Status data: Access via HLI
The PLC can access the data listed below via the HLI.
Block search active
The interpolator works in block search mode. No axis motion occurs. As long the block search process in the interpolator remains in the HLI_BS_ACTIVE or HLI_BS_WAIT_FOR_PLC_OFF state, this value indicates TRUE.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.block_search_active_r
Data type
Value range
[TRUE = active - Interpolator works in block search mode., FALSE]
Access
PLC is reading
Block search, state
Indicates the current state of the block search mode in the interpolator.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.block_search_state_r
Data type
INT
Value range
Constant
Value
HLI_BS_INACTIVE
0
HLI_BS_WAIT_FOR_PLC_ON
1
HLI_BS_ACTIVE
2
3
HLI_BS_WAIT_RETURN_TO_CONTOUR
4
HLI_BS_RETURNING_TO_CONTOUR
5
HLI_BS_WAIT_FOR_CONTINUE_CONTOUR
6
Access
PLC is reading
Status data: Access via HLI 1:
Block search states
Covered block motion path
Part of the path motion traversed in the current block in relation to the total path.
This status datum contains the current block position referred to the path distance in space in the motion block in per mil sd(t).
Status data: Access via HLI 2:
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.covered_distance_r
Data type
DINT
Unit
0.1 %
Access
PLC is reading
Special features
If a main axis participates in the motion, the covered path motion is in relation to the block path of the first three axes. If no main axis participates in the motion, the covered path motion is the position lag with the longest motion time in relation to the block path.
Currently covered path in the NC program (PCS)
Reads the current distance covered in the NC program since program start or since the last # DISTANCE PROG START CLEAR NC command. The calculation is based on the current position in the current NC block.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.dist_prog_start
Data type
UDINT (* LREAL)
Unit
0.1 µm
Access
PLC is reading
Special features
* As of CNC Build V3.1.3104.01 the data element is provided in LREAL forma.
Line counter, NC program
The datum indicates the NC program line which is the source of the command just processed by the interpolator.
The value is derived from the number of NC program lines which the decoder has read since the NC program started. All the lines read the decoder are counted, i.e. repeatedly read lines, empty and comment lines. All commands to the interpolator resulting from decoding a NC program line are assigned to the associated line counter.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.block_count_r
Data type
UDINT
Access
PLC is reading
Block search, distance from continuation position
If a NC program is started in block search modus, the NC program is processed in simulative mode (without axis motion) until the continuation position is reached. Block search is then in the HLI_BS_WAIT_FOR_PLC_OFF state and calculates the distance between the actual positions of the axis and the continuation position. If block search is in the HLI_BS_RETURNING_TO_CONTOUR state, this value is refreshed cyclically.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.block_search_path_deviation_r
Data type
UDINT
Unit
0.1 µm
Value range
[0, MAX_SGN32]
Access
PLC is reading
Stop condition
Displays the condition why the current motion was stopped.
Signal flow
CNC → PLC
ST path
gpCh[channel_idx]^.bahn_state.stop_conditions_r
Data type
DINT
Value range
See Value range of stop conditions with explanations.
Access
PLC is reading
Constant in PLC
Value
Explanation
HLI_SC_FEEDHOLD
0x0001
Path feed stop
HLI_SC_VFG
0x0002
No axis-specific feed enable.
HLI_SC_SINGLE_BLOCK
0x0004
Single step mode active.
HLI_SC_M00_OR_M01
0x0010
M00 (programmed stop), M01 (optional stop) is active.
HLI_SC_PLC_ACKNOWLEDGE
0x0020
Stop occurs due to waiting for an acknowledgement from the SPS. This may occur as a result of the output of M or H technology functions but is not restricted to them alone.
HLI_SC_OVERRIDE_ZERO
0x0040
Override = 0.
HLI_SC_OVERRIDE_RAPID_ZERO
0x0080
Override = 0 with rapid traverse blocks
HLI_SC_DELAY_TIME
0x0200
Dwell time.
HLI_SC_CHANNEL_SYNC
0x0800
Channel synchronisation is active.
HLI_SC_IPO_INPUT_EMPTY
0x1000
Input FIFO of the interpolation is empty.
HLI_SC_IPO_INPUT_DISABLED
0x2000
Input of function blocks (e.g. motion blocks etc.) disabled.
HLI_SC_WAIT_FOR_AXES
0x8000
Stop occurs due to waiting until a commanded axis swap is completed.
HLI_SC_CHANNEL_ERROR
0x00010000
An error occurred in the channel.
HLI_SC_WAIT_TECHNO_ACK
0x00020000
Waiting for acknowledgement of M/H/ST technology functions.
HLI_SC_W_C_AFTER_COLLISION
0x00040000
After a detected collision, waiting for motion resumption.
HLI_SC_SLOPE_SUPPLY_PROBLEM
0x00080000
Block supply problem (only occurs in conjunction with HSC slope).
HLI_SC_BACK_INTERPOLATION
0x00100000
Back interpolation after tracking mode is active.
HLI_SC_STOP_REVERSIBLE
0x00200000
Stop since M00 (programmed stop) is active. However, the NC program can be processed backwards despite M00 (available as of V3.1.3039.01).
HLI_SC_BREAKPOINT_STOP
0x00400000
Stop after a breakpoint (stop point) is reached; available as of V3.1.3039.01.
HLI_SC_M0_STOP
0x02000000
Stop after an M00 function is reached
HLI_SC_M1_STOP
0x04000000
Stop after an M01 function is reached
HLI_SC_INSERT_STOP_AT_DIST
0x08000000
Stop after an M function inserted by the Control Unit “Inserting stop marks” is reached.
HLI_SC_DEC_SYN_CHAN_EMPTY
0x10000000
Decoder is waiting for synchronisation. NC channel has no job.
HLI_SC_WAIT_FOR_ADD_IFC
0x20000000
Stop because waiting condition is active in the additive interface (3D distance control).
HLI_SC_WAIT_FOR_AXIS_DIST_CTRL
0x40000000
Stop because waiting condition is active in the distance control (2D).