0x80n0 | Configuration data
Index 80n0 ENC Settings 0 Ch.n (for n = 0 [channel 1], n = 1 [channel 2])
Index (hex)
Meaning
Data type
Flags
Default
80n0:0
ENC Settings 0 Ch.n
Maximum subindex
UINT8
RO
0x23 (35dec)
80n0:01
Enable C reset
The counter is reset via the C input.
BOOLEAN
RW
0x00 (0dec)
80n0:02
Enable extern reset
A counter reset is triggered via the external latch input (24 V)
BOOLEAN
RW
0x00 (0dec)
80n0:04
Gate polarity
0: “Disable gate”
1: “Enable pos. gate” (gate locks with HIGH signal level)
2: “Enable neg. gate” (gate locks with LOW signal level)
BIT2
RW
0x01 (1dec)
80n0:06
Evaluation mode
0: “4-fold” (four-fold evaluation)
1: “1-fold” (single evaluation)
2: “2-fold” (two-fold evaluation)
BIT2
RW
0x00 (0dec)
80n0:08
Disable filter
0: Activates the input filter (inputs A, /A, B, /B, C, /C only)
1: Deactivates the input filter
If a filter is activated a signal edge must be present for at least 2.4 µs in order to be counted as an increment.
BOOLEAN
RW
0x01 (1dec)
80n0:0A
Enable micro increments
If activated, the terminal interpolates micro-increments between the integral encoder increments in DC mode. The lower 8 bits of the counter value are used in each case for the display. A 32-bit counter thus becomes a 24+8-bit counter, a 16-bit counter becomes an 8+8-bit counter.
BOOLEAN
RW
0x00 (0dec)
80n0:0B
Error detection A
A broken wire or short circuit on track A is indicated in index 0x60n0:07 and as process data. Diagnostics is only possible, if the associated input is wired differentially.
BOOLEAN
RW
0x01 (1dec)
80n0:0C
Error detection B
A broken wire or short circuit on track B is indicated in index 0x60n0:07 and as process data. Diagnostics is only possible, if the associated input is wired differentially.
BOOLEAN
RW
0x01 (1dec)
80n0:0D
Error detection C
A broken wire or short circuit on track C is indicated in index 0x60n0:07 and as process data. Diagnostics is only possible, if the associated input is wired differentially.
BOOLEAN
RW
0x00 (0dec)
80n0:0E
Reversion of rotation
Activates reversion of rotation
BOOLEAN
RW
0x00 (0dec)
80n0:10
Extern reset polarity
0: “Fall” (the counter is set to zero with a falling edge)
1: “Rise” (the counter is set to zero with a rising edge)
BIT1
RW
0x01 (1dec)
80n0:11
Frequency window
Minimum time over which the frequency is determined; default value: 10 ms  [resolution: 1 µs].
The frequency is calculated from the number of increments (changes of position value) in the “Frequency window” time interval.
The determined frequency is output via the process data in index 0x60n0:13 “Frequency value”.
The frequency calculation is carried out locally without distributed clocks function.
UINT16
RW
0x2710 (10000dec)
80n0:13
Frequency scaling
Scaling of the frequency measurement (must be divided by this value to obtain the unit in Hz):
100: “0.01 Hz” (default)
1: “1 Hz”
UINT32
RW
0x00000064 (100dec)
80n0:14
Period scaling
Resolution of the period value in the process data:
10: “10 ns” Period value is a multiple of 10 ns
100: “100 ns” Period value is a multiple of 100 ns
500: “500 ns” Period value is a multiple of 500 ns
UINT32
RW
0x0000000A (10dec)
Index (hex)
Meaning
Data type
Flags
Default
80n0:17
Frequency Wait Time
Waiting time [ms] for frequency measurement
If no full period is detected within the “Frequency window”, another frequency window is started to record a full period. This happens until the maximum frequency wait time has elapsed.
At least double the period value of the minimum frequency to be measured should be entered here. t >= 2* (1 / fmin)
UINT16
RW
0x53E2 (21474dec)
80n0:1D
Frequency numerator
Frequency counter value, frequency scaling
UINT32
RW
0x00000001 (1dec)
80n0:1E
Frequency denominator
frequency counter value, used for scaling the frequency and the velocity calculation (increments / unit).
UINT32
RW
0x00000001 (1dec)
80n0:21
Enable encoder plausibility check
Activation of plausibility check
BOOLEAN
RW
0x00 (0dec)
80n0:22
Enable continuous latch extern
FALSE:
The following pulses at the Latch input have no influence on the latch value in index 0x60n0:12 “Latch value” when the bit in index 0x70n0:02 or 0x70n0:04 is set.
TRUE:
The counter value is written to index 0x60n0:12 “Latch value” at every parameterized edge at the Latch input.
There is no need to reactivate index 0x70n0:02 or 0x70n0:04.
BOOLEAN
RW
0x00 (0dec)
80n0:23
Enable continuous latch extern 2
FALSE:
The following pulses at the “Latch extern 2” input have no influence on the latch value in index 0x60n0:22 “Latch value 2” when the bit in index 0x70n0:0C or 0x70n0:0D is set.
TRUE:
The counter value is written to index 0x60n0:22 “Latch value 2” at every parameterized edge at the “Latch extern 2” input.
BOOLEAN
RW
0x00 (0dec)
Index 80n1 ENC Settings 1 Ch.n (for n = 0 [channel 1], n = 1 [channel 2])
Index (hex)
Meaning
Data type
Flags
Default
80n1:0
ENC Settings 1 Ch.n
Maximum subindex
UINT8
RO
0x1D (29dec)
80n1:17
Supply voltage
Setting the sensor supply
50dec: 5.0 V (default)
120dec: 12.0 V
240dec: 24.0 V
Refer to the Note on setting the encoder supply
UINT32
RW
0x00000032 (50dec)
80n1:19
Filter settings
Filter settings:
10dec: 10 kHz
25dec: 25 kHz
50dec: 50 kHz
100dec: 100 kHz
250dec: 250 kHz
500dec: 500 kHz
1000dec: 1 MHz
2500dec: 2.5 MHz
5000dec: 5 MHz (default)
UINT32
RW
0x00001388 (5000dec)
80n1:1A
Limit counter value
Specifies the value for the upper counter limit.
UINT32
RW
0xFFFFFFFF (-1dez)
80n1:1B
Reset counter value
Specifies the value for the lower counter limit.
UINT32
RW
0x00000000 (0dec)
80n1:1C
Direction inversion hysteresis
Enter the hysteresis in number of increments. A value greater than 0 must be selected.
If the counter value exceeds the value, the bit in index 0x60n2:13 “Direction inversion detected” is set in the next PLC cycle.
UINT8
RW
0x0A (10dec)
80n1:1D
Counter mode
0: Encoder RS422 (diff. input)
1: Counter RS422 (diff. input)
2: Encoder TTL (single ended)
3: Counter TTL (single ended)
4: Encoder open collector
5: Counter open collector
UINT32
RW
0x00000000 (0dec)