ActivePower
The parameters of the ActivePower group are used to set the active power control (see Active power controller).
Default
Min
Max
Unit
Data type
ActiveNominal
10000000
1.0
W/pu
REAL
Nominal power of the power generating plant (Pnom)
ActiveScale
100.0
1.0
REAL
Active power scaling for process data (1.0 = per unit, 100.0 = percent)
ActiveMinimum
0.0
-200.0
200.0
REAL
Minimum possible active power of the plant
ActiveMaximum
100.0
-200.0
+200.0
REAL
Maximum possible active power of the plant
ActiveModeDefault
Normal
ETcPowerPlantActiveMode
Mode of the active power controller on default, failure or restart
ActiveActualFilterTime
10
0
ms
TIME
Filter time of active power measurement
ActiveActualFilterType
PT1
ETcPowerFilterType
Filter type of active power measurement
ActiveTargetDefault
100.0
0.0
100.0
REAL
Active power setpoint in the event of communication failure
ActiveTargetSlopeNormal
0.5
0.1
0.66
%/s
REAL
Gradient of the active power setpoint in normal operation
ActiveTargetSlopeCritical
0.167
0.01
0.66
%/s
REAL
Gradient of the active power setpoint in grid-critical operation (overfrequency or underfrequency)
ActiveTargetSlopeRestart
0.5
0.1
50.0
%/s
REAL
Gradient of the active power setpoint at restart
ActiveTargetSlopeReconnect
0.5
0.1
50.0
%/s
REAL
Gradient of the active power setpoint when reconnected
ActivePredictDeadTime
0
0
ms
TIME
System dead time for compensation in the active power controller (0 = disabled)
ActivePredictFilterTime
0
0
ms
TIME
System transmission time for compensation in the active power controller (0 = disabled)
ActiveControlGain
75.0
0.001
200.0
REAL
Proportional gain in the active power controller
ActiveControlIntegration
500
0
ms
TIME
Integration time constant in the active power controller