Configuration data
Index 8000 FB settings
Index (hex)
Meaning
Data type
Flags
Default
8000:0
FB Settings
Maximum subindex
UINT8
RO
0x13 (19dec)
8000:01
Invert feedback direction
Inverting the count direction
BOOLEAN
RW
0x00 (0dec)
8000:02
Referenced
The box sets this parameter to FALSE in two cases:
  • If a motor with a different serial number was detected.
  • If a motor with single-turn encoder was connected.
If you want to use this function, set the parameter to TRUE and monitor it.
The value of this parameter is retained if the power supply is interrupted.
BOOLEAN
RW
0x00 (0dec)
8000:11
Device type
3: OCT (not changeable)
UINT32
RW
0x00000003 (3dec)
8000:12
Singleturn bits
Number of single-turn bits
UINT8
RW
0x14 (20dec)
8000:13
Multi-turn bits
Number of multi-turn bits
UINT8
RW
0x0C (12dec)
8000:14
Observer bandwidth
Bandwidth of the speed observer [Hz]
UINT16
RW
0x01F4 (500dec)
8000:15
Observer feed-forward
Load ratio [%]
100% = load-free
50% = mass moments of inertia of input and output are equal
UINT8
RW
0x01 (0dec)
8000:17
Position Offset
UINT32
RW
0x00000000 (0dec)
Index 8008 FB OCT Settings
Index (hex)
Meaning
Data type
Flags
Default
8008:0
FB OCT Settings
Maximum subindex
UINT8
RO
0x00 (0dec)
8008:01
Enable autoconfig
Configuration takes place automatically after the reading of the electronic type plate
(see Automatic scanning of the electronic type plates)
BOOLEAN
RW
0x00 (0dec)
8008:02
Reconfig identical motor
When replacing identical motors, reconfiguration takes place automatically after reading the electronic type plate. Enable autoconfig must be activated.
BOOLEAN
RW
0x00 (0dec)
8008:03
Reconfig non-identical motor
When replacing non-identical motors, reconfiguration takes place automatically after reading the electronic type plate. Enable autoconfig must be activated.
BOOLEAN
RW
0x00 (0dec)
Index 8010 DRV Amplifier Settings
Index (hex)
Meaning
Data type
Flags
Default
8010:0
Maximum subindex
UINT8
RO
0x42 (66dec)
8010:01
Enable TxPDOToggle
Show TxPDO toggle in status word (bit 10)
BOOLEAN
RW
0x00 (0dec)
8010:02
Enable input cycle counter
1: enabled
Two-bit counter that is incremented with each process data cycle up to a maximum value of 3, after which it starts again at 0
The low bit is represented in bit 10 and the high bit in bit 14 of the Status word.
BOOLEAN
RW
0x00 (0dec)
8010:11
Device type
1: Servo drive (cannot be changed)
UINT32
RW
0x00000001 (1dec)
8010:12*
Current loop integral time
Integral component of current controller
Unit: 0.1 ms
This value is affected by automatic scanning.
(see Automatic scanning of the electronic identification plates)
UINT16
RW
0x000A (10dec)
8010:13*
Current loop proportional gain
Proportional component of current controller
Unit: 0.1 V/A
UINT16
RW
0x0064 (100dec)
8010:14
Velocity loop integral time
Integral component of velocity controller
Unit: 0.1 ms
UINT32
RW
0x00000032 (50dec)
8010:15
Velocity loop proportional gain
Proportional component of velocity controller
Unit: mA / (rad/s)
UINT32
RW
0x00000096 (150dec)
8010:17
Position loop proportional gain
Proportional component position controller
Unit: (rad/s) / rad
UINT32
RW
0x0000000A (10dec)
8010:19
Nominal DC link voltage
Unit: mV
UINT32
RW
0x0000BB80 (48000dec)
8010:1A
Min DC link voltage
Minimum DC link voltage
Unit: mV
UINT32
RW
0x00001A90 (6800dec)
8010:1B
Max DC link voltage
Maximum DC link voltage
Unit: mV
UINT32
RW
0x0000EA60 (60000dec)
8010:29
Amplifier I2T warn level
I²T model warning threshold
Unit: %
UINT8
RW
0x50 (80dec)
8010:2A
Amplifier I2T error level
I²T model error threshold
Unit: %
UINT8
RW
0x69 (105dec)
8010:2B
Amplifier Temperature warn level
Overtemperature warning threshold
Unit: 0.1 °C
UINT16
RW
0x0320 (800dec)
8010:2C
Amplifier Temperature error level
Overtemperature error threshold
Unit: 0.1 °C
UINT16
RW
0x03E8 (1000dec)
8010:31
Velocity limitation
Velocity limitation
Unit: rpm
UINT32
RW
0x00040000 (262144dec)
8010:32
Short-Circuit Brake duration max
Max. duration of armature short circuit brake
Unit: ms
UINT16
RW
0x03E8 (1000dec)
8010:33
Stand still window
Standstill window
Unit: rpm
UINT16
RW
0x0000 (0dec)
*) see index 9009 FB OCT Nameplate
Index (hex)
Meaning
Data type
Flags
Default
8010:39
Select info data 1
Selection "Info data 1"
Optional display of additional information in the cyclic process data. The following parameters are available.
UINT8
RW
0x01 (1dec)
Torque current (filtered 1ms) [1000th of rated current]
DC link voltage [mV]
PCB temperature [0.1 °C]
Errors:
Bit0: ADC Error
Bit1: Overcurrent
Bit 2: Undervoltage
Bit 3: Overvoltage
Bit 4: Overtemperature
Bit 5: I2T Amplifier
Bit 6: I2T Motor
Bit 7: Encoder
Bit 8: Watchdog
Warnings:
Bit 2: Undervoltage
Bit 3: Overvoltage
Bit 6: I2T Motor
Bit 7: Encoder
I2T Motor [%]
I2T Amplifier [%]
Input Level:
Bit0: Digital Input 1 Level
Bit1: Digital Input 2 Level
Bit8: HWE Level
Feature Bits:
Bit0: Referenced (Parameter 8000:02)
8010:3A
Select info data 2
Selection "Info data 2"
UINT8
RW
0x01 (1dec)
Errors:
Bit0: ADC Error
Bit1: Overcurrent
Bit 2: Undervoltage
Bit 3: Overvoltage
Bit 6: I2T Motor
Bit 7: Encoder
Bit 8: Watchdog
Warnings:
Bit 2: Undervoltage
Bit 3: Overvoltage
Bit 6: I2T Motor
Bit 7: Encoder
I2T Motor [%]
I2T Amplifier [%]
Input Level:
Bit8: HWE Level
Feature Bits:
8010:41
Low-pass filter frequency
Unit: Hz
The following values can be set:
0 Hz = off
160 Hz
320 Hz
UINT16
RW
0x0140 (320dec)
8010:49
Halt ramp deceleration
Unit: 0.1 rad / s²
UINT32
RW
0x0000F570 (62832dec)
8010:50
Following error window
Following error monitor: Following error window
Unit: the given value must be multiplied by the corresponding scaling factor
0xFFFFFFFF (-1dec) = following error monitor off
Any other value = following error monitor on
UINT32
RW
0xFFFFFFFF (-1 dec)
8010:51
Following error time out
Following error monitor: Timeout
Unit: ms
If the following error is larger than the following error window for a time that exceeds the timeout, this leads to an error reaction
UINT16
RW
0x0000 (0 dec)
8010:52
Fault reaction option code
Permitted values
0: Disable drive function, motor is free to rotate
1: Slow down on slow down ramp
UINT16
RW
0x0000 (0 dec)
8010:53
Unit: mA / (rad/s)
UINT32
RW
0x00000000 (0 dec)
8010:54
Feature bits
The adjustable motor current values can be interpreted as peak values or rms values. The feature bit enables the conversion.
Peak value → Bit 0 = 0 (default)
RMS value → Bit 0 = 1
normal output current → Bit 1 = 0 (default)
increased output current → Bit 1 = 1
From these, the following combinations can be set:
0dec → normal output current interpreted as peak value
1dec → normal output current interpreted as rms value
2dec → increased output current interpreted as peak value
3dec → increased output current interpreted as rms value
UINT32
RW
0x00000000 (0 dec)
Index 8011 DRV Motor Settings
Index (hex)
Meaning
Data type
Flags
Default
8011:0
DRV Motor Settings
Maximum subindex
UINT8
RO
0x2D (45dec)
8011:11*
Max current
Peak current
Unit: mA
The adjustable motor current values can be interpreted as peak values or rms values. The feature bit (8010:54) enables the conversion.
UINT32
RW
0x00001770 (6000dec)
8011:12*
Rated current
Nominal current
Unit: mA
UINT32
RW
0x000003E8 (1000dec)
8011:13*
Motor pole pairs
Number of pole pairs
UINT8
RW
0x03 (3dec)
8011:15*
Commutation offset
Commutation offset (between electrical zero position and mechanical single-turn zero position)
Unit:
INT16
RW
0x0000 (0dec)
8011:16*
Torque constant
Torque constant
Unit: mNm / A
UINT32
RW
0x00000000 (0dec)
8011:18*
Rotor moment of inertia
Mass moment of inertia of the motor
Unit: g cm^2
UINT32
RW
0x00000000 (0dec)
8011:19*
Winding inductance
Inductance
Unit: 0.1 mH
UINT16
RW
0x000E (14dec)
8011:1B*
Motor speed limitation
Velocity limitation
Unit: rpm
UINT32
RW
Index (hex)
Meaning
Data type
Flags
Default
8011:29
I2T warn level
I2T model warning threshold
Unit: %
UINT8
RW
0x50 (80dec)
8011:2A
I2T error level
I2T model error threshold
Unit: %
UINT8
RW
0x69 (105dec)
8011:2B*
Motor Temperature warn level
Unit: 0.1 °C
UINT16
RW
0x03E8 (1000dec)
8011:2C*
Motor Temperature error level
Unit: 0.1 °C
UINT16
RW
0x05DC (1500dec)
8011:2D*
Motor thermal time constant
Thermal time constant
Unit: 0.1 s
UINT16
RW
0x0028 (40dec)
Index 8012 DRV Brake Settings
Index (hex)
Meaning
Data type
Flags
Default
8012:0
DRV Brake Settings
Maximum subindex
UINT8
RO
0x14 (20dec)
8012:01
Enable manual override
Manual release of the motor holding brake
BOOLEAN
RW
0x00 (0dec)
8012:02
Manual brake state
0: Release
Release the brake
1: Apply
Apply the brake
BOOLEAN
RW
0x00 (0dec)
8012:11*
Release delay
Time the holding brake requires for opening (releasing) after the current was applied
UINT16
RW
0x0000 (0dec)
8012:12*
Application delay
Time the holding brake requires for closing (holding) after the current was switched off
UINT16
RW
0x0000 (0dec)
8012:13
Emergency application timeout
Time the amplifier waits, until the rotation speed reaches the stand still window after stop request (set rotation speed 0 or Torque off). If the set waiting time is exceeded, the holding brake is triggered independently of the rotation speed.
Note:
For rotatory axes and the setting „torque off“ in error case, this parameter has to be set at least to the „coast to the stop“ time of the axis.
For suspended (hanging) axes and the setting „torque off“ in error case, this parameter has to be set to an appropriate short time, to prevent the axis/load from drop/fall.
UINT16
RW
0x0000 (0dec)
8012:14*
Brake moment of inertia
Mass moment of inertia of the brake
Unit: g cm^2
UINT16
RW
0x0000 (0dec)
*) see index 0x9009 FB OCT Nameplate
Index 8030 DMC settings
Index (hex)
Meaning
Data type
Flags
Default
8030:0
DMC settings
Maximum subindex
UINT8
RO
0x14 (20dec)
8030:07
Emergency deceleration
Deceleration for the emergency stop ramp. (In ms from rated motor speed to standstill)
Unit: 1 ms
UINT16
RW
0x64 (100dec)
8030:08
Calibration position
If homing is successful, the "Actual position" is set to this value.
INT64
RW
0x0000000000000000 (0dec)
8030:09
Calibration velocity (towards plc cam)
Velocity on contact with the cam in 10000ths of the rated motor speed
INT16
RW
0x0064 (100dec)
8030:0A
Calibration velocity (off plc cam)
Velocity on separation from the cam in 10000ths of the rated motor speed
INT16
RW
0x000A (10dec)
8030:0E
Modulo factor
Feedback increments for one mechanical revolution
INT64
RW
0x0000000100000000 (4294967296dec)
8030:12
Block calibration torque limit
Torque limitation for approaching the end stop. In 1000ths of the rated motor current.
UINT16
RW
0x64 (100dec)
8030:13
Block calibration stop distance
After reaching the calibration position, the axis moves out of the end position by this distance.
INT64
RW
8030:14
Block calibration lag threshold
If this lag distance is exceeded, the axis is in the end position
INT64
RW
8030:15
Target position window
Target position window:
The In-Target bit is set when the axis is within this window for at least the time set under 0x8030:16.
INT64
RW
0x16c16c1
8030:16
Target position monitor time
s. 0x8030:15 time in
Unit: ms
UINT16
RW
0x0014 (20dec)
8030:17
Target position timeout
When the set value generator has reached its end position
and the axis is not in the target window after this time has elapsed,
the task is terminated and the in-target bit is not set.
UINT16
RW
0x1770 (6000dec)
Index 8031 DMC features
Index (hex)
Meaning
Data type
Flags
Default
8031:0
DMC features
Maximum subindex
UINT8
RO
0x1B (27dec)
8031:13
Invert calibration cam search direction
Invert travel direction to search for limit switch
(Default: FALSE = search with positive direction of rotation)
BOOLEAN
RW
0x00 (0dec)
8031:14
Invert sync impulse search direction
BOOLEAN
RW
0x01 (1dec)
8031:19
Calibration cam source
Source for the reference switch
0: Input 1
1: Input 2
ENUM8
RW
0x00 (0dec)
8031:1A
Calibration cam active level
State of the reference switch in the actuated state
0: Hi
1: Low
ENUM8
RW
0x00 (0dec)
8031:B
Latch source
Source for the latch unit
0: Input 1
1: Input 2
ENUM8
RW
0x00 (0dec)