FB_BA_SunBldIcePrtc
The function block FB_BA_SunBldIcePrtc deals with direction-independent anti-icing.
Weather protection has the highest priority for blind control (see Overview) and should ensure that the blind is not damaged by ice.
Impending icing up is detected when the measured outside temperature fOtsT falls below the frost limit value fFrstT while at the same time rain is detected on bRainSns. This event is saved internally and remains active until it is ensured that the ice has melted again. In addition, the outside temperature must have exceeded the frost limit value for the entered deicing time nDeiceTi [s]. For safety reasons the icing event is persistently saved, i.e. also beyond a PLC failure. Thus, if the controller fails during the icing up or deicing period, the blind is considered to be newly iced up when then the controller restarts and the deicing timer starts from the beginning again.
If there is a risk of icing, the blind is moved to the protection position specified by fPosProt (height position [%]) and fAnglProt (lamella angle [°]).
bEn : BOOL;
fOtsT : REAL;
bRainSns : BOOL;
fFrstT : REAL;
nDeiceTi : UDINT;
fPosProt : REAL;
fAnglProt : REAL;
bEn | BOOL | A TRUE signal on this input activates the function block and transfers the entered setpoints together with the active flag in the positioning telegram ST_BA_SunBld. A FALSE signal resets the active flag again and sets position and angle to zero. bActv is FALSE. This means that another function takes over control of the blind via the priority controller. |
fOtsT | REAL | Outside temperature [°C] |
bRainSns | BOOL | Input for a rain sensor. |
fFrstT | REAL | Icing up temperature limit value [°] Celsius. This value may not be greater than 0. Otherwise an error is output. |
nDeiceTi | UDINT | Time until the deicing of the blind after icing up [s]. After that the ice alarm is reset. |
fPosProt | REAL | Height position of the blind [%] in the case of protection. |
fAnglProt | REAL | Lamella angle of the blind [°] in the case of protection. |
Inputs CONSTANT PERSISTENT
VAR_INPUT CONSTANT PERSISTENT
ePrio : E_BA_SunBldPrio := E_BA_SunBldPrio.eIce;
ePrio | Priority of the active telegram. |
Outputs
stSunBld : ST_BA_SunBld;
bActv : BOOL;
bIceAlm : BOOL;
nRemTiIceAlm : UDINT;
stSunBld | Output structure of the blind positions. | |
bActv | BOOL | Corresponds to the boolean value bActv in the blind telegram ST_BA_SunBld and is solely used to indicate whether the function block sends an active telegram. |
bIceAlm | BOOL | Indicates the icing up alarm. |
nRemTiIceAlm | UDINT | In the case of impending icing up (bIceAlm = TRUE), this second counter is set to the deicing time. As soon as the temperature lies above the frost point entered (fFrstT), the remaining number of seconds until the 'all-clear' signal is given (bIceAlm = FALSE) is displayed here. This output is 0 as long as no countdown of the time is taking place. |
![]() | If an error occurs, this automatic control is disabled and the position and angle are set to 0. This means that if a priority controller is in use, another function with a lower priority (see Overview) automatically takes over control of the blind. In the case of a direct connection, conversely, the blind will drive to position/angle 0. |
TwinCAT from v3.1.4024.22 | Tc3_BA2 from v5.2.5.0 |
