Trigger mark mode for residual time calculation (P-CHAN-00833)
P-CHAN-00833
Trigger mark mode for residual time calculation in the look-ahead function.
This parameter defines the mode for the end of the residual time calculation in time look-ahead. The residual time is calculated up to the trigger mark based on the motion blocks available and is provided in the path interpolator status.
NC program example (transition from G0 to G1/G2/G3) Mode 0:
N10 G00 G90 X100
N20 Y200
N30 G01 Z0 F300
NC program example (M50 is end label) Mode 1:
N10 G00 G90 X100
N20 Y200
N30 M50
Parameter
eta.mode
Data type
UNS32
Data range
0: The end label of the residual time calculation is the programmed change from rapid traverse block to feed block (from G0 to G01, G02, G03) (default)
1: The end label of the residual time calculation is a programmed M/H function with the M/H number defined in P-CHAN-00832.
Dimension
Default value
0
Remarks
This function is available as of CNC Build V3.1.3080.16 or V3.1.3107.51.
Caution:
The required buffer effect when calculating the residual time is cancelled out by specific control blocks in the program sequence, e.g. position request or selecting/deselecting kinematic transformations (#TRAFO ON/OFF). In these cases, the residual time is 0.