ReactivePower
The parameters of the ReactivePower
group are used to set the reactive power control (see Reactive power controller).
Name | Default | Min | Max | Unit | Data type |
| 100.0 | 1.0 |
| REAL |
Active power scaling for process data (1.0 = per unit, 100.0 = percent) | |||||
| -33.0 | -100.0 | 0.0 | % | REAL |
Maximum possible reactive power of the underexcited plant | |||||
| +33.0 | +100.0 | 0.0 | % | REAL |
Maximum possible reactive power of the overexcited plant | |||||
Mode of the reactive power controller on default, failure or restart | |||||
| 10 | 0 |
| ms | TIME |
Filter time of reactive power measurement | |||||
| PT1 | ||||
Filter type of reactive power measurement | |||||
| 0.0 | -100.0 | +100.0 | % | REAL |
Reactive power setpoint in the event of communication failure | |||||
| 2000 | 0 |
| ms | TIME |
Filter time of control value of reactive power | |||||
| PT1 | ||||
Filter type of control value of reactive power | |||||
| 0 | 0 |
| ms | TIME |
Dead time of plant for compensation in the reactive power controller (0 = disabled) | |||||
| 0 | 0 |
| ms | TIME |
First order (PT1) filter time constant of plant for compensation for compensation in the reactive power controller (0 = disabled) | |||||
| 75.0 | 0.1 | 200.0 | % | REAL |
Proportional gain in the reactive power controller | |||||
| 200 | 0 |
| ms | TIME |
Integration time constant in the reactive power controller |