ActivePower
The parameters of the ActivePower group are used to set the active power control (see Active power controller).
Name | Default | Min | Max | Unit | Data type |
| 10000000 | 1.0 |
| W/pu | REAL |
Nominal power of the power generating plant (Pnom) | |||||
| 100.0 | 1.0 |
| REAL |
Active power scaling for process data (1.0 = per unit, 100.0 = percent) | |||||
| 0.0 | -200.0 | 200.0 | % | REAL |
Minimum possible active power of the plant | |||||
| 100.0 | -200.0 | +200.0 | % | REAL |
Maximum possible active power of the plant | |||||
| Normal | ||||
Mode of the active power controller on default, failure or restart | |||||
| 10 | 0 |
| ms | TIME |
Filter time of active power measurement | |||||
| PT1 | ||||
Filter type of active power measurement | |||||
| 100.0 | 0.0 | 100.0 | % | REAL |
Active power setpoint in the event of communication failure | |||||
| 0.5 | 0.1 | 0.66 | %/s | REAL |
Gradient from the active power setpoint in normal operation | |||||
| 0.167 | 0.01 | 0.17 | %/s | REAL |
Gradient from the active power setpoint in grid-critical operation (overfrequency or underfrequency) | |||||
| 0.5 | 0.1 | 50.0 | %/s | REAL |
Gradient of the active power setpoint at restart | |||||
Gradient of the active power setpoint when reconnected | |||||
| 0 | 0 |
| ms | TIME |
Dead time of plant for compensation in the active power controller (0 = disabled) | |||||
| 0 | 0 |
| ms | TIME |
First order (PT1) filter time constant of plant for compensation in the active power controller (0 = disabled) | |||||
| 100.0 | 0.1 | 200.0 | % | REAL |
Proportional gain in the active power controller | |||||
| 500 | 0 |
| ms | TIME |
Integration time constant in the active power controller | |||||