FB_BA_AC_SpTRm_02
FB_BA_AC_SpTRm_02 1:
The template is a setpoint program for an air conditioning system.
It serves as a setpoint program for an extract air/supply air cascade with a separate room temperature setpoint for heating and cooling mode, including summer and winter compensation.
There are two basic room temperature setpoints (SpHtgY1, SpColY1), with an energy-neutral zone between the lower setpoint (heating mode) and the upper setpoint (cooling mode). An outside temperature-dependent offset of the basic room temperature setpoints is realized via two curve functions (summer/winter compensation).
FB_BA_AC_SpTRm_02 2:
FB_BA_AC_SpTRm_02 3:
The initialization of the template takes place within the method FB_Init.
Block diagram
FB_BA_AC_SpTRm_02 4:
Principle diagram01
FB_BA_AC_SpTRm_02 5:
Principle diagram02
FB_BA_AC_SpTRm_02 6:
FUNCTION_BLOCK FB_BA_AC_SpTRm_02 EXTENDS FB_BA_View
  fTWth         : REAL;
  fSpHtg        : REAL;
  fSpCol        : REAL;
VAR_INPUT CONSTANT
  SpColX1       : FB_BA_AV_Op;
  SpColX2       : FB_BA_AV_Op;
  SpColY1       : FB_BA_AV_Op;
  SpColY2       : FB_BA_AV_Op;
  SpHtgX1       : FB_BA_AV_Op;
  SpHtgX2       : FB_BA_AV_Op;
  SpHtgY1       : FB_BA_AV_Op;
  SpHtgY2       : FB_BA_AV_Op;
  SpHtg         : FB_BA_AV_Op;
  SpCol         : FB_BA_AV_Op;
  SpColScale    : FB_BA_Chrct02;
  SpHtgScale    : FB_BA_Chrct02;
FB_BA_AC_SpTRm_02 7: Inputs CONSTANT
Type
fTWth
REAL
Current value of the outside temperature.
FB_BA_AC_SpTRm_02 8: Outputs
Type
fSpHtg
REAL
Calculated setpoint of the supply air temperature for the heater.
fSpCol
REAL
Calculated setpoint of the supply air temperature for the cooler.
FB_BA_AC_SpTRm_02 9: Inputs CONSTANT
Type
SpColX1
FB_BA_AV_Op
Input of the value for interpolation point X1 of the summer compensation for the cooling setpoint.
SpColX2
FB_BA_AV_Op
Input of the value for interpolation point X2 of the summer compensation for the cooling setpoint.
SpColY1
FB_BA_AV_Op
Input of the value for interpolation point Y1 of the summer compensation for the cooling setpoint.
SpColY1 is the base cooling setpoint.
SpColY2
FB_BA_AV_Op
Input of the value for interpolation point Y2 of the summer compensation for the cooling setpoint.
SpHtgX1
FB_BA_AV_Op
Input of the value for interpolation point X1 of the winter compensation for the heating setpoint.
SpHtgX2
FB_BA_AV_Op
Input of the value for interpolation point X2 of the winter compensation for the heating setpoint.
SpHtgY1
FB_BA_AV_Op
Input of the value for interpolation point Y1 of the winter compensation for the heating setpoint.
SpHtgY1 is the base heating setpoint.
SpHtgY2
FB_BA_AV_Op
Input of the value for interpolation point Y2 of the winter compensation for the heating setpoint.
SpHtg
FB_BA_AV_Op
Analog value object for displaying the calculated room temperature setpoint heating.
SpCol
FB_BA_AV_Op
Analog value object for displaying the calculated room temperature setpoint cooling.
Variables
Type
SpColScale
FB_BA_Chrct02
The function block calculates the characteristic cooling setpoint curve (summer compensation) for the current room temperature as a function of the outside temperature.
FB_BA_AC_SpTRm_02 10:
SpHtgScale
FB_BA_Chrct02
The function block calculates the characteristic heating setpoint curve (winter compensation) for the current room temperature as a function of the outside temperature.
FB_BA_AC_SpTRm_02 11: