Configuration data
Index 80n0*** AI settings (for 0 ≤ n ≤ 3)
80n0:0 | AI Settings | Maximum subindex | UINT8 | RO | 0x18 (24dec) |
80n0:01 | User scale is active. | BOOLEAN | RW | 0x00 (0dec) | |
80n0:02 | 0: Signed presentation 1: Unsigned presentation 2: Absolute value with MSB as sign | BIT3 | RW | 0x00 (0dec) | |
80n0:05 | The S5 bits are displayed in the three low-order bits | BOOLEAN | RW | 0x00 (0dec) | |
80n0:06 | Enable filter | Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary | BOOLEAN | RW | 0x00 (0dec) |
80n0:07 | Limit 1 enabled | BOOLEAN | RW | 0x00 (0dec) | |
80n0:08 | Limit 2 enabled | BOOLEAN | RW | 0x00 (0dec) | |
80n0:0A | Enabling of the user calibration | BOOLEAN | RW | 0x00 (0dec) | |
80n0:0B | Enabling of the vendor calibration | BOOLEAN | RW | 0x01 (1dec) | |
80n0:0E | Changing of the Limit Bits | BOOLEAN | RW | 0x00 (0dec) | |
80n0:11 | User scaling offset | INT16 | RW | 0x0000 (0dec) | |
80n0:12 | User scaling gain. | INT32 | RW | 0x00010000 (65536dec) | |
80n0:13 | First limit value for setting the status bits | INT16 | RW | 0x0000 (0dec) | |
80n0:14 | Second limit value for setting the status bits | INT16 | RW | 0x0000 (0dec) | |
80n0:15 | Filter settings | This object determines the digital filter settings, if it is active via Enable filter (index 0x80n0:06). 0: 50 Hz FIR | UINT16 | RW | 0x0000 (0dec) |
80n0:17 | User offset compensation | INT16 | RW | 0x0000 (0dec) | |
80n0:18 | User calibration gain | INT16 | RW | 0x4000 (16384dec) | |
***) since revision no. EL31xx-00xx-0016 | |||||
![]() | The filter characteristics are set via index 0x8000:15 The filter frequencies are set for all channels centrally via index 0x8000:15 (channel 1). All other corresponding indices 0x80n0:15 have no parameterization function! The latest firmware version (see status table) returns an EtherCAT-compliant error message, if the filter characteristics of other channels (index 0x80n0:06, 0x80n0:15) are set. |
Index 80nD AI Advanced settings (for 0 ≤ n ≤ 3, only EL3174 and EL3174-00xx)
Index (hex) | Name | Meaning | Data type | Flags | Default | |
80nD:0 | AI Advanced Settings | Maximum subindex | UINT8 | RO | 0x12 (18dec) | |
80nD:11 | Input Type | Measurement mode, allowed values: | UINT16 | RW | 0x0002 (2dec) | |
0x01 | ±60 V (only EL3174-0042) | |||||
0x02 | ±10 V (not EL3174-0032/0042) | |||||
0x0D | 0..60 V (only EL3174-0042) | |||||
0x0E | 0..10 V (not EL3174-0032/0042) | |||||
0x11 | ±20 mA (not EL3174-0042) | |||||
0x12 | 0..20 mA (not EL3174-0042) | |||||
0x13 | 4.. 20 mA (not EL3174-0042) | |||||
0x14 | 4..20 mA (NAMUR) (not EL3174-0042) | |||||
80nD:12 | Scaler | Scaling range, allowed values: | UINT16 | RW | 0x0000 (0dec) | |
0x00 | Extended Range | |||||
0x03 | 0x03 Legacy Range | |||||
80nD:17 | Low Range Error | Lower threshold for setting the error bit and error led | INT32 | RW | Dependent on 80nD:11 | |
80nD:18 | High Range Error | Upper threshold for setting the error bit and error led | INT32 | RW | Dependent on 80nD:11 | |
