FB_BA_SunblindZone
FB_BA_SunblindZone 1:
In a blind zone, one or more blinds are combined for simultaneous control. The template FB_BA_SunblindZone bundles the predefined data of the facades and decides on the basis of a zone presence detection and local selection and deselection which functionality is active.
Together with the resulting telegram of high-priority functions from the facade, these functionalities are placed on a telegram selector at the end of the template. This then uses the priority to decide which telegram in the higher-level room template is passed on to the blinds.
Functions
Input stReferenceFeedback
Information about the controlled blind actuator or the reference actuator of a group is fed back into the blind control function via this input.
These are the position details and status of the reference actuator.
Data exchange HMI
The data exchange with the HMI is realized here in the base class FB_BA_Ext_SunblindAngle (internal function block). The use of the following variables is visible in this template:
FB_BA_SunblindZone 2:
The HMI is used to specify the lamella angles to be controlled in 0% (lamella at upper limit position fAnglLmtUp) to 100% (lamella at lower limit position fAnglLmtDwn), with 50% being the zero position (0° = lamella horizontal).
It must be ensured that the upper lamella angle is greater than 0° and the lower lamella angle is less than 0° at this point in order to be able to carry out the calculation correctly.
FB_BA_SunblindZone 3:
The initialization of the template takes place within the method FB_Init.
Block diagram
FB_BA_SunblindZone 4:
FUNCTION_BLOCK FB_BA_SunblindZone EXTENDS FB_BA_Ext_SunblindAngle
  fRoomTempSen           : REAL;
  bPrcDetc               : BOOL;
  bSwiUp                 : BOOL;
  bSwiDwn                : BOOL;
  bRstManFnct            : BOOL;
  stBuildingSpRmT        : ST_BA_SpRmT;
  stFacade               : ST_BA_Facade;
  stScene                : ST_BA_Sunbld;
  stReferenceFeedback    : ST_BA_SunblindActuatorFeedback;
  stSunBldOut            : ST_BA_SunBld;
VAR_INPUT CONSTANT PERSISTENT
  bThAutoSlcn            : BOOL;
  fThAutoColPos          : REAL;
  fThAutoColAngl         : REAL;
  bSunPrtcSlcn           : BOOL;
  bTwiLgtAutoSlcn        : BOOL;
  fTwiLgtAutoPos         : REAL;
  fTwiLgtAutoAngl        : REAL;
  nSwiOverTi             : UDINT;
VAR_INPUT CONSTANT
  ManSwi                 : FB_BA_SunBldSwi := (ePrio:= E_BA_SunBldPrio.eManualGroup);
  ThAuto                 : FB_BA_SunBldEvt := (ePrio:= E_BA_SunBldPrio.eGroupThermoAuto);
  SunPrtc                : FB_BA_SunBldEvt := (ePrio:= E_BA_SunBldPrio.eSunProtection);
  TwiLgtAuto             : FB_BA_SunBldEvt := (ePrio:= E_BA_SunBldPrio.eGroupTwiLightAuto);
  ThAutoSwi              : FB_BA_Swi2P;
  PrioSwi                : FB_BA_SunBldTgmSel8;
  EnSunBldSwi            : SR;
FB_BA_SunblindZone 5: Inputs
Type
fRoomtempSen
REAL
Room temperature sensor [°C].
bPrcDetc
Presence detection.
bSwiUp
Local push button "up".
bSwiDwn
Local push button "down".
bRstManFnct
Input for resetting all internal manual functions, both those via the inputs bSwiUp/bSwiDwn, and external control (e.g. HMI).
stBuildingSpRmT
ST_BA_SpRmT
Structure of room setpoints (Protection Cooling..Comfort Cooling and Protection Heating ... Comfort Heating).
stFacade
ST_BA_Facade
Facade-specific blind data and telegrams.
stScene
ST_BA_Sunbld
Reserved telegram input for scene control.
stReferenceFeedback
Feedback input of the controlled blind actuator or the reference actuator of the controlled group.
FB_BA_SunblindZone 6: Outputs
Type
stSunBldOut
ST_BA_SunBld
resulting zone telegram.
FB_BA_SunblindZone 7: Inputs CONSTANT PERSISTENT
Type
bThAutoSlcn
Thermal automatic enable.
fThAutoColPos
REAL
Thermal automatic cooling position [%].
fThAutoColAngl
REAL
Thermal automatic cooling angle [°].
bSunPrtcSlcn
Shading automatic enable.
bTwiLgtAutoSlcn
Twilight automatic enable.
fTwiLgtAutoPos
REAL
Twilight automatic position [%].
fTwiLgtAutoAngl
REAL
Twilight automatic position [°].
nSwiOverTi
UDINT
Changeover time [ms] of the manual switch SunBldSwi for latching.
FB_BA_SunblindZone 8: Inputs CONSTANT
Type
ManSwi
FB_BA_SunBldSwi
Group (zone) push button block.
ThAuto
FB_BA_SunBldEvt
Telegram block for group (zone) thermal automatic.
SunPrtc
FB_BA_SunBldEvt
Telegram block for group (zone) shading automatic.
TwiLgtAuto
FB_BA_SunBldEvt
Telegram block for group (zone) twilight automatic.
Type
ThAutoSwi
FB_BA_Swi2P
Hysteresis block for heating/cooling changeover for group (zone) thermal automatic.
PrioSwi
FB_BA_SunBldTgmSel8
Selection of the resulting telegram.
EnSunBldSwi
SR
Activation memory of the above mentioned function block.
Development environment
Necessary function
TwinCAT from v3.1.4024.35
TF8040 | TwinCAT Building Automation from V5.0.0.0
