Control commands of a channel
Skip mode, NC block
Activates/deactivates skip mode at interpreter level for the NC program. The status of skip mode is only evaluated at the start of the NC program. Switchover during execution of an NC program has no effect.
Data type
MC_CONTROL_BOOL_UNIT, see description of Control unit
Available as of CNC Build V3.01.3021.1 MC_CONTROL_UNS32_UNIT
Access
PLC reads request_r + state_r and writes command_w + enable_w
ST path
gpCh[channel_idx]^.decoder_mc_control.program_block_ignore
Commanded, requested and return values
ST element
.command_w
.request_r
.state_r
Data type
BOOL or UNS32
Value range
[TRUE = skip mode NC block ON, FALSE = skip mode NC block OFF, default: FALSE]
Available as of CNC Build V3.01.3021.1 for UNS32:
0x0 - Skip mode NC block OFF
0x1 – Skip level 1
0x2 - Skip level 2
0x4 - Skip level 3
0x8 - Skip level 4
0x10 – Skip level 5
0x20 - Skip level 6
0x40 - Skip level 7
0x80 - Skip level 8
0x100 – Skip level 9
0x200 - Skip level 10
Skip levels active simultaneously are enabled by bitwise ORing.
Example:
Enable all skip levels by setting 0x3FF.
Redirection
ST element
.enable_w
Single-block mode at interpreter level NC block
Activates/deactivates single-block mode at interpreter level. A restart must be present for each block
Data type
Special features
Not supported.
Access
ST path
gpCh[channel_idx]^.decoder_mc_control.single_block
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = single-block mode ON, FALSE]
Redirection
ST element
.enable_w
Enable processing of next NC block
Enable to process the next NC block. This element serves to synchronise the geometry chain with the PLC. For this purpose, the PLC blocks the single-block step enable and thus stops the interpreter.
Data type
Special features
Not supported.
Access
ST path
gpCh[channel_idx]^.decoder_mc_control.continue_machining
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
Continue NC program decoding
Continues decoding an NC program after an error has occurred if syntax check (simulation mode) and interactive step enabling of decoding is activated (decoder parameter, characteristic parameter:= 1).
Data type
Special features
Not supported.
Access
ST path
gpCh[channel_idx]^.decoder_mc_control.release_stop
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
Stop NC program decoding
Stops the decoding of an NC program if interactive enabling of further processing of the NC program was enabled in Syntax Check Simulation mode.
Data type
Special features
Not supported.
Access
ST path
gpCh[channel_idx]^.decoder_mc_control.dec_stop
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
Channel operation mode
Selects a special channel operation mode, e.g. syntax check or machining time calculation
Data type
MC_CONTROL_SGN32_UNIT, see description of Control Unit
Access
ST path
gpCh[channel_idx]^.decoder_mc_control.execution_mode
ST element
.command_w
.request_r
.state_r
Data type
DINT
Value range
Value
Constant
Meaning
0x0000
ISG_STANDARD
Normal mode
0x0001
SV
Block search
0x0002
SOLLKON
Nominal contour visualisation simulation with output of visualisation data
0x0802
SOLLKON_SUPRESS_OUTPUT & SOLLKON
Nominal contour visualisation simulation without output of visualisation data
0x0004
ON_LINE
Online visualisation simulation
0x0008
SYNCHK
Syntax check simulation
0x0010
PROD_TIME
Simulation machining time calculation
(in TwinCAT without function)
0x0020
ONLINE_PROD_TIME
Simulation of online machining time calculation
0x0040
MACHINE_LOCK
Dry run without axis motion
0x0080
ADD_MDI_BLOCK
Extended manual block mode: the end of a manual block is not evaluated as a program end. It permits the commanding of further manual blocks.
0x0100
KIN_TRAFO_OFF
Overwrites automatic enable for kinematic transformations by a characteristic parameter defined in the channel parameters (sda_mds*.lis).
0x1000
BEARB_MODE_SCENE
When SCENE mode is enabled, the output of #SCENE commands is activated on the interface (see also [FCT-C17// Scene contour visualisation]).
An additional client is linked to this output via DataFactory / CORBA.
0x2000
SUPPRESS_TECHNO_OUTPUT
Without output of technology functions (M/H/T). Set implicitly in connection with syntax check.
0x10000
SUPPRESS_POSITION_REQUEST
Fast program start without position request at program start
0x20000
SUPPRESS_PROG_START_INIT
Suppress program start sequence for machining on the belt
Redirection
ST element
.enable_w
Index of clamp position offset group
A clamp position offset defines an additional offset. For instance, this takes into consideration different clamping positions of a workpiece in a machine workspace.
Clamp position offsets are defined in the clamp position offset data. The clamp position offsets for each axis are specified in a clamp position offset group. A clamp position offset group is selected by the group index. Clamp position offset data is evaluated by the CNC at program start.
Data type
MC_CONTROL_SGN16_UNIT, see description of Control unit
Access
ST path
gpCh[channel_idx]^.decoder_mc_control.clamp_position
ST element
.command_w
.request_r
.state_r
Data type
INT
Value range
[0, 67]
Redirection
ST element
.enable_w
Feedhold ON/OFF type 1
Channel-specific feedhold.
Setting this element to TRUE means immediate ramp-down of the feed rate during interpolation in accordance with the parameterised accelerations to feed rate = 0.
Data type
Special features
The channel-specific parameter P-CHAN-00097 can be used to exert additional influence on the parameterised accelerations to be used.
Feedhold ON/OFF can also be commanded by the control unit for switching operation modes (see sec. 8.2). A HOLD command results in stopping the channel; a RESUME command cancels the stop command.
If the PLC is registered at both control units, pay attention to the following safety note:
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.feedhold
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = feedhold ON, FALSE]
Redirection
ST element
.enable_w
CAUTION
Stop command to CNC is not executed.
Possible damage to machine.
Similar to other control units, a command from an external application, e.g. an HMI, is indicated in request_r. If the PLC operates this control unit and therefore sets enable_w to TRUE, the command from the external application only becomes effective when request_r is written to command_w. Here the semaphores must be operated as usual.
This must also be considered if the PLC operates the control unit in order to switch operation modes (see section 8.2) and therefore sets the enable_w to TRUE A HOLD command sent by this control unit triggers the NC kernel to send a request to activate feedhold. This is again indicated in request_r of the control unit described here and only becomes effective when the PLC copies request_r to command_w. This also applies to cancelling feedhold.
The figures below depict these functions.
Control commands of a channel 1:
Interaction between feedhold and NC channel stop
Control commands of a channel 2:
Time sequence of feedhold and NC channel stop
Feedhold ON/OFF type 2
When this element is set to TRUE, the feed rate is immediately ramped down to feed rate = 0 during interpolation.
Data type
Special features
Irrespective of the channel-specific parameter P-CHAN-00097, the effective deceleration is defined by the values of the parameterised feedhold acceleration which is specified by the axis parameters P-AXIS-00024, P-AXIS-00053 (a_feedh) and P-AXIS-00081 (tr_feedh).
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.e_feedhold
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = emergency stop, feedhold ON, FALSE]
Redirection
ST element
.enable_w
Emergency stop, channel
If this emergency stop element is set active (TRUE), interpolation is aborted immediately by output of the zero command value or by a deceleration as specified in the emergency deceleration. The NC kernel reverts to error state.
This type of motion influence has maximum priority.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.emergency_stop
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = emergency stop active, FALSE]
Redirection
ST element
.enable_w
Single-block mode
Activate/deactivate single-block mode.
Single-block mode refers only to motion blocks. As long as single-block mode is activated, the system is decelerated to feed rate = 0 at the end of each motion block. The following blocks can then only be executed by setting the element “continue motion” if all axes are located in the control window.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.single_block
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
Optional stop
Activating/deactivating optional stop.
If the function M01 (optional stop) is programmed in the current block of the NC program, set this element to the value TRUE to stop at block end (ramped deceleration complying with the permissible accelerations).
The following block can be enabled by activating the element “continue machining” if the NC kernel indicates that all axes are located within the control window by resetting the status wait_axes_in_position_r.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.m01_stop_enable
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = optional stop active, FALSE]
Redirection
ST element
.enable_w
Resume motion
If program execution is interrupted by selecting "Single block mode" or "Optional stop" or by M00, this control unit can resume NC program execution.
A falling edge for the command value (command_w) of the control unit "Continue motion", i.e. a transition from TRUE to FALSE, leads to a resumption of NC program execution. The condition for this is that all axes are located in the control window.
Data type
Special features
Falling edge of the command resumes NC program execution.
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.continue_motion
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
Machining simulation ON/OFF
Activating/deactivating machining simulation.
During machining simulation, all technology functions of the NC program are not output to the PLC but are acknowledged internally.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.machining_simulation
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = machining simulation active, FALSE = machining simulation inactive]
Redirection
ST element
.enable_w
Feed override
Feed override allows the programmed path velocity to be weighted with an additional factor.
Data type
MC_CONTROL_UNS16_UNIT, see description of Control unit
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.override_feedrate
ST element
.command_w
.request_r
.state_r
Data type
UINT
Unit
0.1%
Value range
[0, P-CHAN-00056]
The parameter P-CHAN-00056 is a channel-specific parameter. Its value is typically 1000.
Redirection
ST element
.enable_w
Rapid traverse override
The rapid traverse override can weight G0 path motions by an additional factor.
See also special features.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.override_rapid_move
ST element
.command_w
.request_r
.state_r
Data type
UINT
Unit
0.1%
Value range
[0, 1000]
Redirection
ST element
.enable_w
Special features
Parameterisation / mode of operation
Rapid traverse override is only active if this function is also activated in the channel parameter list. Otherwise, there is no distinction made between feed and rapid traverse blocks.
Setting options in the channel parameter P-CHAN-00181:
Rapid traverse override is inactive. Rapid traverse override acts on feed and rapid traverse blocks.
Rapid traverse override is active. Feed override acts on feed blocks; the minimum of feed and rapid traverse override acts on rapid traverse blocks.
Rapid traverse override is active. Feed override acts on feed blocks; only rapid traverse override acts on rapid traverse blocks.
Interrupt output of command values to real axes
This interrupts the output of NC channel command values to physical axes. The NC channel is stopped and assignment to the real axes is disabled.
Physical axes can then be requested and moved by another channel. A different logical axis can be linked to a physical axis here.
After clearing this interruption, the axes can be requested again and the original channel continues its motion.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.suspend_axis_output
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
External path velocity specified
External path velocity specified. The path velocity setting is activated by the control unit ext_command_speed_valid.
If the velocity specified in negative, the tool moves backwards along the path.(See FCT-C7// Forward/backward motion on the path)
Data type
MC_CONTROL_UNS32_UNIT, see description of Control unit
Special features
The path velocity transferred by this interface is automatically restricted to the limits defined in the axis parameters.
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.ext_command_speed
Commanded, requested value
ST element
.command_w
.request_r
Data type
UDINT
Unit
1 μm/s
Return value
ST element
.state_r
Data type
UDINT
Unit
1 μm/s
Special features
The state_r element indicates the path velocity actually used in the interpolator, including any influence by override.
By default the externally specified velocity only affects machin8ing motions (G01, G02, G03). The channel parameter P-CHAN-00102 (plc_command_rapid_feed) can set whether the externally specified velocity also acts on rapid traverse motions (G00).
Redirection
ST element
.enable_w
Activation of external path velocity
Activate the velocity commanded in the ext_command_speed control unit. To reach the commanded velocity, all axes involved in the motion are accelerated or decelerated.
If this value is TRUE, the sign is considered in the current path feed (active_feed_r) control unit.
Data type
MC_CONTROL_BOOL_UNIT, see description Control unit
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.ext_command_speed_valid
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
Input disable, interpolator
When the control unit is activated, the interpolator stops after it has processed the input command blocks since this control unit can disable the input of further command blocks.
The channel parameter P-CHAN-00267 can define the event at which an activated input disable becomes effective, e.g. effective as of the next rapid traverse block.
Data type
Special features
See safety not below.
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.input_disable
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
CAUTION
This must also be considered if the PLC operates the control unit in order to switch operation modes (see section 8.2) and therefore sets the enable_w to TRUE A HOLD command given by this control unit triggers the NC kernel to request input disable. This is again indicated in request_r of the control unit described here and only becomes effective when the PLC copies request_r to command_w. The same also applies to cancelling input disable.
Control commands of a channel 3:
Interaction of input disable and NC channel stop
Control commands of a channel 4:
Time sequence of input disable and NC channel stop
Reduced velocity, channel
When this signal is set, the path velocity is reduced to the values defined in the axis parameters P-AXIS-00214 and P-AXIS-00155.
Data type
Special features
The limits of the axes participating in the motion are taken into consideration. The effective value for reduced velocity is determined so that none of the axes participating in the motion overshoots its configured limit.
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.reduced_speed
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = reduced velocity active, FALSE = reduced velocity not active]
Redirection
ST element
.enable_w
Reduced velocity in zone 1, channel
When this signal is set, the path velocity is limited to the velocity defined in the axis parameter P-AXIS-00030 if the axis is located within the area defined by the parameters P-AXIS-00085 and P-AXIS-00093. If necessary the axis is decelerated after entering the zone.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.reduced_speed_zone
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = reduced velocity in zone 1 active, FALSE = reduced velocity in zone 1 not active]
Redirection
ST element
.enable_w
Reduced velocity in zone 2, channel
When this signal is set, the path velocity is limited to the velocity defined in the axis parameter P-AXIS-00030 if the axis is located within the area defined by the parameters P-AXIS-00097 and P-AXIS-00105. If necessary the axis is decelerated after entering the zone.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.reduced_speed_2_zone
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = reduced velocity in zone 2 active, FALSE = reduced velocity in zone 2 not active]
Redirection
ST element
.enable_w
Path acceleration reduction
This control unit is used to reduce path acceleration while the program is running.
The change in acceleration is time-delayed and is therefore only suitable for slow changes. The state of the control unit returns the commanded value as soon as the value is accepted the first time. If a value outside the value range is commanded, the value is not accepted and the state 0 is displayed.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.reduction_acceleration
ST element
.command_w
.request_r
.state_r
Data type
UDINT
Unit
[0.1%]
Value range
[0, 999]
Redirection
ST element
.enable_w
Activate reduced manual mode acceleration
This control unit activates the parameterised reduced maximum axis acceleration (P-AXIS-00545) in manual mode without any parallel interpolation.
Data type
Access
PLC reads requested + feedback values and writes commanded value + redirection.
ST path
gpCh[channel_idx]^.bahn_mc_control.reduced_acceleration
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
Time override valid
Time override is activated
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.command_t_ovrd_valid
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = time override is activated, time override is not activated]
Redirection
ST element
.enable_w
Time override
Time override can influence the internal CNC time base for motions. Its effect is similar to slow motion.
Time override acts in different ways on path velocity and acceleration.
Example:
At 50% time override (command_w = 500), velocity is reduced by a factor of 2 and acceleration by a factor of 4.
Data type
Special features
The channel parameter P-CHAN-00111 can be used to influence the effect of time override on the dwell time function.
Access
ST path
ST element
.command_w
.request_r
.state_r
Data type
UINT
Unit
0.1%
Value range
[100, 1000]
Redirection
ST element
.enable_w
Notice
Time override affects real-time and safety functions.
Delays in the use of these functions may lead to longer reaction times for safety functions under certain circumstances.
Time override affects path feed and acceleration independent of real-time functions such as feedhold or safety functions such as reduced speed. The user must consider this when using this function.
Suppress the capture of tool life data
Capture of tool life data is suppressed when this control unit is activated.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.tool_life_suppress_capture
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = tool life data is not captured,
FALSE = tool life data is captured]
Redirection
ST element
.enable_w
Delete distance to go, command
The rising edge of the commanded value has the effect that the CNC channel is decelerated to feed velocity 0. Then a linear motion is executed to the target position of the next motion block (short cut).
The command only affects motion blocks.
The functional description [FCT-C28] deals with the topic of “Delete distance to go” in detail.
Data type
Special features
See state data delete_distance_to_go_active_r.
P-STUP-00033 must be configured for the channel.
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.delete_distance_to_go
ST element
.command_w
.request_r
.state_r (TRUE indicates that the command was detected by the CNC)
Data type
Value range
[TRUE = distance to go to be deleted,
FALSE = no impacts on motion blocks]
Redirection
ST element
.enable_w
Delete distance to go, end marker
This control unit sets the end marker defined in the NC program online to valid. A bit mask is defined for this in the NC program.
If at least one single bit in the end marker is set on the NC interface, this marker is valid as a jump target.
Example:
N10 #DEL DIST2GO [END = '16#0014']
The end marker can be set to valid by bit3 (hexadecimal 4) or by bit5 (hexadecimal 0x10).
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.delete_distance_to_go_activation
ST element
.command_w
.request_r
.state_r
Data type
UDINT
Value range
32-bit
Redirection
ST element
.enable_w
Online tool compensation (OTC)
The tool radius is compensated by specifying a wear value. The wear value is specified as an offset from the planned cutting edge.
It is only possible to used the control unit in the RADIUS or TOOL_DIR modes and in the DISC or AUTO mode.
See NC command #OTC.
See also functional description [FCT-C20].
Data type
MC_CONTROL_SGN32_UNIT, see description of Control unit
Special features
If the wear value changes, this change is distributed over several interpolation cycles to avoid sudden changes.
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.otc_radius_offset
ST element
.command_w
.request_r
.state_r
Data type
DINT
Unit
0.1 µm
Value range
[-P-TOOL-00031, P-TOOL-00031]
Redirection
ST element
.enable_w
Reversible stop
Select/deselect reversible stop.
If the function #STOP REVERSIBLE [LEVEL=<bitmask>] is programmed in the current block of the NC program, the program stops at block end (ramped deceleration complying with permitted acceleration values) if the same value assigned to the option LEVEL was already sent by this control unit to the Motion Controller and the stop command was activated.
The next block is enabled by a control unit command "Continue motion" (continue_motion) if the NC kernel displays that all axes are located in the control window by resetting the status display "Wait for axis group in position" (wait_axes_in_position_r).
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.stop_reversible_level
ST element
.command_w
.request_r
.state_r
Data type
UDINT
Value range
[0, MAX_UNS32]
Redirection
ST element
.enable_w
Backward motion
Select/deselect backward motion on the path In basic setting, M/H functions are executed without synchronisation (MOS) in this mode.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.backward_motion
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
Simulated motion
Select/deselect simulated forward motion on the path
Sections in the NC program can be skipped during program runtime in combination with the NC command #OPTIONAL EXECUTION.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.simulate_motion
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
Reset backward motion memory
Deselects backward motion memory No further NC block is saved in the memory. The memory is deleted.
The backward motion memory can only be cleared if no NC program is active.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.backward_storage_off
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
Suppress error output from working space monitoring in manual mode
This control unit suppresses the output of error messages from the working space monitoring system [FCT-C14] in manual mode.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.suppress_area_mon_manual_mode
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE = suppress error output; FALSE]
Redirection
ST element
.enable_w
Simulate motion mask
This control unit specifies a mask. Sections in the NC program can be skipped during program runtime in combination with the “simulate motion” control unit and the NC command #OPTIONAL EXECUTION.
When the “simulate motion” control unit is on a positive edge, all sections flagged by
#OPTIONAL EXECUTION [SIMULATE MASK=<mask>]
containing a bit of the mask are skipped.
Data type
MC_CONTROL_UNS64_UNIT, see description of Control unit
Access
PLC reads request_r + state_r and writes command_w + enable_w.
ST path
gpCh[channel_idx]^.bahn_mc_control.simulate_motion_mask
ST element
.command_w
.request_r
.state_r
Data type
ULINT
Value range
0 – MAX(UNS64)
Redirection
ST element
.enable_w
Special feature
Available as of CNC Build V3.1.3107.12
Switch on velocity limit
By setting this command, the maximum path velocity is limited according to the kinematic and velocity settings.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.tcp_velocity_limit
ST element
.command_w
.request_r
.state_r
Data type
Unit
Value range
[TRUE = limits active, FALSE = limits not active]
Redirection
ST element
.enable_w
Special feature
Available as of CNC Build V3.1.3079.26
Save current system data for later electrode retraction
When a die-sinking system is used, it is difficult for the user to extract an electrode out of the workpiece manually without damaging it after a power failure.
This control unit offers the option of signalling the CNC to save the current system data for later reuse with automatic retraction. This control unit should therefore be activated as soon as a power failure is detected and the CNC is shut down.
The data is saved on a positive edge and the control unit must be placed on hold until the status has been updated.
Data type
Access
ST path
gpCh[channel_idx]^.bahn_mc_control.save_retract_data
ST element
.command_w
.request_r
.state_r
Data type
Value range
[TRUE, FALSE]
Redirection
ST element
.enable_w
Special feature
Control unit is available as of CNC Build V4.23.0