Configuration data
Index 8000 AI Settings UBridge Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
8000:0
Max. Subindex
UINT8
RO
0x18 (24dec)
8000:01
Enable User Scale
User scaling is active
BOOLEAN
RW
0x00 (0dec)
8000:02
Presentation
0: Signed presentation
The measured value is displayed in two's complement.
Maximum presentation range at 16 bits:
-32768dec ... +32767dec
1: Unsigned presentation
Maximum presentation range for 16 bits:
0 ... +65535dec
2: Absolute value with MSB as sign
The measured value is output in the signed amount representation.
- 32768dec ... +32767dec
BIT3
RW
0x00 (0dec)
8000:06
Enable Filter 1
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8000:07
Enable Limit 1
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8000:08
Enable Limit 2
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8000:0A
Enable user calibration
BOOLEAN
RW
0x00 (0dec)
8000:0B
Enable vendor calibration
BOOLEAN
RW
0x01 (1dec)
8000:0E
Swap Limit Bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8000:11
User Scale Offset
User scale offset
INT16
RW
0x0000 (0dec)
8000:12
User Scale Gain
User scale gain.
The gain has a fixed-point representation with a factor of 2-16.
The value 1 corresponds to 65535 (0x00010000).
INT32
RW
0x00010000 (65536dec)
8000:13
Limit 1
First limit value for setting the status bits
INT16
RW
0x0000 (0dec)
8000:14
Limit 2
Second limit value for setting the status bits
INT16
RW
0x0000 (0dec)
8000:15
Filter 1 Settings
This object determines the digital filter settings if it is active via Enable filter (Index 0x8000:06).
The possible settings are numbered consecutively.
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
Refer to the Note on setting the filter characteristics
UINT16
RW
0x0000 (0dec)
8000:17
User calibration offset
INT16
RW
0x0000 (0dec)
8000:18
User calibration gain
UINT16
RW
0x7FFF (32767dec)
Index 800C AI User Calibration Data UBridge Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
800C:0
Max. Subindex
UINT8
RO
0x0D (13dec)
800C:01
Calibration Data
4 bytes of free memory space;
here it is possible to store the calibration date in the form of 8 CHAR, for example
OCTET-STRING[4]
RW
{0}
800C:03
S0
Real32 coefficient S0
REAL32
RW
0x00000000 (0dec)
800C:04
S1
Real32 coefficient S1
REAL32
RW
0x00000000 (0dec)
800C:05
S2
Real32 coefficient S2
REAL32
RW
0x00000000 (0dec)
800C:06
S3
Real32 coefficient S3
REAL32
RW
0x00000000 (0dec)
800C:07
T1
Real32 coefficient T1
REAL32
RW
0x00000000 (0dec)
800C:08
T1S1
Real32 coefficient T1S1
REAL32
RW
0x00000000 (0dec)
Index 800D AI Advanced Settings UBridge Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
800D:0
Max. Subindex
UINT8
RO
0x2E (46dec)
800D:11
Input Interface
Values:
0 - None
48 - V ±20 mV
49 - V ±75 mV
50 - V ±4 V
UINT16
RW
0x0002 (2dec)
800D:12
Integer Scaler
Values:
0 - Extended Range
3 - Legacy Range
UINT16
RW
0x0000 (0dec)
800D:17
Low Range Error
Low Range limit value
INT32
RW
0xFFFF8000 (-32768dec)
800D:018
High Range Error
High Range limit value
INT32
RW
0x00007FFF (32767dec)
800D:1A
Filter 2 Settings
Values:
0 – Off
1 - HP 0.001 Hz
2 - HP 0.01 Hz
3 - HP 0.1 Hz
4 - HP 1 Hz
5 - HP 10 Hz
UINT16
RW
0x0000 (0dec)
800D:1C
User Scale Offset (Real32)
User scale offset (Real32)
REAL32
RW
0x00000000 (0.0)
800D:1D
User Scale Gain (Real32)
User scale gain. (Real32)
REAL32
RW
0x3F800000 (1.0)
800D:27
Low Range Error (Real32)
Limit value Low Range Error (Real32)
REAL32
RW
0xC12BCC79 (-10.7374201)
800D:28
High Range Error (Real32)
Limit value High Range Error (Real32)
REAL32
RW
0x412BCC79 (10.7374201)
800D:29
Limit 1 (Real32)
Limit value Limit1
REAL32
RW
0x00000000 (0.0)
800D:2A
Limit 2 (Real32)
Limit 2 (INT16) in the AI settings is adjusted automatically
REAL32
RW
0x00000000 (0.0)
800D:2B
Steady state Window
Time constant for the "Steady state" bit
UINT16
RW
0x0064 (100dec)
800D:2C
Steady state tolerance
Tolerance window for the "Steady state" bit
REAL32
RW
0x3F800000 (1065353216dec)
800D:2D
Low Range Warning (Real32)
Limit value Low Range Warning (Real32)
REAL32
RW
0xBCA3D70A (-1130113270dec)
800D:2E
High Range Warning (Real32)
Limit value High Range Warning (Real32)
REAL32
RW
0x3CA3D70A (1017370378dec)
Index 800F AI Vendor Calibration Data UBridge Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
800F:0
Max. Subindex
UINT8
RO
0x08 (8dec)
800F:01
Calibration Data
OCTET-STRING[4]
RW
{0}
800F:03
S0
REAL32
RW
0x00000000 (0dec)
800F:04
S1
REAL32
RW
0x00000000 (0dec)
800F:05
S2
REAL32
RW
0x00000000 (0dec)
800F:06
S3
REAL32
RW
0x00000000 (0dec)
800F:07
T1
REAL32
RW
0x00000000 (0dec)
800F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8010 AI Settings USense Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
8010:0
Max. Subindex
UINT8
RO
0x18 (24dec)
8010:01
Enable User Scale
BOOLEAN
RW
0x00 (0dec)
8010:02
Presentation
0 ... +65535dec
BIT3
RW
0x00 (0dec)
8010:06
Enable Filter 1
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8010:07
Enable Limit 1
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8010:08
Enable Limit 2
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8010:0A
BOOLEAN
RW
0x00 (0dec)
8010:0B
BOOLEAN
RW
0x01 (1dec)
8010:0E
Swap Limit Bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8010:11
User Scale Offset
User scale offset
INT16
RW
0x0000 (0dec)
8010:12
User Scale Gain
User scale gain.
INT32
RW
8010:13
Limit 1
INT16
RW
0x0000 (0dec)
8010:14
Limit 2
INT16
RW
0x0000 (0dec)
8010:15
Filter 1 Settings
This object determines the digital filter settings if it is active via Enable filter (Index 0x8010:06).
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
UINT16
RW
0x0000 (0dec)
8010:17
INT16
RW
0x0000 (0dec)
8010:18
UINT16
RW
0x7FFF (32767dec)
Index 801C AI User Calibration Data USense Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
801C:0
Max. Subindex
UINT8
RO
0x0D (13dec)
801C:01
Calibration Data
OCTET-STRING[4]
RW
{0}
801C:03
S0
REAL32
RW
0x00000000 (0dec)
801C:04
S1
REAL32
RW
0x00000000 (0dec)
801C:05
S2
REAL32
RW
0x00000000 (0dec)
801C:06
S3
REAL32
RW
0x00000000 (0dec)
801C:07
T1
REAL32
RW
0x00000000 (0dec)
801C:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 801D AI Advanced Settings USense Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
801D:0
Max. Subindex
UINT8
RO
0x2E (46dec)
801D:11
Input Interface
Values:
0 - None
48 - V ±20 mV
49 - V ±75 mV
50 - V ±4 V
UINT16
RW
0x0002 (2dec)
801D:12
Integer Scaler
Values:
0 - Extended Range
3 - Legacy Range
UINT16
RW
0x0000 (0dec)
801D:17
Low Range Error
INT32
RW
0xFFFF8010 (-32768dec)
801D:18
High Range Error
INT32
RW
801D:1A
Filter 2 Settings
Values:
0 – Off
1 - HP 0.001 Hz
2 - HP 0.01 Hz
3 - HP 0.1 Hz
4 - HP 1 Hz
5 - HP 10 Hz
UINT16
RW
0x0000 (0dec)
801D:1C
REAL32
RW
0x00000000 (0.0)
801D:1D
REAL32
RW
0x3F801000 (1.0)
801D:27
REAL32
RW
801D:28
REAL32
RW
801D:29
Limit 1 (Real32)
Limit value Limit1
REAL32
RW
0x00000000 (0.0)
801D:2A
Limit 2 (Real32)
REAL32
RW
0x00000000 (0.0)
801D:2B
Steady state Window
UINT16
RW
0x0064 (100dec)
801D:2C
REAL32
RW
0x3F801000 (1065353216dec)
801D:2D
REAL32
RW
801D:2E
REAL32
RW
Index 801F AI Vendor Calibration Data USense Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
801F:0
Max. Subindex
UINT8
RO
0x08 (8dec)
801F:01
Calibration Data
OCTET-STRING[4]
RW
{0}
801F:03
S0
REAL32
RW
0x00000000 (0dec)
801F:04
S1
REAL32
RW
0x00000000 (0dec)
801F:05
S2
REAL32
RW
0x00000000 (0dec)
801F:06
S3
REAL32
RW
0x00000000 (0dec)
801F:07
T1
REAL32
RW
0x00000000 (0dec)
801F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8020 RMB Settings Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
8020:0
RMB Settings Ch.1
Max. Subindex
UINT8
RO
0x18 (24dec)
8020:01
Enable User Scale
BOOLEAN
RW
0x00 (0dec)
8020:02
Presentation
0 ... +65535dec
BIT3
RW
0x00 (0dec)
8020:06
Enable Filter 1
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8020:07
Enable Limit 1
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8020:08
Enable Limit 2
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8020:0A
BOOLEAN
RW
0x00 (0dec)
8020:0B
BOOLEAN
RW
0x01 (1dec)
8020:0E
Swap Limit Bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8020:11
User Scale Offset
User scale offset
INT16
RW
0x0000 (0dec)
8020:12
User Scale Gain
User scale gain.
INT32
RW
8020:13
Limit 1
INT16
RW
0x0000 (0dec)
8020:14
Limit 2
INT16
RW
0x0000 (0dec)
8020:15
Filter 1 Settings
This object determines the digital filter settings if it is active via Enable filter (Index 0x8020:06).
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
UINT16
RW
0x0000 (0dec)
8020:17
INT16
RW
0x0000 (0dec)
8020:18
UINT16
RW
0x7FFF (32767dec)
Index 802C RMB User Calibration Data Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
802C:0
RMB User calibration Data Ch.1
Max. Subindex
UINT8
RO
0x0D (13dec)
802C:01
Calibration Data
OCTET-STRING[4]
RW
{0}
802C:03
S0
REAL32
RW
0x00000000 (0dec)
802C:04
S1
REAL32
RW
0x00000000 (0dec)
802C:05
S2
REAL32
RW
0x00000000 (0dec)
802C:06
S3
REAL32
RW
0x00000000 (0dec)
802C:07
T1
REAL32
RW
0x00000000 (0dec)
802C:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 802D RMB Advanced Settings Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
802D:0
Max. Subindex
UINT8
RO
0x2E (46dec)
802D:11
Input Interface
Values:
0 - None
48 - V ±20 mV
49 - V ±75 mV
50 - V ±4 V
UINT16
RW
0x0002 (2dec)
802D:12
Integer Scaler
Values:
0 - Extended Range
3 - Legacy Range
UINT16
RW
0x0000 (0dec)
802D:17
Low Range Error
INT32
RW
0xFFFF8020 (-32768dec)
802D:018
High Range Error
INT32
RW
802D:1A
Filter 2 Settings
Values:
0 – Off
1 - HP 0.001 Hz
2 - HP 0.01 Hz
3 - HP 0.1 Hz
4 - HP 1 Hz
5 - HP 10 Hz
UINT16
RW
0x0000 (0dec)
802D:1C
REAL32
RW
0x00000000 (0.0)
802D:1D
REAL32
RW
0x3F802000 (1.0)
802D:27
REAL32
RW
802D:28
REAL32
RW
802D:29
Limit 1 (Real32)
Limit value Limit1
REAL32
RW
0x00000000 (0.0)
802D:2A
Limit 2 (Real32)
Limit 2 (INT16) in the RMB settings is automatically adjusted
REAL32
RW
0x00000000 (0.0)
802D:2B
Steady state Window
UINT16
RW
0x0064 (100dec)
802D:2C
REAL32
RW
0x3F802000 (1065353216dec)
802D:2D
REAL32
RW
802D:2E
REAL32
RW
Index 802F RMB Vendor Calibration Data Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
802F:0
Max. Subindex
UINT8
RO
0x08 (8dec)
802F:01
Calibration Data
OCTET-STRING[4]
RW
{0}
802F:03
S0
REAL32
RW
0x00000000 (0dec)
802F:04
S1
REAL32
RW
0x00000000 (0dec)
802F:05
S2
REAL32
RW
0x00000000 (0dec)
802F:06
S3
REAL32
RW
0x00000000 (0dec)
802F:07
T1
REAL32
RW
0x00000000 (0dec)
802F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8030 RMB Sensor Settings Ch.1
Index (hex)
Meaning
Data Type
Flags
Default value
8030:0
UINT8
RO
0x28 (40dec)
8030:23
Sensitivity
Characteristic value of the load cell mV/V
REAL32
RW
0x40000000 (1073741824dec)
8030:24
Nominal Load
Nominal load of the load cell
REAL32
RW
8030:25
Zero Balance
Zero offset of the load cell
REAL32
RW
0x00000000 (0dec)
8030:26
Gravity of Earth
Acceleration of gravity (normal: 9.806650)
REAL32
RW
0x411CE80A (1092413450dec)
8030:27
Scale factor
Scaling factor
REAL32
RW
0x447A0000 (1148846080dec)
8030:28
Reference load
Value of the weight used for adjustment
REAL32
RW
Index 8040 AI Settings UBridge Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
8040:0
Max. Subindex
UINT8
RO
0x18 (24dec)
8040:01
Input Interface
BOOLEAN
RW
0x00 (0dec)
8040:02
Integer Scaler
0 ... +65535dec
BIT3
RW
0x00 (0dec)
8040:06
Low Range Error
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8040:07
High Range Error
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8040:08
Filter 2 Settings
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8040:0A
BOOLEAN
RW
0x00 (0dec)
8040:0B
BOOLEAN
RW
0x01 (1dec)
8040:0E
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8040:11
User scale offset
INT16
RW
0x0000 (0dec)
8040:12
Limit 1 (Real32)
User scale gain.
INT32
RW
8040:13
Limit 2 (Real32)
INT16
RW
0x0000 (0dec)
8040:14
Steady state Window
INT16
RW
0x0000 (0dec)
8040:15
This object determines the digital filter settings if it is active via Enable filter (Index 0x8040:06).
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
UINT16
RW
0x0000 (0dec)
8040:17
INT16
RW
0x0000 (0dec)
8040:18
UINT16
RW
0x7FFF (32767dec)
Index 804C AI User Calibration Data UBridge Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
804C:0
Max. Subindex
UINT8
RO
0x0D (13dec)
804C:01
Calibration
OCTET-STRING[4]
RW
{0}
804C:03
S0
REAL32
RW
0x00000000 (0dec)
804C:04
S1
REAL32
RW
0x00000000 (0dec)
804C:05
S2
REAL32
RW
0x00000000 (0dec)
804C:06
S3
REAL32
RW
0x00000000 (0dec)
804C:07
T1
REAL32
RW
0x00000000 (0dec)
804C:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 804D AI Advanced Settings UBridge Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
804D:0
Max. Subindex
UINT8
RO
0x2E (46dec)
804D:11
Input Interface
Values:
0 - None
48 - V ±20 mV
49 - V ±75 mV
50 - V ±4 V
UINT16
RW
0x0002 (2dec)
804D:12
Integer Scaler
Values:
0 - Extended Range
3 - Legacy Range
UINT16
RW
0x0000 (0dec)
804D:17
Low Range Error
INT32
RW
0xFFFF8040 (-32768dec)
804D:018
High Range Error
INT32
RW
804D:1A
Filter 2 Settings
Values:
0 – Off
1 - HP 0.001 Hz
2 - HP 0.01 Hz
3 - HP 0.1 Hz
4 - HP 1 Hz
5 - HP 10 Hz
UINT16
RW
0x0000 (0dec)
804D:1C
REAL32
RW
0x00000000 (0.0)
804D:1D
REAL32
RW
0x3F804000 (1.0)
804D:27
REAL32
RW
804D:28
REAL32
RW
804D:29
Limit 1 (Real32)
Limit value Limit1
REAL32
RW
0x00000000 (0.0)
804D:2A
Limit 2 (Real32)
REAL32
RW
0x00000000 (0.0)
804D:2B
Steady state Window
UINT16
RW
0x0064 (100dec)
804D:2C
REAL32
RW
0x3F804000 (1065353216dec)
804D:2D
REAL32
RW
804D:2E
REAL32
RW
Index 804F AI Vendor Calibration Data UBridge Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
804F:0
Max. Subindex
UINT8
RO
0x08 (8dec)
804F:01
Calibration Data
OCTET-STRING[4]
RW
{0}
804F:03
S0
REAL32
RW
0x00000000 (0dec)
804F:04
S1
REAL32
RW
0x00000000 (0dec)
804F:05
S2
REAL32
RW
0x00000000 (0dec)
804F:06
S3
REAL32
RW
0x00000000 (0dec)
804F:07
T1
REAL32
RW
0x00000000 (0dec)
804F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8050 AI Settings USense Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
8050:0
Max. Subindex
UINT8
RO
0x18 (24dec)
8050:01
Enable User Scale
BOOLEAN
RW
0x00 (0dec)
8050:02
Presentation
0 ... +65535dec
BIT3
RW
0x00 (0dec)
8050:06
Enable Filter 1
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8050:07
Enable Limit 1
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8050:08
Enable Limit 2
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8050:0A
BOOLEAN
RW
0x00 (0dec)
8050:0B
BOOLEAN
RW
0x01 (1dec)
8050:0E
Swap Limit Bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8050:11
User Scale Offset
User scale offset
INT16
RW
0x0000 (0dec)
8050:12
User Scale Gain
User scale gain.
INT32
RW
8050:13
Limit 1
INT16
RW
0x0000 (0dec)
8050:14
Limit 2
INT16
RW
0x0000 (0dec)
8050:15
Filter 1 Settings
This object determines the digital filter settings if it is active via Enable filter (Index 0x8050:06).
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
UINT16
RW
0x0000 (0dec)
8050:17
INT16
RW
0x0000 (0dec)
8050:18
UINT16
RW
0x7FFF (32767dec)
Index 805C AI User Calibration Data USense Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
805C:0
Max. Subindex
UINT8
RO
0x0D (13dec)
805C:01
Calibration Data
OCTET-STRING[4]
RW
{0}
805C:03
S0
REAL32
RW
0x00000000 (0dec)
805C:04
S1
REAL32
RW
0x00000000 (0dec)
805C:05
S2
REAL32
RW
0x00000000 (0dec)
805C:06
S3
REAL32
RW
0x00000000 (0dec)
805C:07
T1
REAL32
RW
0x00000000 (0dec)
805C:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 805D AI Advanced Settings USense Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
805D:0
Max. Subindex
UINT8
RO
0x2E (46dec)
805D:11
Input Interface
Values:
0 - None
48 - V ±20 mV
49 - V ±75 mV
50 - V ±4 V
UINT16
RW
0x0002 (2dec)
805D:12
Integer Scaler
Values:
0 - Extended Range
3 - Legacy Range
UINT16
RW
0x0000 (0dec)
805D:17
Low Range Error
INT32
RW
0xFFFF8050 (-32768dec)
805D:18
High Range Error
INT32
RW
805D:1A
Filter 2 Settings
Values:
0 – Off
1 - HP 0.001 Hz
2 - HP 0.01 Hz
3 - HP 0.1 Hz
4 - HP 1 Hz
5 - HP 10 Hz
UINT16
RW
0x0000 (0dec)
805D:1C
REAL32
RW
0x00000000 (0.0)
805D:1D
REAL32
RW
0x3F805000 (1.0)
805D:27
REAL32
RW
805D:28
REAL32
RW
805D:29
Limit 1 (Real32)
Limit value Limit1
REAL32
RW
0x00000000 (0.0)
805D:2A
Limit 2 (Real32)
REAL32
RW
0x00000000 (0.0)
805D:2B
Steady state Window
UINT16
RW
0x0064 (100dec)
805D:2C
REAL32
RW
0x3F805000 (1065353216dec)
805D:2D
REAL32
RW
805D:2E
REAL32
RW
Index 805F AI Vendor Calibration Data USense Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
805F:0
Max. Subindex
UINT8
RO
0x08 (8dec)
805F:01
Calibration Data
OCTET-STRING[4]
RW
{0}
805F:03
S0
REAL32
RW
0x00000000 (0dec)
805F:04
S1
REAL32
RW
0x00000000 (0dec)
805F:05
S2
REAL32
RW
0x00000000 (0dec)
805F:06
S3
REAL32
RW
0x00000000 (0dec)
805F:07
T1
REAL32
RW
0x00000000 (0dec)
805F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8060 RMB Settings Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
8060:0
RMB Settings Ch.2
Max. Subindex
UINT8
RO
0x18 (24dec)
8060:01
Enable User Scale
BOOLEAN
RW
0x00 (0dec)
8060:02
Presentation
0 ... +65535dec
BIT3
RW
0x00 (0dec)
8060:06
Enable Filter 1
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8060:07
Enable Limit 1
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8060:08
Enable Limit 2
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8060:0A
BOOLEAN
RW
0x00 (0dec)
8060:0B
BOOLEAN
RW
0x01 (1dec)
8060:0E
Swap Limit Bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8060:11
User Scale Offset
User scale offset
INT16
RW
0x0000 (0dec)
8060:12
User Scale Gain
User scale gain.
INT32
RW
8060:13
Limit 1
INT16
RW
0x0000 (0dec)
8060:14
Limit 2
INT16
RW
0x0000 (0dec)
8060:15
Filter 1 Settings
This object determines the digital filter settings if it is active via Enable filter (Index 0x8060:06).
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
UINT16
RW
0x0000 (0dec)
8060:17
INT16
RW
0x0000 (0dec)
8060:18
UINT16
RW
0x7FFF (32767dec)
Index 806C RMB User Calibration Data Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
806C:0
RMB User calibration Data Ch.2
Max. Subindex
UINT8
RO
0x0D (13dec)
806C:01
Calibration Data
OCTET-STRING[4]
RW
{0}
806C:03
S0
REAL32
RW
0x00000000 (0dec)
806C:04
S1
REAL32
RW
0x00000000 (0dec)
806C:05
S2
REAL32
RW
0x00000000 (0dec)
806C:06
S3
REAL32
RW
0x00000000 (0dec)
806C:07
T1
REAL32
RW
0x00000000 (0dec)
806C:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 806D RMB Advanced Settings Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
806D:0
Max. Subindex
UINT8
RO
0x2E (46dec)
806D:11
Input Interface
Values:
0 - None
48 - V ±20 mV
49 - V ±75 mV
50 - V ±4 V
UINT16
RW
0x0002 (2dec)
806D:12
Integer Scaler
Values:
0 - Extended Range
3 - Legacy Range
UINT16
RW
0x0000 (0dec)
806D:17
Low Range Error
INT32
RW
0xFFFF8060 (-32768dec)
806D:018
High Range Error
INT32
RW
806D:1A
Filter 2 Settings
Values:
0 – Off
1 - HP 0.001 Hz
2 - HP 0.01 Hz
3 - HP 0.1 Hz
4 - HP 1 Hz
5 - HP 10 Hz
UINT16
RW
0x0000 (0dec)
806D:1C
REAL32
RW
0x00000000 (0.0)
806D:1D
REAL32
RW
0x3F806000 (1.0)
806D:27
REAL32
RW
806D:28
REAL32
RW
806D:29
Limit 1 (Real32)
Limit value Limit1
REAL32
RW
0x00000000 (0.0)
806D:2A
Limit 2 (Real32)
REAL32
RW
0x00000000 (0.0)
806D:2B
Steady state Window
UINT16
RW
0x0064 (100dec)
806D:2C
REAL32
RW
0x3F806000 (1065353216dec)
806D:2D
REAL32
RW
806D:2E
REAL32
RW
Index 806F RMB Vendor Calibration Data Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
806F:0
Max. Subindex
UINT8
RO
0x08 (8dec)
806F:01
Calibration Data
OCTET-STRING[4]
RW
{0}
806F:03
S0
REAL32
RW
0x00000000 (0dec)
806F:04
S1
REAL32
RW
0x00000000 (0dec)
806F:05
S2
REAL32
RW
0x00000000 (0dec)
806F:06
S3
REAL32
RW
0x00000000 (0dec)
806F:07
T1
REAL32
RW
0x00000000 (0dec)
806F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8070 RMB Sensor Settings Ch.2
Index (hex)
Meaning
Data Type
Flags
Default value
8070:0
UINT8
RO
0x28 (40dec)
8070:23
Sensitivity
REAL32
RW
8070:24
Nominal Load
REAL32
RW
8070:25
Zero Balance
REAL32
RW
0x00000000 (0dec)
8070:26
Gravity of Earth
REAL32
RW
8070:27
Scale factor
Scaling factor
REAL32
RW
8070:28
Reference load
REAL32
RW
Index F800 DEV Settings
Index (hex)
Meaning
Data Type
Flags
Default value
F800:0
DEV Settings
Max. Subindex
UINT8
RO
0x01 (1dec)
F800:01
Sensor supply
Values:
0 - OFF
5000 - 5 V
10000 - 10 V
UINT16
RW
0x2710 (10000dec)