3FFF
20 mA
32767
0x7FFF
Output signal
Value
EL4112-0010
Decimal
Hexadecimal
-10 mA
-32768
0x8000
-5 mA
-16383
0xC001
0 mA
0
0x0000
5 mA
16383
0x3FFF
10 mA
32767
0x7FFF
Output signal
Value
EL4122
Decimal
Hexadecimal
4 mA
0
0x0000
12 mA
16383
0x3FFF
20 mA
32767
0x7FFF
Output signal
Value
EL4132
Decimal
Hexadecimal
-10 V
-32768
0x8000
-5 V
-16383
0xC001
0 V
0
0x0000
5 V
16383
0x3FFF
10 V
32767
0x7FFF
Producer codeword
Operating modes and settings 2:
Code Wort
The vendor reserves the authority for the basic calibration of the terminals. The Producer codeword is therefore at present reserved.