Index 8000 AI Settings UBridge Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8000:0
Max. subindex
UINT8
RO
0x18 (24dec)
8000:01
Enable User Scale
User scaling is active
BOOLEAN
RW
0x00 (0dec)
8000:02
Presentation
0: Signed presentation
The measured value is displayed in two's complement.
Maximum presentation range at 16 bits:
-32768dec… +32767dec
1: Unsigned presentation
Maximum presentation range for 16 bits:
0… +65535dec
2: Absolute value with MSB as sign
The measured value is output in the signed amount representation.
BIT3
RW
0x00 (0dec)
8000:06
Enable Filter 1
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8000:07
Enable Limit 1
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8000:08
Enable Limit 2
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8000:0A
Enable User Calibration
Enable user calibration
BOOLEAN
RW
0x00 (0dec)
8000:0B
Enable Vendor Calibration
Enable vendor calibration
BOOLEAN
RW
0x01 (1dec)
8000:0E
Swap Limit Bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8000:11
User Scale Offset
User scale offset
INT16
RW
0x0000 (0dec)
8000:12
User Scale Gain
User scale gain.
The gain has a fixed-point presentation with a factor of 2-16.
The value 1 corresponds to 65535 (0x00010000).
INT32
RW
0x00010000 (65536dec)
8000:13
Limit 1
First limit value for setting the status bits
INT16
RW
0x0000 (0dec)
8000:14
Limit 2
Second limit value for setting the status bits
INT16
RW
0x0000 (0dec)
8000:15
Filter 1 Settings
This object determines the digital filter settings if it has been activated via the Enable filter (index 0x8000:06).
The potential settings are numbered consecutively.
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
Refer to the note on setting the filter characteristics
UINT16
RW
0x0000 (0dec)
8000:17
User calibration offset
INT16
RW
0x0000 (0dec)
8000:18
User calibration gain
UINT16
RW
0x7FFF (32767dec)
Index 800C AI User Calibration Data UBridge Ch.1
Index (hex)
Meaning
Data type
Flags
Default
800C:0
Max. subindex
UINT8
RO
0x0D (13dec)
800C:01
Calibration Data
4 bytes of free memory space;
here, the calibration date can be stored in 8 CHAR format, for example
OCTET STRING[4]
RW
{0}
800C:03
S0
Real32 coefficient S0
REAL32
RW
0x00000000 (0dec)
800C:04
S1
Real32 coefficient S1
REAL32
RW
0x00000000 (0dec)
800C:05
S2
Real32 coefficient S2
REAL32
RW
0x00000000 (0dec)
800C:06
S3
Real32 coefficient S3
REAL32
RW
0x00000000 (0dec)
800C:07
T1
Real32 coefficient T1
REAL32
RW
0x00000000 (0dec)
800C:08
T1S1
Real32 coefficient T1S1
REAL32
RW
0x00000000 (0dec)
Index 800D AI Advanced Settings UBridge Ch.1
Index (hex)
Meaning
Data type
Flags
Default
800D:0
Max. subindex
UINT8
RO
0x2E (46dec)
800D:11
Input Interface
Values:
0 – None
48 – V ±20 mV
49 – V ±75 mV
50 – V ±4 V
UINT16
RW
0x0002 (2dec)
800D:12
Integer Scaler
Values:
0 – Extended Range
3 – Legacy Range
UINT16
RW
0x0000 (0dec)
800D:17
Low Range Error
Low Range limit value
INT32
RW
0xFFFF8000 (-32768dec)
800D:018
High Range Error
High Range limit value
INT32
RW
0x00007FFF (32767dec)
800D:1A
Filter 2 Settings
Values:
0 – Off
1 – HP 0.001 Hz
2 – HP 0.01 Hz
3 – HP 0.1 Hz
4 – HP 1 Hz
5 – HP 10 Hz
UINT16
RW
0x0000 (0dec)
800D:1C
User Scale Offset (REAL32)
User scale offset (Real32)
REAL32
RW
0x00000000 (0.0)
800D:1D
User Scale Gain (REAL32)
User scale gain (Real32)
REAL32
RW
0x3F800000 (1.0)
800D:27
Low Range Error (Real32)
Low Range Error (Real32) limit value
REAL32
RW
0xC12BCC79 (-10.7374201)
800D:28
High Range Error (Real32)
High Range Error limit value (Real32)
REAL32
RW
0x412BCC79 (10.7374201)
800D:29
Limit 1 (Real32)
Limit1 limit value
REAL32
RW
0x00000000 (0.0)
800D:2A
Limit 2 (Real32)
Limit 2 (INT16) in the AI settings is adjusted automatically
REAL32
RW
0x00000000 (0.0)
800D:2B
Steady state Window
Time constant for the “Steady state” bit
UINT16
RW
0x0064 (100dec)
800D:2C
Steady state tolerance
Tolerance window for the “Steady state” bit
REAL32
RW
0x3F800000 (1065353216dec)
800D:2D
Low Range Warning (Real32)
Low Range Warning (Real32) limit value
REAL32
RW
0xBCA3D70A (-1130113270dec)
800D:2E
High Range Warning (Real32)
High Range Warning (Real32) limit value
REAL32
RW
0x3CA3D70A (1017370378dec)
Index 800F AI Vendor Calibration Data UBridge Ch.1
Index (hex)
Meaning
Data type
Flags
Default
800F:0
Max. subindex
UINT8
RO
0x08 (8dec)
800F:01
Calibration Data
OCTET STRING[4]
RW
{0}
800F:03
S0
REAL32
RW
0x00000000 (0dec)
800F:04
S1
REAL32
RW
0x00000000 (0dec)
800F:05
S2
REAL32
RW
0x00000000 (0dec)
800F:06
S3
REAL32
RW
0x00000000 (0dec)
800F:07
T1
REAL32
RW
0x00000000 (0dec)
800F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8010 AI Settings USense Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8010:0
Max. subindex
UINT8
RO
0x18 (24dec)
8010:01
Enable User Scale
BOOLEAN
RW
0x00 (0dec)
8010:02
Presentation
0… +65535dec
BIT3
RW
0x00 (0dec)
8010:06
Enable Filter 1
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8010:07
Enable Limit 1
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8010:08
Enable Limit 2
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8010:0A
BOOLEAN
RW
0x00 (0dec)
8010:0B
BOOLEAN
RW
0x01 (1dec)
8010:0E
Swap Limit Bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8010:11
User Scale Offset
User scale offset
INT16
RW
0x0000 (0dec)
8010:12
User Scale Gain
User scale gain.
INT32
RW
8010:13
Limit 1
INT16
RW
0x0000 (0dec)
8010:14
Limit 2
INT16
RW
0x0000 (0dec)
8010:15
Filter 1 Settings
This object determines the digital filter settings if it has been activated via the Enable filter (index 0x8010:06).
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
UINT16
RW
0x0000 (0dec)
8010:17
INT16
RW
0x0000 (0dec)
8010:18
UINT16
RW
0x7FFF (32767dec)
Index 801C AI User Calibration Data USense Ch.1
Index (hex)
Meaning
Data type
Flags
Default
801C:0
Max. subindex
UINT8
RO
0x0D (13dec)
801C:01
Calibration Data
OCTET STRING[4]
RW
{0}
801C:03
S0
REAL32
RW
0x00000000 (0dec)
801C:04
S1
REAL32
RW
0x00000000 (0dec)
801C:05
S2
REAL32
RW
0x00000000 (0dec)
801C:06
S3
REAL32
RW
0x00000000 (0dec)
801C:07
T1
REAL32
RW
0x00000000 (0dec)
801C:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 801D AI Advanced Settings USense Ch.1
Index (hex)
Meaning
Data type
Flags
Default
801D:0
Max. subindex
UINT8
RO
0x2E (46dec)
801D:11
Input Interface
Values:
0 – None
48 – V ±20 mV
49 – V ±75 mV
50 – V ±4 V
UINT16
RW
0x0002 (2dec)
801D:12
Integer Scaler
Values:
0 – Extended Range
3 – Legacy Range
UINT16
RW
0x0000 (0dec)
801D:17
Low Range Error
INT32
RW
0xFFFF8010 (-32768dec)
801D:18
High Range Error
INT32
RW
801D:1A
Filter 2 Settings
Values:
0 – Off
1 – HP 0.001 Hz
2 – HP 0.01 Hz
3 – HP 0.1 Hz
4 – HP 1 Hz
5 – HP 10 Hz
UINT16
RW
0x0000 (0dec)
801D:1C
REAL32
RW
0x00000000 (0.0)
801D:1D
REAL32
RW
0x3F801000 (1.0)
801D:27
REAL32
RW
801D:28
REAL32
RW
801D:29
Limit 1 (Real32)
Limit1 limit value
REAL32
RW
0x00000000 (0.0)
801D:2A
Limit 2 (Real32)
REAL32
RW
0x00000000 (0.0)
801D:2B
Steady state Window
UINT16
RW
0x0064 (100dec)
801D:2C
REAL32
RW
0x3F801000 (1065353216dec)
801D:2D
REAL32
RW
801D:2E
REAL32
RW
Index 801F AI Vendor Calibration Data USense Ch.1
Index (hex)
Meaning
Data type
Flags
Default
801F:0
Max. subindex
UINT8
RO
0x08 (8dec)
801F:01
Calibration Data
OCTET STRING[4]
RW
{0}
801F:03
S0
REAL32
RW
0x00000000 (0dec)
801F:04
S1
REAL32
RW
0x00000000 (0dec)
801F:05
S2
REAL32
RW
0x00000000 (0dec)
801F:06
S3
REAL32
RW
0x00000000 (0dec)
801F:07
T1
REAL32
RW
0x00000000 (0dec)
801F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8020 RMB Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8020:0
RMB Settings Ch.1
Max. subindex
UINT8
RO
0x18 (24dec)
8020:01
Enable User Scale
BOOLEAN
RW
0x00 (0dec)
8020:02
Presentation
0… +65535dec
BIT3
RW
0x00 (0dec)
8020:06
Enable Filter 1
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8020:07
Enable Limit 1
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8020:08
Enable Limit 2
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8020:0A
BOOLEAN
RW
0x00 (0dec)
8020:0B
BOOLEAN
RW
0x01 (1dec)
8020:0E
Swap Limit Bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8020:11
User Scale Offset
User scale offset
INT16
RW
0x0000 (0dec)
8020:12
User Scale Gain
User scale gain.
INT32
RW
8020:13
Limit 1
INT16
RW
0x0000 (0dec)
8020:14
Limit 2
INT16
RW
0x0000 (0dec)
8020:15
Filter 1 Settings
This object determines the digital filter settings if it has been activated via the Enable filter (index 0x8020:06).
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
UINT16
RW
0x0000 (0dec)
8020:17
INT16
RW
0x0000 (0dec)
8020:18
UINT16
RW
0x7FFF (32767dec)
Index 802C RMB User Calibration Data Ch.1
Index (hex)
Meaning
Data type
Flags
Default
802C:0
Max. subindex
UINT8
RO
0x0D (13dec)
802C:01
Calibration Data
OCTET STRING[4]
RW
{0}
802C:03
S0
REAL32
RW
0x00000000 (0dec)
802C:04
S1
REAL32
RW
0x00000000 (0dec)
802C:05
S2
REAL32
RW
0x00000000 (0dec)
802C:06
S3
REAL32
RW
0x00000000 (0dec)
802C:07
T1
REAL32
RW
0x00000000 (0dec)
802C:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 802D RMB Advanced Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
802D:0
Max. subindex
UINT8
RO
0x2E (46dec)
802D:11
Input Interface
Values:
0 – None
48 – V ±20 mV
49 – V ±75 mV
50 – V ±4 V
UINT16
RW
0x0002 (2dec)
802D:12
Integer Scaler
Values:
0 – Extended Range
3 – Legacy Range
UINT16
RW
0x0000 (0dec)
802D:17
Low Range Error
INT32
RW
0xFFFF8020 (-32768dec)
802D:018
High Range Error
INT32
RW
802D:1A
Filter 2 Settings
Values:
0 – Off
1 – HP 0.001 Hz
2 – HP 0.01 Hz
3 – HP 0.1 Hz
4 – HP 1 Hz
5 – HP 10 Hz
UINT16
RW
0x0000 (0dec)
802D:1C
REAL32
RW
0x00000000 (0.0)
802D:1D
REAL32
RW
0x3F802000 (1.0)
802D:27
REAL32
RW
802D:28
REAL32
RW
802D:29
Limit 1 (Real32)
Limit1 limit value
REAL32
RW
0x00000000 (0.0)
802D:2A
Limit 2 (Real32)
Limit 2 (INT16) in the RMB settings is automatically adjusted
REAL32
RW
0x00000000 (0.0)
802D:2B
Steady state Window
UINT16
RW
0x0064 (100dec)
802D:2C
REAL32
RW
0x3F802000 (1065353216dec)
802D:2D
REAL32
RW
802D:2E
REAL32
RW
Index 802F RMB Vendor Calibration Data Ch.1
Index (hex)
Meaning
Data type
Flags
Default
802F:0
Max. subindex
UINT8
RO
0x08 (8dec)
802F:01
Calibration Data
OCTET STRING[4]
RW
{0}
802F:03
S0
REAL32
RW
0x00000000 (0dec)
802F:04
S1
REAL32
RW
0x00000000 (0dec)
802F:05
S2
REAL32
RW
0x00000000 (0dec)
802F:06
S3
REAL32
RW
0x00000000 (0dec)
802F:07
T1
REAL32
RW
0x00000000 (0dec)
802F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8030 RMB Sensor Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8030:0
UINT8
RO
0x28 (40dec)
8030:23
Sensitivity
Characteristic value of the load cell mV/V
REAL32
RW
0x40000000 (1073741824dec)
8030:24
Nominal Load
Nominal load of the load cell
REAL32
RW
8030:25
Zero Balance
Zero offset of the load cell
REAL32
RW
0x00000000 (0dec)
8030:26
Gravity of Earth
Acceleration of gravity (normal: 9.806650)
REAL32
RW
0x411CE80A (1092413450dec)
8030:27
Scale factor
Scaling factor
REAL32
RW
0x447A0000 (1148846080dec)
8030:28
Reference load
Value of the weight used for adjustment
REAL32
RW
Index 8040 AI Settings UBridge Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
8040:0
Max. subindex
UINT8
RO
0x18 (24dec)
8040:01
Input Interface
BOOLEAN
RW
0x00 (0dec)
8040:02
Integer Scaler
0… +65535dec
BIT3
RW
0x00 (0dec)
8040:06
Low Range Error
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8040:07
High Range Error
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8040:08
Filter 2 Settings
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8040:0A
BOOLEAN
RW
0x00 (0dec)
8040:0B
BOOLEAN
RW
0x01 (1dec)
8040:0E
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8040:11
User scale offset
INT16
RW
0x0000 (0dec)
8040:12
Limit 1 (Real32)
User scale gain.
INT32
RW
8040:13
Limit 2 (Real32)
INT16
RW
0x0000 (0dec)
8040:14
Steady state Window
INT16
RW
0x0000 (0dec)
8040:15
This object determines the digital filter settings if it has been activated via the Enable filter (index 0x8040:06).
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
UINT16
RW
0x0000 (0dec)
8040:17
INT16
RW
0x0000 (0dec)
8040:18
UINT16
RW
0x7FFF (32767dec)
Index 804C AI User Calibration Data UBridge Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
804C:0
Max. subindex
UINT8
RO
0x0D (13dec)
804C:01
Calibration
OCTET STRING[4]
RW
{0}
804C:03
S0
REAL32
RW
0x00000000 (0dec)
804C:04
S1
REAL32
RW
0x00000000 (0dec)
804C:05
S2
REAL32
RW
0x00000000 (0dec)
804C:06
S3
REAL32
RW
0x00000000 (0dec)
804C:07
T1
REAL32
RW
0x00000000 (0dec)
804C:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 804D AI Advanced Settings UBridge Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
804D:0
Max. subindex
UINT8
RO
0x2E (46dec)
804D:11
Input Interface
Values:
0 – None
48 – V ±20 mV
49 – V ±75 mV
50 – V ±4 V
UINT16
RW
0x0002 (2dec)
804D:12
Integer Scaler
Values:
0 – Extended Range
3 – Legacy Range
UINT16
RW
0x0000 (0dec)
804D:17
Low Range Error
INT32
RW
0xFFFF8040 (-32768dec)
804D:018
High Range Error
INT32
RW
804D:1A
Filter 2 Settings
Values:
0 – Off
1 – HP 0.001 Hz
2 – HP 0.01 Hz
3 – HP 0.1 Hz
4 – HP 1 Hz
5 – HP 10 Hz
UINT16
RW
0x0000 (0dec)
804D:1C
REAL32
RW
0x00000000 (0.0)
804D:1D
REAL32
RW
0x3F804000 (1.0)
804D:27
REAL32
RW
804D:28
REAL32
RW
804D:29
Limit 1 (Real32)
Limit1 limit value
REAL32
RW
0x00000000 (0.0)
804D:2A
Limit 2 (Real32)
REAL32
RW
0x00000000 (0.0)
804D:2B
Steady state Window
UINT16
RW
0x0064 (100dec)
804D:2C
REAL32
RW
0x3F804000 (1065353216dec)
804D:2D
REAL32
RW
804D:2E
REAL32
RW
Index 804F AI Vendor Calibration Data UBridge Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
804F:0
Max. subindex
UINT8
RO
0x08 (8dec)
804F:01
Calibration Data
OCTET STRING[4]
RW
{0}
804F:03
S0
REAL32
RW
0x00000000 (0dec)
804F:04
S1
REAL32
RW
0x00000000 (0dec)
804F:05
S2
REAL32
RW
0x00000000 (0dec)
804F:06
S3
REAL32
RW
0x00000000 (0dec)
804F:07
T1
REAL32
RW
0x00000000 (0dec)
804F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8050 AI Settings USense Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
8050:0
Max. subindex
UINT8
RO
0x18 (24dec)
8050:01
Enable User Scale
BOOLEAN
RW
0x00 (0dec)
8050:02
Presentation
0… +65535dec
BIT3
RW
0x00 (0dec)
8050:06
Enable Filter 1
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8050:07
Enable Limit 1
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8050:08
Enable Limit 2
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8050:0A
BOOLEAN
RW
0x00 (0dec)
8050:0B
BOOLEAN
RW
0x01 (1dec)
8050:0E
Swap Limit Bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8050:11
User Scale Offset
User scale offset
INT16
RW
0x0000 (0dec)
8050:12
User Scale Gain
User scale gain.
INT32
RW
8050:13
Limit 1
INT16
RW
0x0000 (0dec)
8050:14
Limit 2
INT16
RW
0x0000 (0dec)
8050:15
Filter 1 Settings
This object determines the digital filter settings if it has been activated via the Enable filter (index 0x8050:06).
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
UINT16
RW
0x0000 (0dec)
8050:17
INT16
RW
0x0000 (0dec)
8050:18
UINT16
RW
0x7FFF (32767dec)
Index 805C AI User Calibration Data USense Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
805C:0
Max. subindex
UINT8
RO
0x0D (13dec)
805C:01
Calibration Data
OCTET STRING[4]
RW
{0}
805C:03
S0
REAL32
RW
0x00000000 (0dec)
805C:04
S1
REAL32
RW
0x00000000 (0dec)
805C:05
S2
REAL32
RW
0x00000000 (0dec)
805C:06
S3
REAL32
RW
0x00000000 (0dec)
805C:07
T1
REAL32
RW
0x00000000 (0dec)
805C:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 805D AI Advanced Settings USense Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
805D:0
Max. subindex
UINT8
RO
0x2E (46dec)
805D:11
Input Interface
Values:
0 – None
48 – V ±20 mV
49 – V ±75 mV
50 – V ±4 V
UINT16
RW
0x0002 (2dec)
805D:12
Integer Scaler
Values:
0 – Extended Range
3 – Legacy Range
UINT16
RW
0x0000 (0dec)
805D:17
Low Range Error
INT32
RW
0xFFFF8050 (-32768dec)
805D:18
High Range Error
INT32
RW
805D:1A
Filter 2 Settings
Values:
0 – Off
1 – HP 0.001 Hz
2 – HP 0.01 Hz
3 – HP 0.1 Hz
4 – HP 1 Hz
5 – HP 10 Hz
UINT16
RW
0x0000 (0dec)
805D:1C
REAL32
RW
0x00000000 (0.0)
805D:1D
REAL32
RW
0x3F805000 (1.0)
805D:27
REAL32
RW
805D:28
REAL32
RW
805D:29
Limit 1 (Real32)
Limit1 limit value
REAL32
RW
0x00000000 (0.0)
805D:2A
Limit 2 (Real32)
REAL32
RW
0x00000000 (0.0)
805D:2B
Steady state Window
UINT16
RW
0x0064 (100dec)
805D:2C
REAL32
RW
0x3F805000 (1065353216dec)
805D:2D
REAL32
RW
805D:2E
REAL32
RW
Index 805F AI Vendor Calibration Data USense Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
805F:0
Max. subindex
UINT8
RO
0x08 (8dec)
805F:01
Calibration Data
OCTET STRING[4]
RW
{0}
805F:03
S0
REAL32
RW
0x00000000 (0dec)
805F:04
S1
REAL32
RW
0x00000000 (0dec)
805F:05
S2
REAL32
RW
0x00000000 (0dec)
805F:06
S3
REAL32
RW
0x00000000 (0dec)
805F:07
T1
REAL32
RW
0x00000000 (0dec)
805F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8060 RMB Settings Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
8060:0
RMB Settings Ch.2
Max. subindex
UINT8
RO
0x18 (24dec)
8060:01
Enable User Scale
BOOLEAN
RW
0x00 (0dec)
8060:02
Presentation
0… +65535dec
BIT3
RW
0x00 (0dec)
8060:06
Enable Filter 1
Enable filter 1
BOOLEAN
RW
0x01 (1dec)
8060:07
Enable Limit 1
Enable Limit 1
BOOLEAN
RW
0x00 (0dec)
8060:08
Enable Limit 2
Enable Limit 2
BOOLEAN
RW
0x00 (0dec)
8060:0A
BOOLEAN
RW
0x00 (0dec)
8060:0B
BOOLEAN
RW
0x01 (1dec)
8060:0E
Swap Limit Bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8060:11
User Scale Offset
User scale offset
INT16
RW
0x0000 (0dec)
8060:12
User Scale Gain
User scale gain.
INT32
RW
8060:13
Limit 1
INT16
RW
0x0000 (0dec)
8060:14
Limit 2
INT16
RW
0x0000 (0dec)
8060:15
Filter 1 Settings
This object determines the digital filter settings if it has been activated via the Enable filter (index 0x8060:06).
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
UINT16
RW
0x0000 (0dec)
8060:17
INT16
RW
0x0000 (0dec)
8060:18
UINT16
RW
0x7FFF (32767dec)
Index 806C RMB User Calibration Data Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
806C:0
Max. subindex
UINT8
RO
0x0D (13dec)
806C:01
Calibration Data
OCTET STRING[4]
RW
{0}
806C:03
S0
REAL32
RW
0x00000000 (0dec)
806C:04
S1
REAL32
RW
0x00000000 (0dec)
806C:05
S2
REAL32
RW
0x00000000 (0dec)
806C:06
S3
REAL32
RW
0x00000000 (0dec)
806C:07
T1
REAL32
RW
0x00000000 (0dec)
806C:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 806D RMB Advanced Settings Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
806D:0
Max. subindex
UINT8
RO
0x2E (46dec)
806D:11
Input Interface
Values:
0 – None
48 – V ±20 mV
49 – V ±75 mV
50 – V ±4 V
UINT16
RW
0x0002 (2dec)
806D:12
Integer Scaler
Values:
0 – Extended Range
3 – Legacy Range
UINT16
RW
0x0000 (0dec)
806D:17
Low Range Error
INT32
RW
0xFFFF8060 (-32768dec)
806D:018
High Range Error
INT32
RW
806D:1A
Filter 2 Settings
Values:
0 – Off
1 – HP 0.001 Hz
2 – HP 0.01 Hz
3 – HP 0.1 Hz
4 – HP 1 Hz
5 – HP 10 Hz
UINT16
RW
0x0000 (0dec)
806D:1C
REAL32
RW
0x00000000 (0.0)
806D:1D
REAL32
RW
0x3F806000 (1.0)
806D:27
REAL32
RW
806D:28
REAL32
RW
806D:29
Limit 1 (Real32)
Limit1 limit value
REAL32
RW
0x00000000 (0.0)
806D:2A
Limit 2 (Real32)
REAL32
RW
0x00000000 (0.0)
806D:2B
Steady state Window
UINT16
RW
0x0064 (100dec)
806D:2C
REAL32
RW
0x3F806000 (1065353216dec)
806D:2D
REAL32
RW
806D:2E
REAL32
RW
Index 806F RMB Vendor Calibration Data Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
806F:0
Max. subindex
UINT8
RO
0x08 (8dec)
806F:01
Calibration Data
OCTET STRING[4]
RW
{0}
806F:03
S0
REAL32
RW
0x00000000 (0dec)
806F:04
S1
REAL32
RW
0x00000000 (0dec)
806F:05
S2
REAL32
RW
0x00000000 (0dec)
806F:06
S3
REAL32
RW
0x00000000 (0dec)
806F:07
T1
REAL32
RW
0x00000000 (0dec)
806F:08
T1S1
REAL32
RW
0x00000000 (0dec)
Index 8070 RMB Sensor Settings Ch.2 (ED3362-0100 only)
Index (hex)
Meaning
Data type
Flags
Default
8070:0
UINT8
RO
0x28 (40dec)
8070:23
Sensitivity
REAL32
RW
8070:24
Nominal Load
REAL32
RW
8070:25
Zero Balance
REAL32
RW
0x00000000 (0dec)
8070:26
Gravity of Earth
REAL32
RW
8070:27
Scale factor
Scaling factor
REAL32
RW
8070:28
Reference load
REAL32
RW
Index F800 DEV Settings
Index (hex)
Meaning
Data type
Flags
Default
F800:0
DEV Settings
Max. subindex
UINT8
RO
0x01 (1dec)
F800:01
Sensor supply
Values:
0 – OFF
5000 – 5 V
10000 – 10 V
UINT16
RW
0x2710 (10000dec)