MC_CamScaling
This function block changes the scaling and offsets of an existing cam table coupling on a slave. InSync of the existing cam table coupling is not affected by this function block.
Definition:
FUNCTION_BLOCK MC_CamScaling
Slave : Type_Camming1D;
CamObject : Type_CouplingFunction1D;
Execute : BOOL;
Scaling : CamScalingData;
ActivationOptions : CamActivationOptions;
Done : BOOL;
Busy : BOOL;
Active : BOOL;
CommandAborted : BOOL;
Error : BOOL;
ErrorId : UDINT;
Name | Type | Description |
Slave | Reference to the slave axis | |
CamObject | Reference to the cam object | |
Execute | BOOL | Apply cam scaling at rising edge |
Scaling | New cam scaling | |
ActivationOptions | Options controlling when the new scaling takes effect (mode, position, reference object). ActivationOptions.ReferenceObject must be either not set or CamObject. |
Outputs
Done | BOOL | Cam scaling succeeded |
Busy | BOOL | Function block is not finished and new output values are to be expected. |
Active | BOOL | Function block has active control on the axis. |
CommandAborted | BOOL | Command is aborted by another command. |
Error | BOOL | Error occurred within function block. |
ErrorId | UDINT | Error identifier |
Further information
A cam plate coupling can be scaled with the function block MC_CamScaling. The raw table data of the cam plate are not affected; instead, the scaling refers to an active master/slave coupling. The following parameters can be modified: scaling factors for master and slave, and offsets for the cam plate within the coordinate system.
Optionally, the modification will only take effect from a certain master position, enabling precise scaling during the motion.
Notice | |
Property damage due to modifying an active cam plate coupling This function block can also be used for an active cam plate. Valid changes are applied to the cam plate and may result in setpoint jumps. To activate cam plate scaling at a specific time or at a specific position, the following procedure is recommended:
Possible error codes
For this function block, the following values, among others, are possible for the ErrorId output:
Error(Hex) | Error(Dec) | Error type | Description |
0x8145 | 33093 | Function Block | Mapping of cyclic interface between NC and PLC is missing (e.g., AXIS_REF, AXES_GROUP_REF, ...). A reference used by the function block (e.g., to an axis, group, mover or other motion object) is not linked to the corresponding NC object, or its cyclic mapping is incomplete. |
0x8169 | 33129 | Function Block | Master axis does not exist or cannot be used. The axis passed as master does not exist or has no cyclic mapping and therefore cannot be used as master (e.g., for camming or gearing). |
0x81af | 33199 | Function Block | Invalid object or object reference passed to function block. An invalid or missing object reference was passed to the function block (e.g., missing CamObject reference on MC_CamIn, MC_CamTableSelect or MC_CamScaling). |
0x81b0 | 33200 | Function Block | Object not allowed (e.g., object is already in use). The supplied object is not allowed in the current context (e.g., source and target are identical in CopyFrom(), the object is already used by another axis). |
0x81b1 | 33201 | Function Block | Invalid size passed to function block (e.g., invalid array size or invalid number of elements). An invalid size was passed to the function block (e.g., CamRef.NumberOfPoints less than two on MC_CamTableSelect). |
0x81b2 | 33202 | Function Block | The given cam activation settings are invalid. The activation settings of the cam table (e.g., ActivationMode and ActivationPosition) are invalid or inconsistent. |
0x81b3 | 33203 | Function Block | The given cam scaling is invalid. The supplied cam table scaling parameters are invalid (e.g., scale factor of zero, or master offset mode Auto which is not supported in the executed operation). |
0x81b4 | 33204 | Function Block | The given cam data point is invalid. At least one data point of the cam table is invalid (e.g., the first or last point is being ignored). |
0x81c2 | 33218 | State | A queued cam command could not be transitioned from queued to active. An error occurred while transitioning a queued cam command (e.g. MC_CamIn, MC_CamAdd, MC_CamExchange, MC_CamScaling or MC_CamRemove) to the active state. This typically happens when the camming state changed between queuing and activation, for example because the referenced cam table is already coupled or no longer coupled, or because the setpoint or activation time could not be computed. |
An overview of all NC error codes can be found here:
Version information
- TwinCAT Standard >= v3.1.4026.23.1
- TF5550 MC3 Camming >= v4.0.6 (includes TF5500 MC3 Base >= v4.0.6)
Required License
TC3 MC3 Camming