Limit 1 and limit 2, Swap Limit Bits
Limit 1 and limit 2, index 0x80n0:13, index 0x80n0:14
If the value exceeds or falls below these values, which can be entered in the indices 0x80n0:13 and 0x80n0:14, then the bits in the indices 0x60n0:03 and 0x60n0:05 are set accordingly (see example below). The indices 0x80n0:07 or 0x80n0:08 serve to activate the limit value monitoring.
Output limit n (2-bit):
Limit 1 and limit 2, Swap Limit Bits 1:
Limit evaluation
The limit evaluation assumes a signed representation. The conversion to the desired representation (index 0x80n0:02) only takes place after the limit evaluation.
Limit 1 and limit 2, Swap Limit Bits 2:
Linking in the PLC with 2-bit values
The limit information consists of 2 bits. Limitn can be linked to the PLC or a task in the System Manager.
Limit 1 and limit 2, Swap Limit Bits 4:Fig.223: Linking of 2-bit variable to additional task
Example for EL3162:
Channel 1; Limit 1 and Limit 2 enabled, Limit 1 = 2.8 V, Limit 2 = 7.4 V, representation: signed integer
Entry in index (Limit 1): 0x8000:13
(2.8 V / 10 V) x 216 / 2 - 1 = 9.174dec
Entry in index (Limit 2): 0x8000:14
(7.4 V / 10 V) x 216 / 2 - 1 = 24.247dec
Output:
Input channel 1
Index 0x6000:03
Index 0x6000:05
1.8 V
0x01hex, (Limit 1, limit value undershot)
0x01hex, (Limit 2, limit value undershot)
2.8 V
0x03hex, (Limit 1, limit value reached)
4.2 V
0x02hex, (Limit 1, limit value exceeded)
8.5 V
0x02hex, (Limit 2, limit value exceeded)
Swap Limit index 0x80n0:0E
The limit function can be inverted by SwapLimitBits in index 0x80n0:0E.
Output Limit n (2-bit):
SwapLimitBits setting
Value
FALSE (default setting)
  • 0: not active
  • 1: value < limit value
  • 2: value > limit value
  • 3: Value is equal to the limit value
TRUE
  • 0: not active
  • 1: value > limit value
  • 2: value < limit value
The Swap limit function is available according to the table below
Terminal
Swap limit function from
EL31x1, EL31x4
All firmware versions
EL3112-0011
EL3102
Firmware 08
EL3112
Firmware 08
EL3122
Firmware 08
EL3142
Firmware 08
EL3152
Firmware 09
EL3162
Firmware 08
EL3174, EL3174-00xx