MC_CamIn
MC_CamIn 1:
This function block initiates camming-based synchronization on a slave.
If the slave is already coupled to one or more cam table couplings, it switches to the cam table coupling that is entered in this function block.
Note: Use MC_CamAdd to switch from single-camming to multi-camming. Switching back and forth between single-camming and multi-camming is possible without limitation.
Definition:
FUNCTION_BLOCK MC_CamIn
    Master                : Type_Master1D;
    Slave                 : Type_Camming1D;
    CamObject             : Type_CouplingFunction1D;
    Execute               : BOOL;
    Scaling               : CamScalingData;
    ActivationOptions     : CamActivationOptions;
    ReactionToMasterError : EReactionToMasterError;
    ReactionToSlaveError  : EReactionToSlaveError;
    CommandHandle         : Reference To MC_CommandHandle;
    InSync                : BOOL;
    Busy                  : BOOL;
    Active                : BOOL;
    CommandAborted        : BOOL;
    Error                 : BOOL;
    ErrorId               : UDINT;
    MasterHasError        : BOOL;
MC_CamIn 2: Inputs
Type
Default
Master
Type_Master1D
Reference to the master axis
Slave
Type_Camming1D
Reference to the slave axis
CamObject
Reference to the cam object
Execute
Start cam in at rising edge.
Scaling
CamScalingData
Scaling of the new coupling
ActivationOptions
Options controlling how the cam coupling is activated (mode, position, reference object).
TriggerSlaveError
Reaction if an error occurs in the master while this command is active.
TriggerMasterError
Reaction if an error occurs in the slave while this command is active.
CommandHandle
Optional. On a rising edge of Execute the handle is cleared and then attached to the command sent. Each call also updates the outputs of the handle. Like any input, it keeps the handle last passed, which must stay valid as long as the function block is called.
MC_CamIn 3: Outputs
Type
InSync
Synchronization succeeded
Busy
Function block is not finished and new output values are to be expected.
Active
Function block has active control on the axis.
CommandAborted
Command is aborted by another command.
Error
Error occurred within function block.
ErrorId
UDINT
Error identifier
MasterHasError
Master is in error state.
Further information
The following rules apply to ActivationOptions.ReferenceObject:
Additional information on ReactionToSlaveError and ReactionToMasterError
As a general rule, if there is an error on the slave axis:
  • Slave axis: The coupling is released, and the response depends on the error type.
  • Master Axis: The master axis reports an error and either follows the MC's stop ramp or continues its current motion without being affected.
If there is an error on the master axis:
  • Master axis: The response depends on the type of error.
  • Slave axis: The slave axis reports an error and follows either the MC's stop ramp or the master axis's setpoints.
Detailed information is provided in the Error behavior chapter.
Possible error codes
For this function block, the following values, among others, are possible for the ErrorId output:
Error(Hex)
Error(Dec)
Error type
0x8145
33093
Function Block
Mapping of cyclic interface between NC and PLC is missing (e.g., AXIS_REF, AXES_GROUP_REF, ...). A reference used by the function block (e.g., to an axis, group, mover or other motion object) is not linked to the corresponding NC object, or its cyclic mapping is incomplete.
0x8169
33129
Function Block
Master axis does not exist or cannot be used. The axis passed as master does not exist or has no cyclic mapping and therefore cannot be used as master (e.g., for camming or gearing).
0x81af
33199
Function Block
Invalid object or object reference passed to function block. An invalid or missing object reference was passed to the function block (e.g., missing CamObject reference on MC_CamIn, MC_CamTableSelect or MC_CamScaling).
0x81b0
33200
Function Block
Object not allowed (e.g., object is already in use). The supplied object is not allowed in the current context (e.g., source and target are identical in CopyFrom(), the object is already used by another axis).
0x81b1
33201
Function Block
Invalid size passed to function block (e.g., invalid array size or invalid number of elements). An invalid size was passed to the function block (e.g., CamRef.NumberOfPoints less than two on MC_CamTableSelect).
0x81b2
33202
Function Block
The given cam activation settings are invalid. The activation settings of the cam table (e.g., ActivationMode and ActivationPosition) are invalid or inconsistent.
0x81b3
33203
Function Block
The given cam scaling is invalid. The supplied cam table scaling parameters are invalid (e.g., scale factor of zero, or master offset mode Auto which is not supported in the executed operation).
0x81b4
33204
Function Block
The given cam data point is invalid. At least one data point of the cam table is invalid (e.g., the first or last point is being ignored).
0x81c2
33218
State
A queued cam command could not be transitioned from queued to active. An error occurred while transitioning a queued cam command (e.g. MC_CamIn, MC_CamAdd, MC_CamExchange, MC_CamScaling or MC_CamRemove) to the active state. This typically happens when the camming state changed between queuing and activation, for example because the referenced cam table is already coupled or no longer coupled, or because the setpoint or activation time could not be computed.
An overview of all NC error codes can be found here:
Version information
  • TwinCAT Standard >= v3.1.4026.23.1
  • TF5550 MC3 Camming >= v4.0.6 (includes TF5500 MC3 Base >= v4.0.6)
Required License
TC3 MC3 Camming