FB_BA_LoopSync
FB_BA_LoopSync 1:
The FB_BA_LoopSync function block is used for parameter synchronization for two controllers of type FB_BA_Loop. This function block can be used, for example, to calibrate master controllers that are used to generate the supply air setpoints for an air conditioning system.
The following parameters of the FB_BA_Loop are synchronized:
Error detection
The error messages listed below are detected by the FB_BA_LoopSync.
The error messages are output in the TwinCAT 3 development environment in the "Error list" window. This can be activated under the "View" menu item.
The error texts are output via the property ErrText and the output sErrText.
In addition, the messages are displayed by the enum eErrState.
Error messages
Message text German
Message text English
Explanation
'Synchronisation eActionRm fehlerhaft'
'Synchronization eActionRm faulty'
Possibly the wrong synchronization can be triggered by the input eActionPgm. This input overwrites the VAR_INPUT CONSTANT variable eActionRm to be monitored when occupied.
'Synchronisation nDampConstant fehlerhaft'
'Synchronization nDampConstant faulty'
It is possible that the wrong synchronization was triggered by the input eActionPgm. This input overwrites the VAR_INPUT CONSTANT variable eActionRm to be monitored when occupied.
'Synchronisation fDerivativeConstant fehlerhaft'
'Synchronization fDerivativeConstant faulty'
'Synchronisation fIntegralConstant fehlerhaft'
'Synchronization fIntegralConstant faulty'
'Synchronisation fMaxOutputRm fehlerhaft'
'Synchronization fMaxOutputRm faulty'
Possibly the wrong synchronization can be triggered by the input fMaxOutputPgm. This input overwrites the VAR_INPUT CONSTANT variable fMaxOutputRm to be monitored when occupied.
'Synchronisation fMinOutputRm fehlerhaft'
'Synchronization fMinOutputRm faulty'
Possibly the wrong synchronization can be triggered by the input fMinOutputPgm. This input overwrites the VAR_INPUT CONSTANT variable fMinOutputRm to be monitored when occupied.
'Synchronisation fNeutralZone fehlerhaft'
'Synchronization fNeutralZone faulty'
'Synchronisation eOpMode fehlerhaft'
'Synchronization eOpMode faulty'
'Synchronisation fProportionalConstant fehlerhaft'
'Synchronization fProportionalConstant faulty'
FUNCTION_BLOCK FB_BA_LoopSync
  bErr         : BOOL;
  sErrText     : T_MaxString;
  eErrState    : E_BA_StateLoopSync;
  Loop01       : FB_BA_Loop;
  Loop02       : FB_BA_Loop;
FB_BA_LoopSync 2: Outputs
Type
bErr
The output indicates when an error has occurred during synchronization.
sErrText
T_MaxString
The variable shows the state of synchronization in text form.
eErrState
E_BA_StateLoopSync
The enumeration shows the state of the synchronization.
FB_BA_LoopSync 3: / FB_BA_LoopSync 4: Inputs Outputs
Type
Loop1
FB_BA_Loop
Reference to controller no. 1 of the parameter adjustment.
Loop2
FB_BA_Loop
Reference to controller no. 2 of the parameter adjustment.
FB_BA_LoopSync 5: Properties
Type
Access
ErrText
T_MaxString
Get
The property ErrText displays the error texts from sErrText.
Development environment
Required PLC library
TwinCAT from v3.1.4024.56