FB_BA_HeatCool_PID
FB_BA_HeatCool_PID 1:
This template is used to control a heating-cooling zone.
The priority selection EnergLvlSlcn first determines the currently valid energy level.
The window contact always has priority and switches to the energy level "Protection" when the window is open. When there is a presence in the room, the "Comfort" level is always activated.
The function block RmTAdj is used for a local shift of the room temperature setpoint for the energy levels "Pre-Comfort" and "Comfort".
The setpoint is shifted via a local input value fRmTAdj or via an external value fRmTAdj_In which is read via the base class FB_BA_Ext_SunblindAngle (internal function block), for example via a HMI. The value that was last changed is always valid; the function block FB_BA_LastWriterWins_R04 is responsible for this. The room temperature value is limited to +/- fRmTAdjLimit (predefined to 1.0 in FB_init).
The instance FnctSel of the function block FB_BA_FnctSel enables the heating or cooling controller of the temperature zone.
Data exchange HMI
The data exchange with the HMI is realized here in the base class FB_BA_Ext_HeatCoolBase (internal function block). The use of the following variables is visible in this template:
FB_BA_HeatCool_PID 2:
The initialization of the template takes place within the method FB_Init.
Block diagram
FB_BA_HeatCool_PID 3:
FUNCTION_BLOCK FB_BA_HeatCool_PID EXTENDS FB_BA_Ext_HeatCoolBase
  bPrc                    : BOOL;
  bWdwCon                 : BOOL;
  eMedium                 : E_BA_Medium;
  bDewPnt                 : BOOL;
  fRmT                    : REAL;
  fRmTAdj                 : REAL;
  stBuildingSpRmT         : ST_BA_SpRmT;
  eBuildingEnergyLevel    : E_BA_EnergyLvlEx;
  bCtrlHtgActv            : BOOL;
  fCtrlValHtg             : REAL;
  bCtrlColActv            : BOOL;
  fCtrlValCol             : REAL;
  eReqdMedium             : E_BA_Medium;
VAR_INPUT CONSTANT PERSISTENT
  ePipeSys                : E_BA_PipeSys;
  nFnctSelChgOvrDly       : UDINT;
  fRmTAdjLimit            : REAL;
VAR_INPUT CONSTANT
  CtrlHtg                 : FB_BA_Loop;
  CtrlCol                 : FB_BA_Loop;
  RmTAdj                  : FB_BA_RmTAdj;
  EnergLvlSlcn            : FB_BA_PrioSwi_UDI04;
  SpSlcnHtg               : FB_BA_MUX_R04;
  SpSclnCol               : FB_BA_MUX_R04;
  FnctSel                 : FB_BA_FnctSel;
FB_BA_HeatCool_PID 4: Inputs
Type
bPrc
Presence detection.
bWdwCon
Window contact (open = TRUE).
eMedium
E_BA_Medium
Medium present (heating or cooling medium, only important for two-pipe operation).
bDewPnt
Dew point sensor (alarm = TRUE).
fRmT
Room temperature [°C].
fRmTAdj
REAL
Room setpoint shift [K].
stBuildingSpRmT
ST_BA_SpRmT
Structure of room setpoints (Protection Cooling...Comfort Cooling and Protection Heating...Comfort Heating).
E_BA_EnergyLvlEx
Current building energy level.
FB_BA_HeatCool_PID 5: Outputs
Type
bCtrlHtgActv
Heating controller is active.
fCtrlValHtg
REAL
Control value heating valve.
bCtrlColActv
Cooling controller is active.
fCtrlValCol
REAL
Control value cooling valve.
eReqdMedium
E_BA_Medium
Requested medium (heating or cooling medium).
FB_BA_HeatCool_PID 6: Inputs CONSTANT PERSISTENT
Type
ePipeSys
E_BA_PipeSys
Selection of two or four-pipe system.
nFnctSelChgOvrDly
UDINT
Switchover delay [s] from heating to cooling or vice versa.
fRmTAdjLimit
REAL
Adjustable range [K] of the setpoint shift fRmTAdj : -fRmTAdjLimit <= fRmTAdj <= +fRmTAdjLimit.
FB_BA_HeatCool_PID 7: Inputs CONSTANT
Type
CtrlHtg
FB_BA_Loop
Heating controller.
CtrlCol
FB_BA_Loop
Cooling controller.
Variables
Type
RmTAdj
FB_BA_RmTAdj
Function block that applies the sh to the corresponding setpoints and outputs them explicitly.
EnergLvlSlcn
FB_BA_PrioSwi_UDI04
Prioritizing selection and conversion of the possible energy levels into a numerical value.
SpSlcnHtg
FB_BA_MUX_R04
Selection of the heating setpoint.
SpSclnCol
FB_BA_MUX_R04
Selection of the cooling setpoint.
FnctSel
FB_BA_FnctSel
Function selection heating or cooling.