Status information of a channel
Covered block motion path
Part of the path motion traversed in the current block in relation to the total path.
This status datum contains the current block position referred to the path distance in space in the motion block in per mil sd(t).
Status information of a channel 1:
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.covered_distance_r
Data type
DINT
Unit
0.1 %
Access
PLC is reading
Special features
If a main axis participates in the motion, the covered path motion is in relation to the block path of the first three axes. If no main axis participates in the motion, the covered path motion is the position lag with the longest motion time in relation to the block path.
Currently covered path in the NC program (PCS)
Reads the current distance covered in the NC program since program start or since the last # DISTANCE PROG START CLEAR NC command. The calculation is based on the current position in the current NC block.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.dist_prog_start
Data type
UDINT (* LREAL)
Unit
0.1 µm
Access
PLC is reading
Special features
* As of CNC Build V3.1.3104.01 the data element is provided in LREAL forma.
Line counter, NC program
The datum indicates the NC program line which is the source of the command just processed by the interpolator.
The value is derived from the number of NC program lines which the decoder has read since the NC program started. All the lines read the decoder are counted, i.e. repeatedly read lines, empty and comment lines. All commands to the interpolator resulting from decoding a NC program line are assigned to the associated line counter.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.block_count_r
Data type
UDINT
Access
PLC is reading
Programmed path feed
Path feed that was was programmed by the F word in the NC program..
e.g. using F10000
Status information of a channel 2:
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.command_feed_r
Data type
DINT
Unit
1 µm/s
Access
PLC is reading
Path deed programmed taking into account real-time influences
Path feed was programmed in the NC program<value> Weighted by the current real-time influences such as override.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.command_feed_active_r
Data type
DINT
Unit
1 µm/s
Access
PLC reads
Current path feed
Current path feed during interpolation.
This value is displayed with sign when the external path speed (extern_command_speed_valid control unit) is active
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.active_feed_r
Data type
DINT
Unit
1 µm/s
Access
PLC is reading
Due to the architecture of the NC kernel in which various components operate asynchronously to each other, certain status information may be provided several times by the various control components.
For example, the program_end_r signal in the decoder status flag means that the decoder has completed program decoding whereas the actual interpolation by the path interpolator may not have finished. The end of interpolation of the path axes is indicated by the program_end_r signal in the status data of the path interpolator.
End of program reached
This status information indicates that the interpolator has reached program end or that no NC program is currently under in execution.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.program_end_r
Data type
Value range
[TRUE = End of program reached, FALSE]
Access
PLC is reading
Decoder has reached program end.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.decoder_state.program_end_r
Data type
Value range
Access
PLC is reading
Special features
Caution: The machine cannot move any further since the interpolation signal is relevant for machine motion.
Look Ahead function has reached program end
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bavo_state.program_end_r
Data type
Value range
Access
PLC is reading
Special features
Required for diagnosis only.
Stop condition
Displays the condition why the current motion was stopped.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.stop_conditions_r
Data type
DINT
Value range
See Value range of stop conditions with explanations.
Access
PLC is reading
Constant in PLC
Value
Explanation
HLI_SC_FEEDHOLD
0x0001
Path feed stop
HLI_SC_VFG
0x0002
No axis-specific feed enable.
HLI_SC_SINGLE_BLOCK
0x0004
Single step mode active.
HLI_SC_M00_OR_M01
0x0010
M00 (programmed stop), M01 (optional stop) is active.
HLI_SC_PLC_ACKNOWLEDGE
0x0020
Stop occurs due to waiting for an acknowledgement from the SPS. This may occur as a result of the output of M or H technology functions but is not restricted to them alone.
HLI_SC_OVERRIDE_ZERO
0x0040
Override = 0.
HLI_SC_OVERRIDE_RAPID_ZERO
0x0080
Override = 0 with rapid traverse blocks
HLI_SC_DELAY_TIME
0x0200
Dwell time.
HLI_SC_CHANNEL_SYNC
0x0800
Channel synchronisation is active.
HLI_SC_IPO_INPUT_EMPTY
0x1000
Input FIFO of the interpolation is empty.
HLI_SC_IPO_INPUT_DISABLED
0x2000
Input of function blocks (e.g. motion blocks etc.) disabled.
HLI_SC_WAIT_FOR_AXES
0x8000
Stop occurs due to waiting until a commanded axis swap is completed.
HLI_SC_CHANNEL_ERROR
0x00010000
An error occurred in the channel.
HLI_SC_WAIT_TECHNO_ACK
0x00020000
Waiting for acknowledgement of M/H/ST technology functions.
HLI_SC_W_C_AFTER_COLLISION
0x00040000
After a detected collision, waiting for motion resumption.
HLI_SC_SLOPE_SUPPLY_PROBLEM
0x00080000
Block supply problem (only occurs in conjunction with HSC slope).
HLI_SC_BACK_INTERPOLATION
0x00100000
Back interpolation after tracking mode is active.
HLI_SC_STOP_REVERSIBLE
0x00200000
Stop since M00 (programmed stop) is active. However, the NC program can be processed backwards despite M00 (available as of V3.1.3039.01).
HLI_SC_BREAKPOINT_STOP
0x00400000
Stop after a breakpoint (stop point) is reached; available as of V3.1.3039.01.
HLI_SC_M0_STOP
0x02000000
Stop after an M00 function is reached
HLI_SC_M1_STOP
0x04000000
Stop after an M01 function is reached
HLI_SC_INSERT_STOP_AT_DIST
0x08000000
Stop after an M function inserted by the Control Unit “Inserting stop marks” is reached.
HLI_SC_DEC_SYN_CHAN_EMPTY
0x10000000
Decoder is waiting for synchronisation. NC channel has no job.
HLI_SC_WAIT_FOR_ADD_IFC
0x20000000
Stop because waiting condition is active in the additive interface (3D distance control).
HLI_SC_WAIT_FOR_AXIS_DIST_CTRL
0x40000000
Stop because waiting condition is active in the distance control (2D).
Error occurred – awaiting clearance
An internal error has occurred. The interpolator waits for the error to be cleared.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.wait_error_removal_r
Data type
Value range
[TRUE = Error occurred - interpolator waiting, FALSE]
Access
PLC reads
Error occurred waiting for external input
In syntax check mode, the decoder waits after an error for an external input (continue, abort)
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.decoder_state.wait_after_error_r
Data type
Value range
[TRUE = Error occurred – decoder waiting, FALSE]
Access
PLC reads
Interpolator active
Machine is to be/is moved.
If a subroutine with path motions is in process, this status is set.
Example:
N10 G01 F1000 X0 Y0
N20 G01 F1000 Y10 Y20 (block is interpolated)
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.interpolation_active_r
Data type
Value range
[TRUE = Machine is to be/is moved, FALSE]
Access
PLC is reading
Technology function acknowledgement
The interpolator waits for the acknowledgement of a technology function from the PLC.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.wait_techno_acknowledge_r
Data type
Value range
[TRUE = Waiting for acknowledgement of technology function, FALSE]
Access
PLC reads
Enable continuation of motion
The interpolator waits for an Enable to continue the motion after a stop in single-step mode.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.wait_continue_r
Data type
Value range
[TRUE = Interpolator waiting motion to continue, FALSE]
Access
PLC reads
Dwell time active
The interpolator waits due to a programmed dwell time (G04).
If a subroutine with a dwell time is in process, this status is set.
Example:
N10 G01 X10 F1000
N20 #TIME 10 ( Dwell time 10 seconds)
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.dwell_time_active_r
Data type
Value range
[TRUE = Interpolator waiting, FALSE]
Access
PLC is reading
Violation detected in workspace monitoring
This datum reads a violation detected by the workspace monitoring system [FCT-C14].
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.area_mon_violation_detected_r
Data type
Value range
[TRUE = error detected in workspace monitoring, FALSE]
Access
PLC is reading
Axis group in position
All axes in the axis group have reached their programmed end positions.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.axes_in_position_r
Data type
Value range
[TRUE, FALSE]
Access
PLC reads
Waiting for axis group in position
The interpolator waits for all axes to be in position in single-block mode, a programmed stop (M00), an optional stop (M01) or a exact stop set (G60/G360).
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.wait_axes_in_position_r
Data type
Value range
[TRUE, FALSE]
Access
PLC is reading
Waiting for requested axis
The look ahead function waits for a programmed axis request (see [PROG//#CALL AX]) top contain the axis.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bavo_state.wait_for_axis_r
Data type
Value range
[TRUE = Waiting for requested axis, FALSE]
Access
PLC reads
Block search active
The interpolator works in block search mode. No axis motion occurs. As long the block search process in the interpolator remains in the HLI_BS_ACTIVE or HLI_BS_WAIT_FOR_PLC_OFF state, this value indicates TRUE.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.block_search_active_r
Data type
Value range
[TRUE = active - Interpolator works in block search mode., FALSE]
Access
PLC is reading
Block search active
Look ahead works in block search mode
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bavo_state.block_search_active_r
Data type
Value range
[TRUE = active – Look ahead works in block search mode, FALSE]
Access
PLC reads
Block search active
The decoder works in block search mode
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.decoder_state.block_search_active_r
Data type
Value range
[TRUE = active - Decoder works in block search mode, FALSE]
Access
PLC reads
Block search, distance from continuation position
If a NC program is started in block search modus, the NC program is processed in simulative mode (without axis motion) until the continuation position is reached. Block search is then in the HLI_BS_WAIT_FOR_PLC_OFF state and calculates the distance between the actual positions of the axis and the continuation position. If block search is in the HLI_BS_RETURNING_TO_CONTOUR state, this value is refreshed cyclically.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.block_search_path_deviation_r
Data type
UDINT
Unit
0.1 µm
Value range
[0, MAX_SGN32]
Access
PLC is reading
Block search, state
Indicates the current state of the block search mode in the interpolator.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.block_search_state_r
Data type
INT
Value range
Constant
Value
HLI_BS_INACTIVE
0
HLI_BS_WAIT_FOR_PLC_ON
1
HLI_BS_ACTIVE
2
3
HLI_BS_WAIT_RETURN_TO_CONTOUR
4
5
HLI_BS_WAIT_FOR_CONTINUE_CONTOUR
6
Access
PLC is reading
Rapid traverse velocity, axes move in the channel
If the value is TRUE, the path axes move on the programmed path when rapid traverse velocity was specified as path velocity.
TRUE is only indicated if at least one axis actually moves.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.rapid_mode_r
Data type
Value range
[TRUE = at least one path axis moves and rapid traverse velocity is specified, FALSE]
Access
PLC reads
Collision detected, wait to continue motion
Indicates that after a collision is detected, the axis waits for a command to continue the motion.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.wait_continue_after_collision_r
Data type
Value range
[TRUE = after a collision is detected, wait to continue the path, FALSE]
Access
PLC reads
Block number, current path motion
If the N function [PROG//N function] is used in the active NC program to program NC block numbers, this datum indicates the NC block number of the NC block currently processed in the interpolator in this datum.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.block_nr_r
Data type
UDINT
Value range
[0, MAX_UNS32]
Access
PLC is reading
NC program, file name
Name of the file containing the active NC program.
If the active NC program is a global subroutine, the filename containing the global subroutine is indicated.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.file_name_r.zeichen
Data type
STRING(HLI_NAME_SIZE)
Access
PLC reads
NC program, file offset
This indicates the current command processed in the interpolator and the offset at which the related NC program line starts in the NC program file.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.active_fileoffset_r
Data type
DINT
Unit
Byte
Value range
[0, MAX_SGN32]
Access
PLC reads
NC block, inserted
Indicates whether an additional NC block was inserted by the control unit during interpolation. Additional NC blocks may be created by functions such as polynomial contouring or tool radius compensation.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.block_inserted_r
Data type
Value range
[TRUE = the control unit inserted an NC block, FALSE]
Access
PLC reads
Manual mode is active, without parallel interpolation
Indicates whether exclusive manual mode is active. No interpolation is active at the same time.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.g200_active_r
Data type
Value range
[TRUE = Manual mode is active without parallel interpolation, FALSE]
Access
PLC reads
Manual mode active, with parallel interpolation
Indicates whether superimposed manual mode is active.
This means that the setpoints for the axes to be moved are calculated by superimposing the defaults for path interpolation and the mode interface of a particular axis.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.g201_active_r
Data type
Value range
[TRUE = Manual mode is active with parallel interpolation, FALSE]
Access
PLC reads
Measurement process, active
Indicates that a measurement process was commanded by G100 or G108.
The rising edge of the datum indicates that the measurement process was started. The value then remains TRUE until a measurement event was triggered for all the axes participating in the measurement run and for which measurement was activated.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.measure_active_r
Data type
Value range
[TRUE = A measurement process is commanded but the measurement results have not yet been received for all measuring axes,
FALSE= measurement process not active]
Access
PLC is reading
Look ahead distance
Indicates the look ahead distance up to which the motion was calculated by the interpolator. The distance is referred to program starts or to the position where the last NC command #DISTANCE PROG START CLEAR was executed.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.dist_contour_lah_high
gpCh[channel_idx]^.bahn_state. dist_contour_lah _low
Data type
UDINT
Unit
0,1 µm
Access
PLC reads
Special features
In the NC this is an integer number which occupies 8 bytes in the memory. At the HLI the number is provided in the form of two 4-byte wide values. The value in dist_prog_start_low represents the 4 lower bytes 0 to 3 and the value in dist_prog_start_high the 4 higher bytes 4 to 7 of the 8-byte value present in the NC kernel.
Available as of Build V3.1.3030.0 and higher
Delete distance to go, state
If a command is sent via the delete_distance_to_go control unit, this value is TRUE as long as the NC block which exerts a linear motion to the target position of the next motion block is executed (short cut). It also remains TRUE if the active short cut is itself shortened by a new command.
The signal is again reset when the active NC block is no longer related to the command of the delete_distance_to_go control unit.
See functional description [FCT-C28].
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.delete_distance_to_go_active_r
Data type
Value range
[TRUE = linear motion is executed to the target position of the next motion block (short cut), FALSE]
Access
PLC is reading
High-resolution velocity setpoint, state
The value indicates whether the interface for the external input of velocities continues to process the inputs at high resolution. Processing the input at high resolution is enabled by the NC command #EDM ON and disabled by programming #EDM OFF. This is used in combination with electrical discharge machining.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.edm_active_r
Data type
Value range
[TRUE = high-resolution processing of input value is active, FALSE = input values are not processed at high resolution]
Access
PLC reads
Time to next motion command containing G01, G02
Is rapid traverse velocity is specified for the current path motion, this datum indicates the time until the next motion block containing G01 or G02 is active.
This time is only calculated and displayed if it is enabled in the channel parameter P-CHAN-00650 of the channel or, alternatively, in the start-up parameter P-STUP-00070 by specifying
FCT_LOOK_AHEAD_STANDARD | FCT_CALC_TIME.
(See Interpolation function table.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.time_to_next_feed_block_r
Data type
UDINT
Value range
[0, MAX_UNS32]
Access
PLC is reading
Stop, value
When a reversible stop is programmed, an additional user-specific parameter can be specified:
     #STOP REVERSIBLE[USR_VAL = ....]
That value is indicated in this element as soon as a stop is executed at this position. After resuming the motion, the value is deleted.
In this context also see the "Reversible stop” control unit (stop_reversible_level) and the functional description [FCT-C7// Automatic reversing after stop].
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.stop_reversible_usr_val_r
Data type
UDINT
Value range
[0, MAX_UNS32]
Access
PLC reads
Example
Reversible stop
Required channel parameter:
forward_backward.disable_stop_backward      0
forward_backward.disable_stop_2nd_forward   0
forward_backward.disable_stop_1st_forward   0
NC program:
%stop_reversible
N01 X0 Y0 Z0
N10 X100
N20 Y100
N30 X0
N40 Y0
N45 #STOP REVERSIBLE[ USR_VAL=500]
N50 X0 Y0 Z0
N60 X100
N70 Y100
N80 X0
N90 Y0
N95 #STOP REVERSIBLE[ USR_VAL=2000]
M30
Status information of a channel 3:
Stop interaction on backward/forward motion
Distance to edge below limit
This signals that the distance to the edge defined by the channel parameter P-CHAN-00222 (edge_machining.pre_dist), was undershot. As from this time, motion on the programmed path is effective at the path feed defined by the channel parameter P-CHAN-00223 (edge_machining.pre_feed).
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.edge_function_r.signal_1
Data type
Value range
[TRUE = active – Distance to edge undershoots parametrised limit, FALSE]
Access
PLC reads
Wait time at edge
The signal indicates that the motion was stopped at the edge and the wait time specified by the channel parameter P-CHAN-00224 (edge_maching.wait_time) is expiring.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.edge_function_r.signal_2
Data type
Value range
[TRUE = active – wait time active, FALSE]
Access
PLC reads
Distance after edge below limit
The signal indicates that the tool is moving away from the edge but the distance from the edge is still smaller than the value defined by the channel parameter P-CHAN-00225 (edge_machining.post_dist). The path feed valid for this section is defined by the channel parameter P-CHAN-00226 (edge_machining.post_feed).
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.edge_function_r.signal_3
Data type
Value range
[TRUE = active - distance after edge not reached, FALSE]
Access
PLC reads
Angle between active and next NC block
Indicates the angle between 2 consecutive NC blocks if both NC blocks are motion blocks containing programmed feed. The indicated value is in the range of [0, 1800000] which corresponds to [0°, 180°].
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.edge_function_r.angle_end
Data type
DINT
Unit
10-4 °
Value range
[0,10000000]
Access
PLC reads
Special features
If the the next motion block is a
rapid traverse block, value 5000000 is output
NC block that leads to motion stop, value 6000000
is output.
In all other cases the default value 10000000 is indicated.
Velocity at end of current NC block
Indicates the velocity at transition from currently interpolated to next motion block which results from evaluating the geometrical situation and the velocity of the next block.
If the dwell time is programmed or a predictable motion stop is programmed at the transition between the NC blocks caused by the output of a technology function with corresponding synchronisation start in the next block, the value 0 is indicated.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.block_dynamic_r.vel_end_geo
Data type
DINT
Unit
1 μm/s
Value range
[0, MAX_SGN32]
Access
PLC reads
Numerator of the real-time loop
The datum shows the number of passes of the real-time loop in which the current machining is located.
If a loop transition is in a forward direction, the datum is incremented by 1 and it is decremented in a backward direction.
If more loop passes were processed in the backward direction, a negative numeral is displayed.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.rt_loop_count_r
Data type
DINT
Access
PLC reads
Special feature
Date available as of CNC Build V3.1.3105.01 and higher
Real-time loop active
The datum indicates whether current machining is located in a #RT WHILE - #RT ENDWHILE sequence.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.inside_rt_loop_r
Data type
Value range
[TRUE = Machining within #RT WHILE #RT ENDWHILE,
FALSE]
Access
PLC is reading
Special feature
Waiting for external command velocity
The NC channel waits for an external command velocity.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.wait_ext_command_speed_r
Data type
Value range
[TRUE = channel is waiting
FALSE = external velocity exists]
Access
PLC is reading
Current interpretation of manual mode movements with orientation axes
This data item indicates the active interpretation type for manual mode movements of orientation axes. It can be changed using the NC command #MANUAL[…].
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.orientation_mode_for_manual_mode_r
Data type
DINT
Unit
Value range
0: Rotations about the global coordinate system (ROT_WORLD_CS_AXES)
1: Rotations about the tool coordinate system (ROT_ACT_CS_AXES)
2: Direct change of the Euler angle (ADD_ANGLE_IN_ACT_CS)
Access
PLC is reading
Special feature
Available as of V3.1.3133.0