FB_BA_LightActrDALI_TC
The FB_BA_LightActrDALI_TC function block is used to control a DALI light actuator, a DALI group or DALI devices with a broadcast, whereby color temperature control is supported.
Function
Four routines are executed in the function block:
- Setting the light value if it deviates from the current value. This is subjected to a hysteresis range nHysLgtVal, see below.
- Setting the color temperature if it deviates from the current value. This is subjected to a hysteresis range fHysLgtT, see below.
- Reading the light value. This is done cyclically at the interval nPrdQueryLgtVal in seconds.
- Reading the color temperature. This is done cyclically at the interval nPrdQueryLgtT in seconds.
The "current value" is always initially assumed to be the value that was sent without errors. The cyclic query of the respective read function will correct the value if a telegram is nevertheless "lost" or the control gear has been controlled in another way.
This procedure ensures that, on the one hand, the DALI bus is not overloaded, but on the other hand, the actual light value is always read.
The function block is controlled via values from the light telegram stLightingCmd. The control values of the light and the color temperature are limited to the limits that were previously transferred to the control gear or the devices by an initialization routine with other configuration parameters, see VAR_INPUT CONSTANT PERSISTENT. Initialization takes place via the input bInitialize. Fixed values are also transferred here, see VAR CONSTANT.
A color temperature setpoint of "0" is explicitly ignored. This allows telegrams to be generated that only influence the brightness, but not the color temperature previously set elsewhere.
The light value is set internally exclusively via the DALI command FB_DALI102DirectArcPowerControl. This means that the FadeTime is the time taken to dim to the new light value.
This dimming time is pre-set to 0 s so that dimming ramps can only be implemented in the PLC.
If group or broadcast control is selected, the control and initialization commands are directed to all devices. Read commands, on the other hand, are only sent to the reference device.
FUNCTION_BLOCK FB_BA_LightDALI_TC
bEn : BOOL;
bInitialize : BOOL;
stLightingCmd : ST_BA_Lighting;
eAdrType : Tc3_DALI.E_DALIAddressType := Tc3_DALI.E_DALIAddressType.Short;
nAdr : BYTE;
nAdrRefDev : BYTE;
ipDALICommunication : Tc3_DALI.I_DALICommunication;
nActlLgtVal : BYTE;
fActlLgtVal : REAL;
fActlLgtT : REAL;
bInitializing : BOOL;
bErr : BOOL;
nHysLgtVal : BYTE;
fHysLgtT : REAL;
nPrdQueryLgtVal : UDINT;
nPrdQueryLgtT : UDINT;
nMinLevel : BYTE := 126;
nMaxLevel : BYTE := 254;
nPowerOnLevel : BYTE := 254;
nSystemFailureLevel : BYTE := 254;
eFadeTime : Tc3_DALI.E_DALIFadeTime := Tc3_DALI.E_DALIFadeTime.Disabled;
eFadeRate : Tc3_DALI.E_DALIFadeRate := Tc3_DALI.E_DALIFadeRate.N358StepsPerSec;
fTemperatureLimitWarmest : LREAL := 2700;
fTemperatureLimitCoolest : LREAL := 6500;
fPowerOnTemperature : LREAL := 3000;
fSystemFailureTemperature : LREAL := 3000;
VAR CONSTANT
eExtendedFadeTimeBase : Tc3_DALI.E_DALIExtendedFadeTimeBase := Tc3_DALI.E_DALIExtendedFadeTimeBase.Base01;
eExtendedFadeTimeMultiplier : Tc3_DALI.E_DALIExtendedFadeTimeMultiplier := Tc3_DALI.E_DALIExtendedFadeTimeMultiplier.Disabled;
Name | Type | Description |
bEn | BOOL | Enabling the function block: a TRUE signal at this input enables the function. |
bInitialize | BOOL | A positive edge at this input starts the DALI initialization routine, which transfers the set parameters to the DALI device, see FB_BA_Swi4DALI. |
stLightingCmd | Light control telegram. | |
eAdrType | Defines whether the input nAdr contains a short address (0...63) or a group address (0...31). The nAdr input has no meaning if a broadcast is sent. | |
nAdr | BYTE | DALI address of the actuator or group. |
nAdrRefDev | BYTE | DALI address of a reference device if group or broadcast control is selected. This reference device then represents all other controlled devices. |
ipDALICommunication | Interface pointer to the DALI communication block. |
nActlLgtVal | BYTE | Current light value in DALI format (0...254). |
fActlLgtVal | REAL | Current light value in percent. |
fActlLgtT | REAL | Current color temperature in Kelvin. |
bInitializing | BOOL | The sensor is in the DALI initialization phase, i.e. the entered parameters are transferred to the DALI device. |
bErr | BOOL | Error output. A plain text is output in TwinCAT in the error list in the output window. |
nHysLgtVal | BYTE | Hysteresis range in DALI resolution around the light setpoint value. A new set command is started if the nHysLgtVal/2 setpoint is above or below the actual value. |
fHysLgtT | REAL | Hysteresis range in Kelvin around the color temperature setpoint value. A new set command is started if the nHysLgtVal/2 setpoint is above or below the actual value. |
nPrdQueryLgtVal | UDINT | Query interval of the light value [s]. |
nPrdQueryLgtT | UDINT | Query interval of the color temperature [s]. |
![]() | The following parameters are transferred to the DALI control gear or the DALI devices by the initialization routine. |
nMinLevel | BYTE | Minimum light control value in DALI output format (0...254). Pre-set to 126. |
nMaxLevel | BYTE | Maximum light control value in DALI output format (0...254). Pre-set to 254. |
nPowerOnLevel | BYTE | Light control value when the supply voltage is applied to the control gear. Pre-set to 254. |
nSystemFailureLevel | BYTE | Light control value in the event of an error on the DALI bus. Pre-set to 254. |
eFadeTime | The FadeTime defines the time the current output value takes to reach the required value. The FadeTime is pre-set to "disabled", which together with the deactivated "Extended FadeTime" (VAR CONSTANT) corresponds to a fade time of 0 s. | |
eFadeRate | The Fade Rate determines the rate of change (in steps per second) of the output value. It is not decisive for the behavior of this function block. It is pre-set to 358 steps/s. | |
fTemperatureLimitWarmest | LREAL | Lower limit of the color temperature range in Kelvin. Pre-set to 2700 K. |
fTemperatureLimitCoolest | LREAL | Upper limit of the color temperature range in Kelvin. Pre-set to 6500 K. |
fPowerOnTemperature | LREAL | Color temperature value when the supply voltage is applied to the control gear. Pre-set to 3000 K. |
fSystemFailureTemperature | LREAL | Color temperature value in the event of an error on the DALI bus. Pre-set to 3000 K. |
VAR CONSTANT
![]() | The following parameters cannot be changed and are transferred to the DALI device by the initialization routine. |
eExtendedFadeTimeBase | The Extended Fade Time is intended for very long dimming ramps of up to 16 minutes. It is disabled for this use case. eExtendedFadeTimeBase designates the time base and is pre-set to the smallest value "Base01". | |
eExtendedFadeTimeMultiplier | eExtendedFadeTimeMultiplier is the multiplier for the time base and is set to the value "Disabled". |